Error code overview
Error 2 - Battery voltage too high:
This error will auto-reset after the battery voltage has dropped. This error can be due to other charging equipment connected to the battery or a fault in the charge controller.
Error 3, Error 4 - Remote temperature sensor failure:
Check if the T-sense connector is properly connected to a remote temperature sensor. Most likely cause: the remote T-sense connector is connected to the BAT+ or BAT- terminal. This error will auto-reset after proper connection.
Error 5 - Remote temperature sensor failure (connection lost):
Check if the T-sense connector is properly connected to a remote temperature sensor. This error will not auto-reset.
Error 6, Error 7 - Remote battery voltage sense failure:
Check if the V-sense connector is properly connected to the battery terminals. Most likely cause: the remote V-sense connector is connected in reverse polarity to the BAT+ or BAT- terminals.
Error 8 - Remote battery voltage sense failure (connection lost):
Error 11 - Battery high ripple voltage:
High DC ripple is usually caused by loose DC cable connections and/or too thin DC wiring. After the inverter has switched off due to high DC ripple voltage, it waits 30 seconds and then restarts.
After three restarts followed by a shutdown due to high DC ripple within 30 seconds of restarting, the inverter will shutdown and stops retrying. To restart the inverter, switch it Off and then On.
Continuous high DC ripple reduces the inverter life expectancy.
Error 17 - Controller overheated despite reduced output current:
This error will auto-reset after charger has cooled down. Check the ambient temperature and check for obstructions near the ventilation grilles,
Error 20 - Maximum Bulk-time exceeded:
The maximum bulk time protection is a feature that was in the chargers when they were just released (2015 or earlier) and later the feature was removed.
If you do see this error, then update to the latest firmware.
If you then still have the error, perform a reset to factory defaults of the configuration, and reconfigure the solar charger.
Error 22, Error 23 - Internal temperature sensor failure:
The internal temperature measurements are out of range.
Disconnect all wires, and then reconnect all wires, to restart the unit.
If the error remains, please contact your dealer, there might be a hardware defect.
Error 27 - Charger short circuit:
This condition indicates an over-current condition on the battery side. It can occur when a battery is attached to the unit using a contactor. Or in case the charger starts up without a battery connected but connected to an inverter that has a large input capacitance.
This error will auto-reset. If the error does not auto-reset disconnect the charge controller from all power-sources, wait 3 minutes, and power up again. If the error persists the charge controller is probably faulty.
Error 29 - Overcharge protection:
This error will auto-reset once the battery voltage drops below the float voltage. To protect the battery from over-charging the battery is disconnected.
Possible causes:
Over-sized PV array configuration, if there are too many panels in series the battery voltage cannot be reduced any further. Consider wiring more PV panels in parallel to reduce the voltage.
Configuration issue, check if the battery settings match with the installation (especially absorption and float voltage settings).
Another charger in the system raises the battery voltage above the expected level.
Error 33 - PV overvoltage:
This error will auto-reset after PV-voltage has dropped to safe limit. This error is an indication that the PV-array configuration with regard to open-circuit voltage is critical for this charger. Check configuration, and if required, re-organise panels.
Error 34 - PV overcurrent:
The current from the solar-panel array has exceeded the rated current limit. This error could be generated due to an internal system fault. Disconnect the charger from all power-sources, wait 3 minutes, and power-up again. If the error persists the controller is probably faulty, contact your dealer.
Error 35 - PV over power:
Please upgrade your firmware to at least v1.08 as the issues causing this error have been addressed.
If you are using firmware v1.08 or newer this error indicates that the internal dc voltage is too high. This error will auto-reset. If the error does not auto-reset disconnect the charge controller from all power-sources, wait 3 minutes, and power up again. If the error persists the charge controller is probably faulty.
Error 41 - Inverter shutdown (panel isolation resistance too low):
PV panel isolation resistance too low. Check the PV array cabling and panel isolation, the inverter restarts automatically once the issue is resolved.
Error 42 - Inverter shutdown (ground current too high >30mA:
The ground leakage current in the PV array exceeds the allowed 30mA limit. Check the PV array cabling and panel isolation. Check the installation and restart the unit using the power-switch.
Error 43 - Inverter shutdown (ground fault):
The voltage difference between Neutral and Ground is too high.
Inverter or Multi (not connected to the grid):
The internal ground relay is activated but the voltage over the relay is too high. The relay might be damaged.
Multi (connected to the grid):
The ground wire in the installation is not present or not connected properly.
Line and Neutral are swapped in the installation.
This error will not auto-reset. Check the installation and restart the unit using the power-switch.
