9. Configuration
9.1. Menu structure and configurable parameters
After completing the installation and setting up the internet connection (if required), go through the menu from top to bottom to configure the GX device as needed.
The menu structure is divided into 6 main categories:
Devices: All connected devices
General: Access control, Display, Firmware, Support
Connectivity: Ethernet, Wi-Fi, Bluetooth, VE.Can
VRM: Remote monitoring portal
Integrations: Relays, Sensors, Tanks, PV, Inverters, Modbus, MQTT...
System Setup: AC/DC system, ESS, DVCC, Battery...
Item | Default | Description |
Settings - The main menu. | ||
Settings → Devices | ||
Various | Various | Lists all devices connected to the GX. Most entries include submenus with further details and configuration options. |
Settings → General | ||
Settings → General → Firmware | ||
Firmware - Read full feature description | ||
Firmware version | x.xx | Shows the installed firmware version. |
Build date/time | Shows build date and time. | |
Image type | Normal | Shows the image type (Normal or Large). |
Online updates | Submenu for online update control. | |
Online updates: Auto update | Check only | Checks for new versions. Options: Disabled, Check only, Checkl and update. |
Online updates: Update feed | Official release | Options: Official release, Beta release. |
Image type | Normal | Normal or Large image. Large adds Node-RED and Signal K server. |
Online updates: Check for updates | Press to check | Manual check for updates. |
Online updates: Update available | Press to update | Shown when updates are available. |
Install firmware from SD/USB | Use this menu to install a new version from a microSD card or USB stick. Insert the card or stick that holds the new firmware .swu file. | |
Stored backup firmware | Submenu for switching between the current and previously installed firmware version. | |
NoteNote that for most system applications our advise is to keep automatic updates disabled; as is also the default factory setting. Instead, update the system at a convenient moment; when people are on location and ready to revert to a previous system and/or troubleshoot in case of issues. | ||
Settings → General → Access & Security | ||
Access level | User and User & Installer | Set this to 'User' to prevent accidental and unwanted changes to the configuration. User & Installer has additional privileges and once changed from default requires a password. Password is available from your dealer. |
Local network security profile | Secured | Secured = Password protection and network communication encryption. A password must be set. Weak = Password protection but no network communication encryption. A password must be set. Unsecured = No password protection and no network communication encryption |
Remote support | Disabled | Enable this to allow Victron engineers to access your system in case there is a problem. |
Remote support tunnel | Offline | Displays 'Online' when 'Remote support' is enabled. |
Remote support IP and port | [IP;port] | Displays the remote support IP address and port. |
Settings → General → Display & Appearance | ||
Adaptive brightness | Enabled | Allows to switch adaptive brightness off. Only for GX Touch displays and Ekrano GX. |
Display off time | 10s | Allows to set the display off time between 10s and 30 minutes, or never. |
GX display appearance | Light | Allows to toggle between light and dark mode. |
Remote Console appearance | Auto | Options are Same as GX display or Auto. |
Start page | Brief page | Submenu to set the start page and define a timeout for reverting to it. |
Brief page | Submenu to adjust the level of detail shown in gauges, tank information, and centre widgets. | |
Boat page | Disabled | Enables or disables the Boat page. When dual E-Drive controllers are connected, additional information and configuration options become available. |
Data units | Submenu to set the units for temperature, volume, electrical power, and GPS. | |
Minimum and maximum gauge ranges | Submenu to set fixed min/max ranges for AC/DC gauges and graphs, or enable auto-ranging. | |
UI Animations | Disabled | Switch to turn off UI animations to reduce CPU usage. |
User interface | New UI | Submenu to switch between the new and classic user interface. |
Settings → General → Alarms & Feedback | ||
Alarms & Feedback | Enabled | When an alarm occurs on the GX device or a connected product, the device will emit a beep, unless this setting is set to disabled. |
Settings → General → Language | ||
Language | English | Submenu to select the user interface language. |
Settings → General → Date & Time | ||
Date & Time | Select your local time zone. The time is then adjusted automatically. | |
Settings → General → Reboot | ||
Reboot | Reboot Now | Reboots the GX device. |
Settings → General → Documentation | ||
Documentation | Submenu with links to product support, the Victron Community, and Where to buy option. | |
Settings → General → Support status | ||
Support status (modification checks) | Submenu showing if the GX device is in standard or modified state, with an option to restore official firmware to fix the modified state. | |
Settings → General → Demo mode | ||
Demo mode | Disabled | Activates a simulation mode to demonstrate product and system features for clients or exhibitions. It allows users to explore the interface without altering real settings. Note: Enabling demo mode adds simulated devices to the VRM installation. Available demos include ESS, Boat, and Motorhome. |
Settings → Connectivity | ||
Settings → Connectivity → Ethernet - Read full feature description | ||
State | Unplugged | Indicates the current connection status of the device: Unplugged, Connecting, or Connected. |
MAC address | Displays the unique hardware address of the network interface. Used for network identification and troubleshooting. | |
IP configuration | Automatic | Options: Automatic (DHCP) and manual IP address allocation |
Allow using ethernet for internet access | Disabled | Use this feature to allow the GX using the connection for internet access. |
IP address | Shows the current IP address assigned to the device for network communication. | |
Netmask | Displays the subnet mask used to define the local network range. | |
Gateway | Displays the IP address of the network gateway used to access external networks, such as the internet. | |
DNS server | Displays the IP address of the DNS (Domain Name System) server used to resolve domain names into IP addresses. | |
Enable Link-local | Disabled | Option to enable the link-local interface. |
Link-local IP address | Displays the automatically assigned IP address used for local network communication when no DHCP server is available. Typically in the 169.254.x.x range. | |
Settings → Connectivity → Wi-Fi - Read full feature description | ||
Create access point | Enabled | Enables or disables the internal WiFi access point of the GX device. Disabling it turns off the device’s ability to broadcast its own network. |
Access Point password | Connect using the WiFi key, printed both on the side of the box and on a card included in the plastic bag. A custom access point password can also be set if required. | |
Allow using WiFi for internet access | Disabled | Use this feature to allow the GX using the connection for internet access. |
Wi-Fi networks | Displays the list of available WiFi networks and the network currently connected to the GX device, if any. | |
Name | Connected | Displays the SSID (network name) of the connected or selected WiFi network. |
Forget network | Forget | Press to remove the saved WiFi network configuration. Use this when switching to a different network or troubleshooting connection issues. |
Signal strength | % | Displays the WiFi signal strength as a percentage (%), indicating the quality of the wireless connection. |
State | Indicates the current WiFi connection status of the GX device. Possible values: Connected, Connecting, or Disconnected. | |
Mac address | Displays the unique hardware address of the network interface. Used for network identification and troubleshooting. | |
IP configuration | Automatic | Choose between Automatic (DHCP) and Manual IP address configuration. |
Settings → Connectivity → Bluetooth (for VictronConnect App) | ||
Bluetooth (for VictronConnect App) | Enabled | Switch to enable or disable the built-in Bluetooth interface. Pincode: For GX devices with serial numbers before HQ2242, the default PIN is 000000. For HQ2242 or later, a random 6-digit PIN is printed on the label on the back of the device. |
Settings → Connectivity → Mobile Network | ||
Mobile Network | No cellular modem connected | Submenu with options to configure a connected GX GSM or GX LTE 4G modem. Read full feature description. |
Settings → Connectivity → VE.Can port | ||
VE.Can port 1..2 (if applicable) | VE.Can (250 kbit/s | Submenu to configure the CAN-bus profile for the VE.Can port(s). Available options include: Disabled, VE.Can (250 kbit/s), VE.Can & CAN-bus BMS (250 kbit/s), VE.Can & CANopen E-drive (250 kbit/s), CAN-bus BMS LV (500 kbit/s), Oceanvolt (250 kbit/s), RV-C (250 kbit/s), CANopen E-drive (500 kbit/s). Additional options include: Devices, NMEA2000-out, Unique Identity Number Selector, Check Unique ID Numbers, and Network Status. |
Settings → VRM - Read full feature description | ||
VRM Portal | Full | This setting determines the system’s connection to the VRM portal:
VRM Portal ID | Use this ID string when registering the GX device on the VRM Portal. | |