Error 50, Error 52 - Inverter overload, inverter peak current:
Some loads like motors or pumps draw large inrush currents in a start-up situation. In such circumstances, it is possible that the start-up current exceeds the over current trip level of the inverter. In this case the output voltage will quickly decrease to limit the output current of the inverter. If the over current trip level is continuously exceeded, the inverter will shut down: wait 30 seconds and then restart.
The Inverter can supply more power than the nominal power level for a short time. If the time is exceed the inverter stops.
After three restarts followed by another overload within 30 seconds of restarting, the inverter will shutdown and remain off. To restart the inverter, switch it Off, then On.
If the error persists reduce the load on the AC out terminal by switching off or disconnecting appliances.
Error 51 -Inverter temperature too high:
A high ambient temperature or enduring high load may result in shut down to over temperature. Reduce load and/or move inverter to better ventilated area and check for obstructions near the fan outlets.
The inverter will restart after 30 seconds. The inverter will not stay off after multiple retries.
Error 53 - Inverter output voltage:
If the battery voltage is getting low and a large load is applied to the AC output the inverter is unable to maintain the proper output voltage. Recharge the battery or reduce the AC loads to continue operation.
Error 54 - Inverter output voltage:
If the battery voltage is getting low and a large load is applied to the AC output the inverter is unable to maintain the proper output voltage. Re-charge the battery or reduce the AC loads to continue operation.
If the error immediately pops up when switching on the inverter (without load) on a full battery the cause is most likely a broken replaceable internal fuse. Contact your Victron dealer for support.
Error 55, Error 56, Error 58 - Inverter self test failed:
The inverter performs diagnostic tests before it activates its output. In the case that one of these tests fails an error message is displayed and the inverter does not turn on.
First try to restart the inverter, by switching it Off, and then On. If error persists the inverter is probably faulty.
Error 57 - Inverter AC voltage on output:
There is already AC voltage on the AC out terminal before switching on the inverter. Check that the AC out is not connected to a mains outlet or to another inverter.
Error 59 - AC-IN1 relay test fault:
Automatic checking of the disconnect means failure. This usually indicates a broken relay (sticky contact) in the AC input stage.
Error 65 - Communication warning:
Communication with one of the paralleled controllers was lost. To clear the warning, switch the controller off and back on again.
Error 66 - Incompatible device:
The controller is being paralleled to another controller that has different settings and/or a different charge algorithm.
Make sure all settings are the same and update firmware on all chargers to the latest version.
This error also appears if MPPTs are connected to a GX device while configured for a VE.Smart network. Disable the VE.Smart networking features and use DVCC on the GX instead.
Further troubleshooting steps described here.
Error 67 - BMS Connection lost:
This error shows when the charger is configured to be controlled by a BMS, but does not receive any BMS control messages. In that situation, the charger stops charging by reducing its output voltage to the battery base voltage. This is a safety mechanism, the reason to still enable the output is to allow a system to self-recover from a battery low situation.
Solar Chargers only show this error when there is solar power available and thus the device is ready to initiate charging. It does not show at night. And in case there is a permanent problem, the error will raise in the morning and clear at night, and so forth.
Solution: check the connection between the charger and the BMS.
How to reconfigure the charger to standalone mode
Our Chargers and Solar Chargers automatically configure themselves to be BMS-controlled when they are connected to one; either direct or via a GX Device. And that setting is semi-permanent: power cycling the charger will not reset it.
When removing charger from such system, and reusing it in a system without BMS, that setting needs to be cleared. Here is how to do that:
Chargers with LCD display: go into the setup menu, and change setting ‘BMS’ from ‘Y’ to ‘N’ (setup item 31).
Other chargers: reset the charger to factory defaults with VictronConnect, and then reconfigure it.
Error 69 - Network misconfigured:
Applies to Inverter RS and Multi RS models. Firmware versions 1.11 and higher.
This error indicates an issue in the configuration. There are units present on the same CAN bus that have different system configurations. Please ensure that all units are set to either “Single Phase” or “Three Phase” and all units are set to either “50Hz” or “60Hz”. All units will remain off until the configuration is fixed, after which the units will resume operation.
Error 70 - Network misconfigured:
Applies to Inverter RS models. Firmware versions 1.11 and higher.
Inverter RS units cannot be paired with a Multi RS and/or Transfer Switch.
Error 71 - Network misconfigured:
There are units present with incompatible firmware on the can bus. Make sure that all units are updated to the same firmware version. All units will remain off until the until the firmwares are updated, after which the units will resume operation.
Error 72 - Phase rotation:
Applies to Inverter RS and Multi RS models. Firmware versions 1.12 and higher.
Check the if the phase order is correct L1→L2→L3.
The inverters remain operational, they won't connect to the grid. Once the issue is resolved the units will connect.