VRM Device Registration | Contains a link and/or QR code for device registration on the VRM Portal. | |
VRM device instances | Provides the device instances for every device connected to the GX. Devices are grouped by service type (e.g. battery monitor, solar charger, AC load) and sorted alphabetically within each group. Instance numbers only need to be unique within the same service type, the same instance number on different device types is not a conflict. | |
Log interval | 15 minutes | Set the interval between data logs to any value from 1 minute to 1 day. For systems with unstable connections, a longer interval is recommended. |
Use secure connection (HTTPS) | 15 minutes | Encrypts communication between the GX device and the VRM server using HTTPS for secure data transmission. |
Last contact | Displays the time elapsed since the GX device last communicated with the VRM server. | |
Connection status | No error | Shows the current status of the VRM connection. If there is a communication error, it will be displayed here. |
Reboot device when no contact | Disabled | When enabled, the GX device will automatically reboot after a set delay if the internet connection is lost. This can help resolve temporary networking issues. |
No contact reset delay (hh:mm) | 01:00 | Defines how long the GX device must be offline before it automatically restarts to restore connectivity. |
Storage location | Internal storage | Indicates whether data is being stored on the internal memory or an external device such as a USB drive or microSD card, if mounted. |
Free disk space | Displays the amount of available storage space on the current storage device. | |
microSD / USB | Use this option to safely eject a connected microSD card or USB storage device before removal. Removing it without ejecting may result in data loss. | |
Stored records | Displays the number of data records stored locally while the device is offline. The GX device will upload these records automatically once the internet connection is restored. | |
Oldest record age | Indicates how old the oldest locally stored record is, in cases where the GX device has been unable to connect to the internet or VRM. | |
Settings → Integrations → PV Inverters - Read full feature description | ||
Inverters | Displays connected AC PV inverters. | |
Position | AC Input 1 | AC input 1, AC input 2, AC Output |
Phase | L1 | |
Show | Yes | |
Dynamic power limiting | Enabled | The PV inverter has support for power limiting. Disable this setting if it interferes with normal operation. |
Find PV inverters | Scan for available PV inverters. | |
Detected IP addresses | Displays the IP address of PV inverters that have been discovered. | |
Add IP address manually | If an inverter has a manually assigned IP address, you can add it directly here. | |
Automatic scanning | This setting will continue to look for PV inverters, this can be useful if using a DHCP assigned IP address that might change. | |
Modbus port and unit ID settings | Submenu where port and unit ID can be added. | |
Settings → Integrations → Energy Meters via RS485 - Read full feature description | ||
Role | Grid meter | Define the role of the energy meter. Available options: Grid, PV inverter, Generator, AC load, EV Charger, Heat pump |
Phase type | Single phase | Select the phase type of the system to be measured: either single-phase or multi-phase. |
Settings → Integrations → Modbus Devices | ||
Automatic scanning | Enabled | Scans automatically for Modbus TCP/UDP devices. |
Scan for devices | Press to scan | Manually trigger a scan for Modbus TCP/UDP devices. |
Saved devices | Displays a list of found Modbus TCP/UDP devices and their IP address. | |
Discovered devices | Displays a list of discovered Modbus TCP/UDP devices. Use this menu to activate these devices. | |
Settings → Integrations → Bluetooth Sensors | ||
Enable | Disabled | Enable this option to scan for supported Bluetooth sensors. Enable to scan for supported Bluetooth sensors. Discovered sensors are listed with a slider to activate them. |
Continuous scanning | Disabled | Forces continuous scanning for supported Bluetooth sensors. May interfere with WiFi operation. |
Bluetooth adapters | Lists built-in and connected Bluetooth adapters with their MAC addresses. | |
Settings → Integrations → Tank and Temperature Sensors | ||
Tank level input (number depends on device) | Disabled | Enable to display the tank level inputs in the Devices list. |
Temperature input (number depends on device) | Disabled | Enable to display the temperature inputs in the Devices list. |
Settings → Integrations → Relays | ||
Function (Relay #) | Alarm relay | Selects the function assigned to the relay. Available options include: Disabled, Alarm relay, Genset start/stop, Connected genset helper relay, Tank pump, Temperature, and Manual. When the relay is set to manual mode, a slider is displayed that allows you to turn the relay on or off manually. |
Polarity (Relay #) | Normally open | Sets the relay polarity on the back of the GX device. Options are Normally open or Normally closed. Note: Using Normally closed increases the power consumption of the GX device. |
Settings → Integrations → Digital I/O | ||
GX Built-in - Digital input # | Disabled | Controls the function of digital inputs. Available options include: Disabled, Door alarm, Bilge pump, Bilge alarm, Burglar alarm, Smoke alarm, Fire alarm, CO₂ alarm, and Generator. On specific GX devices, additional options such as Touch input control and Pulse meter are also available. |
Settings → Integrations → MQTT Access | ||
MQTT Access | Disabled | MQTT access only needs to be enabled when integrating a third party device or service like Home Assistant which requires access to the MQTT broker over the local network. |
Settings → Integrations → Modbus TCP Server | ||
Modbus TCP Server | Submenu to enable Modbus TCP and grant access permissions. | |
Enable Modbus TCP Server | Disabled | This setting enables the ModbusTCP service. More information about ModbusTCP in this document and in the communications white paper https://www.victronenergy.com/upload/documents/Whitepaper-Data-communication-with-Victron-Energy-products_EN.pdf |
Access permissions | Write allowed | Defines whether Modbus clients have read-only access or are also allowed to write values. |
Available services | Lists all available services together with their Unit ID. | |
Settings → Integrations → Venus OS Large Features | ||
Signal K | Enable to start the integrated Signal K server. | |
Node-RED | Enable to start the integrated Node-RED environment. | |
Venus OS Large Documentation | Link to the Venus OS Large documentation. | |
Victron Community | Link to the Victron Community. | |
Settings → System Setup | ||
Settings → System Setup → System name | ||
System name | Automatic | Select the system name - presets or user defined. |
Settings → System Setup → AC System | ||
AC input 1 | Generator | Select Not available, Generator, Grid or Shore power. Note: additional configuration is required for complete setup of these options. |
AC input 2 | Grid | Same choices as above. |
Position of AC loads | AC output only | Options:
Monitor for grid failure | Disabled | Monitors for loss of AC-input and triggers an alarm if detected. Alarm is cleared when the AC-input is reconnected. |
Settings → System Setup → ESS - Read full feature description. | ||
Mode | Optimized with BatteryLife | Options: Optimized with BatteryLife, Optimized without BatteryLife, Keep batteries charged, External control |
Grid metering | Inverter/charger | Leave this setting at Inverter/charger if no external grid meter is used. Set to External meter when using a supported external energy meter. |
Grid meter required | Yes | This option becomes available when Grid metering is set to External meter. Sets the response when the external grid meter is lost.
Self-consumption from battery | All system loads | This setting allows for ESS to only use battery power for essential loads. Options are 'All system loads' or 'Only critical loads'. |
Multiphase regulation | Total of all phases | Use this setting in three-phase grid-connected systems. It enables phase compensation to help balance power flow across all phases. |
Minimum SOC (unless grid fails) | 10% | Configurable minimum SoC limit. ESS will supply loads from the grid once the SoC has fallen to the configured setting - except when the utility grid has failed and the system is in Inverter mode. |
Active SOC limit | 10% | Use this setting to see the current BatteryLife SoC level. Only in 'Optimized with BatteryLife' mode. |
BatteryLife state | Self-Consumption | Displays the BatteryLife state, which can be one of the following: Self-consumption, Discharge disabled, Slow charge, Sustain, or Recharge. Only in 'Optimized with BatteryLife' mode. |
Limit inverter power | Disabled | Limit the power drawn by the Multi: ie. limit the power being inverted from DC to AC. |
Grid set point | 50W | Defines the target power flow to the grid. A higher setpoint provides a buffer to help prevent unintentional energy export during sudden load changes. |
Grid feed-in | Configure and limit the amount of power fed into the grid. Options include: AC-coupled PV - feed in excess, DC-coupled PV - feed in excess, Limit system feed-in. Also displays whether feed-in limiting is currently active. | |
Peak shaving | Above minimum SoC only | Above minimum SoC only, or Always. Also includes a submenu to manually set the system AC import and export current limits per phase. |