Error 73 - Multiple AC inputs:
Per phase only one active connection to the grid is allowed, remove or switch off the redundant connection.
Error 74 - Phase overload:
The number of inverters in parallel doesn't match with the transfer capabilities of the ac input relay of the Multi RS or Transfer switch. Firmware v1.12 does not support parallel units and a grid connection, so any combination of a Multi RS with a grid connection with more than one unit in parallel will trigger this error code on the Multi RS. The Multi RS only supports 3 units in 3-phase configuration at the moment.
Error 75 - Network misconfigured:
Applies to Multi RS models. Firmware versions 1.19 and higher.
Three phase operation is not yet certified in combination with the selected grid code.
Error 76 - Network incomplete:
The inverters shut down because there are insufficient units to operate a networked setup. Check if all required units are powered on and that the CAN interface cables are connected properly. All units remain off until the installation is fixed, after which the units resume operation.
Related configuration settings in VictronConnect are “Prevent CAN network islanding” + “Number of inverters in the system” and “Continue with missing phase” in the System section.
Err 77 - Settings sync disabled
Applies to Inverter RS and Multi RS models. Firmware v1.29 and higher.
This is a warning that indicates a mixed configuration in a networked setup where system settings synchronisation is enabled on some devices but not on all units. The units that have the settings synchronisation disabled show this warning. The units remain operational, to clear the warning either enable or disable system settings synchronisation on all units.
Error 116 - Calibration data lost:
If the unit does not work and error 116 pops up as the active error the unit is faulty, contact your dealer for a replacement.
If the error is only present in the history data and the unit operates normally this error can be ignored safely.
Explanation: When the units power up for the very first time in the factory, it does not have calibration data and an error 116 is logged. Obviously this should have been cleared, but in the beginning units left the factory with this message still in the history data.
Error 117 - Incompatible firmware:
This error indicates that a firmware update did not complete, so the device is only partially updated. Possible causes are: device out of range when updating over the air, a cable got disconnected or power was lost during the update session.
To fix this the update needs to be retried, download the correct firmware for your device from the Victron Professional Portal.
When your GX device is connected to VRM, you can do a remote firmware update using this firmware file. You can do this via the VRM website or using the VRM tab in VictronConnect. VictronConnect can also be used together with the firmware file to update using a Bluetooth connection.
The procedure to add the file to VictronConnect and start the update is described here: 9. Firmware updates.
Error 119 - Settings data lost:
The charger cannot read its configuration, and stopped.
This error will not auto-reset. To get it working again:
First, restore it to factory defaults. (top right in Victron Connect, click on the three dots).
Disconnect the charge controller from all power-sources.
Wait 3 minutes, and power up again.
Reconfigure the charger.
Please do report this to your Victron dealer and ask him to escalate it to Victron; as this error should never happen. Preferably include firmware version and any other specifics (VRM URL, VictronConnect screenshots or similar).
Error 121 - Tester fail:
If the unit does not work and error 121 pops up as the active error the unit is faulty, contact your dealer for a replacement.
If the error is only present in the history data and the unit operates normally this error can be ignored safely. Explanation: when the units powers up for the very first time in the factory, it does not have calibration data and an error 121 is logged. Obviously this should have been cleared, but in the beginning units left the factory with this message still in the history data.
Error 200 - Internal DC voltage error:
The unit performs internal diagnostics when activating its internal DC-DC converter. This error indicates that something is wrong with the DC-DC converter.
This error will not auto-reset. Check the installation and restart the unit using the power-switch. If the error persists the unit is probably faulty.
Error 201 - Internal DC voltage error:
Applies to the MPPT RS, Inverter RS and Multi RS.
This “Internal DC voltage measurement error”, is raised in case an internal (high) voltage measurement does not match certain criteria.
First, make sure to update the firmware to v1.08 or later. The limits were too strict in earlier versions. And it could trigger falsely during MPPT start-up in the morning and MPPT shutdown in the evening.
If the error still occurs after updating to v1.08 or later, then it means that a measurement circuit inside the unit is broken.
This error will not auto-reset. Check the installation and restart the unit using the power-switch. If the error persists, even after above mentioned firmware update, the unit is most likely faulty and must be sent in for repair/replacement.
Err 202 - Internal GFCI sensor error:
The sensor used to measure residual current did not pass the internal self test. This error will not auto-reset. Check the installation and restart the unit using the power-switch.
If the error persists the unit is probably faulty and must be sent in for repair/replacement.
Error 203, Error 204, Error 212, Error 215 - Internal supply voltage error:
The unit performs internal diagnostics when activating its internal voltage supplies. This error indicates that something is wrong with an internal supply voltage.