Scheduled charge levels | Inactive | Allows configuration of up to five time periods during which the system will charge the battery using power from the grid. |
Settings → System Setup → Batteries | ||
Battery monitor | Automatic | Select the SoC source. This function is useful where there is more than one source of battery. Options: Automatic, No battery monitor and available battery monitor sources. For more details see Battery state of charge (SoC). |
Auto-selected | Displays the automatically selected SoC source when the ‘Battery monitor’ is set to ‘Automatic’. | |
[Battery] | Provides live data and a quick link to the individual battery page. Only available if Battery measurement is set to visible. | |
Battery measurements | Use this menu to define the battery data shown when clicking the Battery icon on the Overview page. The same selection is also visible on the VRM Porta. | |
Settings → System Setup → Charge Control - Read full feature description | ||
DVCC | Disabled | Enabling DVCC turns the GX device from a passive monitor into an active controller. By default, it is disabled unless a compatible BMS-Can managed battery is connected, in which case it is set and locked according to the manufacturer’s specifications. |
Limit charge current | Disabled | Sets a user-defined maximum charge current for the entire system, specified in Amps. This allows coordinated charge control across all supported devices. |
Limit managed battery charge voltage | Disabled | This option is intended only for initial balancing of 15s Pylontech batteries. Do not use it for other purposes, as it may lead to undesirable side effects. |
SVS - Shared voltage sense | Disabled | When enabled, the GX device automatically selects the best available voltage measurement and shares it with other connected devices. |
STS - Shared temperature sense | Disabled | When enabled, the GX device transmits the measured battery temperature to the inverter/charger system and all connected solar chargers. |
Temperature sensor | Automatic | Select which temperature sensor is used for Shared Temperature Sense. In automatic mode, the GX device chooses the most suitable available sensor. |
SCS - Shared current sense | No | When enabled, the GX device forwards the battery current measured by a connected battery monitor to all supported solar chargers for coordinated charging behaviour. |
SCS status | Displays if SCS is enabled, or why it is disabled. | |
Controlling BMS | Automatic | Selects which Battery Management System (BMS) is used to control the battery, or disable BMS control. In automatic mode, the GX device chooses the appropriate BMS based on the system configuration. |
Auto selected | Displays the BMS currently selected by the system when ‘Controlling BMS’ is set to ‘Automatic’. | |
Settings → System Setup → Display DC Loads | ||
Display DC Loads | Disabled | Enable this for boats, vehicles and installations with DC loads and chargers - in addition to Multi and MPPT chargers. This won't be applicable to most off-grid installations; and any discrepancy between the DC current measured by the Multi, and by the BMV, will be attributed to a 'DC system'. This may be power-in from an alternator, or power-out from a pump, for example. A positive value indicates consumption. A negative value indicates charging, for example by an alternator. Note that the value shown will always be an approximation, and is affected by the variation in sample rate between elements of the system. To replace the approximated values with accurate measurements, a SmartShunt can be used, which needs to be configured to Monitor mode “DC Energy Meter” and DC meter type “DC System”. |
Wireless AC sensors (if applicable) | ||
Select the position for each AC sensor (PV Inverter on AC-input 1, 2 or on AC-output). More information about the Wireless AC sensors. | ||
Settings → Devices → GPS - Read full feature description | ||
GPS information | - | Displays GPS data including: Status, Latitude, Longitude, Speed, Course, Altitude, and Number of satellites in view. |
Device | - | Displays device related information for diagnostic. |
Settings → Devices → Genset - Read full feature description | ||
Autostart functionality | Disabled | Enable or disable the generator’s Autostart feature. Further configuration is available under Genset → Settings → Conditions. |
Manual control | - | Allows manual generator operation for a specified duration. |
State | Not running | Shows the state of the generator. Possible state messages: Stopped, Warm-up, Manually started, Running by condition, Cool-down, Stopping |
Error | #0 No error | Displays if there is an error (e.g. generator is supposed to be running but no AC input is detected) |
Settings | Contains submenus for further configuration, such as Conditions, Warm-up & Cool-down, and Quiet Hours. Also includes a switch to enable an alarm if the generator is not in Autostart mode. | |
Run time and service | Displays the total generator runtime, daily runtime, time remaining until the next service, and the configured service interval. Includes options to reset both the service timer and the daily runtime counter. | |
Settings → Devices → Genset → Settings → Conditions | ||
On loss of communication | Stop generator | Defines what the system should do if communication with the GX device is lost. Options: Stop generator, Start generator, Keep generator running. |
Stop generator when AC input is available | Disabled | Useful for backup systems where a Quattro is connected to mains on one AC input and a generator on the other. When enabled, the generator will stop automatically once mains power becomes available again. |
Battery SOC | Disabled | Use the battery state of charge (SoC) to control generator start and stop behaviour. Enable to activate. Start when SoC is lower than the defined percentage. A separate start value can be set for quiet hours to override them if necessary. Start after the SOC condition is reached for [seconds]. Stop when SoC is higher than the defined percentage. A separate stop value for quiet hours can be set to minimise runtime once the system has stabilised. A separate stop value can be set for quiet hours to override them if necessary. |
Battery current Battery voltage AC load | Disabled | Use any of the parameters to control generator start and stop behaviour. Enable to activate. Start when value is higher than - Amps / Voltage / Watts Start value during quiet hours - Amps / Voltage / Watts (to override programmed quiet hours when absolutely necessary). Start after condition is reached for [seconds] (to allow for momentary spikes to pass without triggering start). Stop when value is lower than - Amps / Voltage / Watts. Stop value during quiet hours - Amps / Voltage / Watts (allows for less runtime during quiet hours, once system is recovered). Stop after the condition is reached for [seconds] (to allow for momentary dips without stopping the running generator). |
Inverter high temperature Inverter overload | Disabled | Use inverter high temperature warning or inverter overload warning to control generator start and stop behaviour. Enable to activate. Start when warning is active for [seconds] (to allow for momentary spikes to pass without triggering start). When warning is cleared stop after [seconds] (to allow for momentary dips without stopping the running generator). On inverter overload warning it also allows to skip generator warm-up. |
Tank level | Disabled | Use the tank level to control generator start and stop behaviour. Enable to activate. Stop when Tank level is lower than threshold. Prevent start until Tank level is higher than threshold. Trigger warning when the generator is stopped. |
Periodic run | Disabled | Enable - No / Yes Run interval [days] Skip run if has been running for: Start always, 1, 2, 4, 6, 8, 10 hours. Run interval start [date] Start time [hh:mm] Run duration (hh:mm) Run until battery is fully charged. Default is disabled. |
Settings → Devices → Genset → Settings | ||
Conditions | Submenu - see above. | |
Minimum run time | 0m | Defines a minimum run time in minutes. |
Detect generator at AC input | Disabled | When enabled, the system will trigger an alarm if no power from the generator is detected at the selected inverter AC input. Ensure that the correct AC input is assigned to “Generator” in the system setup. |
Alarm when generator is not in autostart mode | Disabled | When enabled, an alarm will trigger if the autostart function remains disabled for more than 10 minutes. |
Quiet hours | Disabled | Quiet hours will prevent normal generator run conditions from starting the generator. It is possible for some settings to specify override values to the quiet hours (an extremely low battery voltage trigger to prevent a system shutdown for example). |
Warm-up & cool-down | ||
Warm-up time | 60 | Sets the delay time for generator warm-up via relay control before it is connected to the system. During this time, the AC input relay remains open and the inverter/charger is not yet connected. |
Cool-down time | 180 | Sets the delay time after the generator is disconnected from the system, allowing it to cool down before shutting off. The AC input relay remains open during this period. |
Generator stop time | 0 | |
Settings → Devices → Genset → Run time and service | ||
Generator total run time (hours) | Hours | Displays the total number of hours the generator has operated. |
Daily run time | Submenu displaying the daily run time for the last 30 days. | |
Reset daily run time counters | Provides an option to reset the generator’s run time counters. This is useful after generator replacement, major repairs, or when the counters are used for service tracking. | |
Runtime until service | Hours | Displays the remaining run time before the next scheduled service. Enter the desired service interval in hours. |
Generator service interval | Hours | Sets the generator service interval in hours. Determines how often maintenance is required based on run time. If not set, the Runtime until service item is hidden. |
Reset service timer | Press to reset the service timer after the service is complete. | |
Settings → Devices → Tank pump - Configure automatic pump start/stop based on tank level (sender) information. | ||
Pump state | - | Indicates whether the pump is currently running or stopped. |
Mode | Auto | Defines the pump control mode. Options are Auto, On, and Off. This acts as a manual override when a tank sensor is connected and start/stop levels are defined. |
Tank Sensor | No tank sensor | Select the tank sensor used to trigger the pump. If no sensor is connected or detected, “No tank sensor” will be shown. |
Start level | 50% | Defines the tank level at which the pump will start (relay closes). When the measured level falls below this value, the pump is activated. |
Stop level | 80% | Defines the tank level at which the pump will stop (relay opens). When the measured level rises above this value, the pump is deactivated. |
Settings → Devices → Shelly | ||
AC Phase [L1..L3] | Displays the voltage (V), current (A) and power (W) per phase | |
AC Totals | Displays the combined power (W) and energy (kWh) across all phases | |
Energy [L1..L3] | Displays the imported (consumed) energy in kWh for each phase | |
Reversed Energy [L1..L3] | Displays the exported (generated/fed-back) energy in kWh for each phase | |
Setup | Submenu to configure the device role (e.g. Grid meter, PV inverter, AC load, Genset), its position in the system, and the phase assignment | |
Outputs | Submenu to configure each output channel: assign a name and group, select switch type, set the function, and enable or disable the show controls option | |
Device | Displays product name, firmware version, connection details, and other device information used for diagnostics | |
9.2. Battery state of charge (SoC)
9.2.1. Which device should I use for SoC calculation?
The GX device does not calculate State of Charge (SoC); it simply displays SoC values received from other devices.
There are three product types that can calculate SoC:
Battery Monitors, such as the BMVs, SmartShunt, Lynx Shunt VE.Can, Lynx Smart BMS or the Lynx Ion BMS
Multi and Quattro inverter/chargers
Batteries with a built-in battery monitor, typically connected via BMS-Can (e.g. BYD, Freedom Won)
When to use which?
Battery with built-in monitor (e.g. BYD, Freedom Won): → Use the battery’s SoC. This is the most accurate and preferred source.
Inverter/charger-only systems: → If the Multi or Quattro is the sole source of charging and discharging, it can reliably calculate SoC, no external battery monitor needed.
Systems with inverter/charger, MPPTs with GX device communication: → Still no need for a separate battery monitor, as the GX device aggregates data from the Victron components for accurate SoC. However, the accuracy of the SOC is improved if a dedicated battery monitor (e.g. BMV, SmartShunt, Lynx Shunt) is installed.
All other systems (e.g. boats, RVs with DC lights, additional DC loads/chargers): A dedicated battery monitor is required (e.g. BMV, SmartShunt, or Lynx Shunt VE.Can) to ensure accurate SoC tracking.
9.2.2. Notes on SoC
The State of Charge (SoC) is primarily used to inform the user and is not essential for system operation or charging behaviour.
⚠️ SoC is not used for battery charging control, but is required if a generator is configured to start/stop automatically based on SoC.
More information:
VRM Portal FAQ - difference between BMV SOC and VE.Bus SOC
See Configurable Parameters Section on Battery monitor selection and Has DC system.
9.2.3. Selecting SoC source
The State of Charge (SoC) source can be selected under: Settings → System Setup → Batteries → Battery monitor. The selected source determines which SoC value is displayed on the Overview screen of your GX device. Automatic mode When Automatic is selected, the system follows this logic: In the same image we have chosen the Automatic setting. When automatic is selected, the System setup screen will be as shown in the next image. The 'Automatic' function uses the following logic:
When to Use ‘No Battery Monitor’ Select No battery monitor in systems where:
9.2.4. Details on VE.Bus SOC
While the inverter/charger is in Bulk, the State of Charge (SoC) will not exceed the value set in VEConfigure under: General tab → State of charge when Bulk finished (default: 85%).
In systems with solar chargers, ensure that the absorption voltage set in the MPPT is slightly higher than the setting in the inverter/charger. This allows the inverter/charger to detect the transition to Absorption, which is required for SoC to increase beyond the Bulk limit.
⚠️ If the inverter/charger does not detect Absorption, the SoC will remain fixed at the configured End-of-Bulk percentage (default: 85%).
9.2.5. The System Status menu
The System Status menu (Settings → System Setup → System Status) provides diagnostic flags to help identify system behaviour and potential issues. ⚠️ This menu is read-only and cannot be used to configure settings. It is only visible for Access level Superuser, and the visibility and state of each flag depend on the system configuration and connected devices. |
Diagnostic flags explained
Synchronise VE.Bus SoC with battery:
If On, it indicates that the Multi/Quattro’s internal battery monitor is automatically syncing its SoC with a more accurate source—such as a BMV, SmartShunt, or BMS.
Use solar charger current to improve VE.Bus SoC:
In a VE.Bus system without a dedicated battery monitor, but with Victron solar chargers, the GX device factors in solar charge current to improve the SoC calculation by the Multi/Quattro.
Solar charger voltage control:
The solar chargers are not using their internal charge algorithm, but are instead following an external voltage setpoint, either from a managed battery or, in ESS systems, from the Multi/Quattro.
Solar charger current control:
The system is limiting solar charger output current, based on:
A managed battery, or
A user-defined maximum charge current set under DVCC
BMS control:
The charge voltage is being controlled by the BMS, overriding the absorption and float voltages configured in the inverter/charger or solar charger.
9.3. LEDs and Push-button
9.3.1. LEDs
The Nucleo GX has two status LEDs on the side of the device, indicating the state of the WiFi Access Point and Bluetooth.
Boot-up sequence
LED behaviour during boot-up depends on whether WiFi Access Point and Bluetooth were enabled prior to startup:
Stage 1: Both LEDs off for ~4 seconds
Stage 2: Wifi Access Point LED starts blinking red for ~40 seconds
Stage 3: Wifi Access Point LED starts blinking green for ~10 seconds (or remains off if Access Point is disabled)
Stage 4: Bluetooth LED blinks blue (or remains off if Bluetooth is disabled)
During operation
Wifi Access Point LED blinks red: built-in WiFi Access Point disabled
Wifi Access Point blinks green: built-in WiFi access point enabled (default)
Bluetooth LED off: Bluetooth disabled
Bluetooth LED blinks blue: Bluetooth enabled
Bluetooth LED solid blue: Bluetooth connection to VictronConnect app established
Disable LEDs
The LEDs can be deactivated via the Remote Console. To do so, go to Settings → General → Enable status LEDs.
9.3.2. Small recessed button above the Power in terminal block
This button controls the WiFi Access Point, Bluetooth, and network reset functions.
Short press: Toggle WiFi Access Point and Bluetooth
Toggles both the internal WiFi Access Point and Bluetooth on/off
LED indicators:
WiFi Access Point LED blinks red + Bluetooth LED off → Both disabled
WiFi Access Point LED blinks green + Bluetooth LED blinks blue → Both enabled
Long press: Reset all network settings and the Bluetooth PIN code to factory defaults
Press and hold for at least 4 seconds
Release when the WiFi Access Point LED blinks green rapidly
LEDs stay on for 2 seconds to confirm the action
Press and hold the small button for a minimum of four seconds. The LEDs will stay on for 2 seconds to indicate that the long press has been recognised; then release the button as soon as the Wifi Access Point LED blinks green quickly.
This resets:
Ethernet to DHCP
Enables WiFi Access Point
Disables Remote Console password
Enables Remote Console on LAN and VRM
Resets Bluetooth PIN code:
For GX devices with serial < HQ2242 → Default PIN: 000000
For GX devices with serial ≥ HQ2242 → 6-digit PIN printed on device label (on the back of the GX device)
Note
⚠️ After resetting, power cycle the GX device (disconnect and reconnect power) to re-enable Bluetooth and WiFi Access Point.