Opportunity Loads increases self-consumption by automatically directing surplus solar energy to flexible AC loads. When the battery is sufficiently charged and PV production exceeds household consumption, the GX device acts as a system-level energy coordinator and activates, adjusts, or disables controllable loads based on the currently available surplus — rather than curtailing production or exporting energy to the grid with little financial benefit.

The feature currently supports two types of controllable devices: Victron EV Charging Stations (EVCS) and Shelly smart relays. These can be used individually or in combination, and are controlled in a coordinated fashion to avoid competing for the same available surplus energy.

Unlike timer- or schedule-based automation, Opportunity Loads reacts continuously to real-time conditions: PV production, battery state, household consumption, and available inverter capacity.

A centralised approach allows surplus energy to be distributed intelligently across multiple devices (e.g. several EV charging stations and Shelly-controlled loads), avoiding the instability that results from independent surplus controllers competing for the same available energy.

Typical use cases include EV charging, water heating, thermal storage, pool pumps, and other non-critical AC loads that can operate flexibly without compromising comfort.

The feature is particularly well-suited to ESS installations, marine and RV systems, remote off-grid installations, and any system with export limitations or low feed-in compensation.

Opportunity_Loads_Cover.png

18.2. System requirements

GX device

One of the following GX devices is required, running Venus OS v3.80 or newer:

  • Ekrano GX

  • Cerbo GX

  • Nucleo GX

  • MultiPlus-II GX

  • EasySolar-II GX

Note

Opportunity Loads is only available in the New UI. The Classic UI is not supported.

Inverter/charger system

One of the following inverter/charger platforms is required:

  • MultiPlus / MultiPlus-II

  • Quattro / Quattro-II

  • Multi RS / Multi RS Solar

  • Multi RS19 / Multi HS19

Battery system

A battery system with one of the following monitoring options is required:

  • Victron Lynx Smart BMS

  • Victron VE.Bus BMS

  • Victron SmartShunt or BMV Smart (via VE.Direct)

  • Supported third-party BMS (via CAN bus)

Photovoltaic (PV) system

Both AC-coupled and DC-coupled PV systems are supported. Supported PV sources include:

  • Victron MPPT solar chargers (VE.Direct or VE.Can connected)

  • Multi RS Solar (in PV inverter mode)

  • Third-party AC PV inverters monitored via SunSpec (Ethernet) or a Victron energy meter (e.g. VM-3P75CT)

Note

Monitoring of all PV production is required for correct operation.

Supported load types

Opportunity Loads controls AC loads only. DC loads are not supported.

  • Victron Energy devices:

    • EV Charging Station, EV Charging Station NS

    • EV Charging Station V2, EV Charging Station NS V2

  • Shelly devices:

    Shelly devices (Gen2+ with relay control and energy measurement):

    • Shelly Plus Plug S

    • Shelly Plug S MTR Gen3

    • Shelly Mini 1PM Gen4

    • Shelly 1PM Gen3/Gen4

    • Shelly Pro 1PM

    • Shelly Pro 4PM

    Notice

    This is not an exclusive list, more devices are supported. However, those listed are known to work.

    Additional devices may be supported in future Venus OS releases.

18.3. Configuration

This chapter describes how to enable and configure Opportunity Loads and controllable devices on a GX device.

18.3.1. Configuring Opportunity Loads Preferences

Navigate to: Settings → System Setup → Opportunity Loads → Preferences

screenshot_2_2.png

Pause if no AC input is connected

When enabled, Opportunity Loads pauses whenever no AC input source is connected. This is useful for backup systems where only essential loads should remain active during grid outages. When disabled (the default), controlled loads are shed as much as possible on AC input loss to support system stability; after approximately one minute, Opportunity Loads may resume if sufficient surplus is available.

Nominal inverter utilisation limit

Defines the maximum continuous power level the inverter/charger should plan for when serving both base loads and controlled loads. The base load is deducted from this value; Opportunity Loads then enables additional loads up to the remaining headroom. AC-PV is always utilised up to 100% regardless of this setting.

This helps avoid inverter overload, maintains headroom for sudden consumption peaks, and improves stability during fluctuating PV conditions. In grid-tied systems, it does not restrict the inverter's ability to export to the grid.

Example: With an 80% limit on a 6,500 W system, the algorithm plans for a maximum of 5.2 kW. At a 2 kW base load, up to 3.2 kW is available for controlled loads. With an additional 4 kW of AC-PV present, up to 7.2 kW becomes available for Opportunity Loads.

Pause after several days without full charge

Relevant for ESS systems when using Optimzed with BatteryLife. When BatteryLife's active SoC limit is reached, Opportunity Loads pauses to give battery charging priority and improve the likelihood of the battery recovering to a healthy SoC. Operation automatically resumes after a full charge.

18.3.2. Arranging Device Priorities

Navigate to: Settings → System Setup → Opportunity Loads

screenshot_2_3.png

When multiple controllable loads are configured, priorities determine how surplus energy is distributed. Devices are arranged in a priority list (top = highest), adjustable via the up/down buttons in the Opportunity Loads overview.

Priority relative to the battery

Each load is positioned either above or below the battery in the priority list:

  • Above the battery: the load may activate as soon as sufficient PV surplus is available, even while the battery is still charging. Suitable for loads that should preferentially consume available solar energy.

  • Below the battery: the load activates only after battery charging requirements are satisfied and additional surplus remains available.

Priority-Aware Best Fit

If the available surplus is insufficient for the highest-priority load, the system may temporarily activate a smaller lower-priority load instead. Once enough surplus becomes available for the higher-priority load, the system switches preference back — potentially turning off the lower-priority load. This ensures surplus energy is never left unused while still preferring higher-priority loads whenever conditions allow.

Example: A 3,000 W load has higher priority but only 1,200 W surplus is available. A lower-priority 1,000 W load runs temporarily. When surplus rises to 3,000 W, the system switches to the higher-priority load.

Multiple loads can also run simultaneously when sufficient surplus is available. The GX device continuously rebalances active loads as conditions change.

18.3.3. Configuring Battery-related Settings

Navigate to: Settings → System Setup → Opportunity Loads → Battery

screenshot_2_4.png

Activate following loads when battery reaches

Defines the SoC threshold from which lower-priority loads (placed below the battery) may begin using surplus solar energy. Below this threshold, only loads placed above the battery will run; all other available solar is used to charge the battery.

Note

If PV production exceeds the battery's charging capability, Opportunity Loads may activate lower-priority loads even below the configured SoC threshold. This requires a compatible battery monitor reporting the real-time charge current limit.

Reserve for battery charging

Two reserve power values can be configured — one at or above the SoC threshold set in Activate following loads when batterxy reaches and one at 100% SoC. Between these two points, the reserved charging power is adjusted gradually, giving the battery higher priority at lower SoC levels and making more surplus available for Opportunity Loads as the SoC rises.

Example: Reserve 2,000 W at 80% SoC, and 100 W at 100% SoC. This maintains healthy charging behaviour, ensures the battery reaches full charge regularly, and maximises solar utilisation at high SoC levels.

18.4. EV Charging Stations

Victron EV Charging Stations (EVCS) can be configured as Opportunity Loads and will dynamically adjust their charging power based on available solar surplus.

18.4.1. Requirements

If the EVCS was previously connected via the legacy Modbus TCP method, it must first be migrated to the new MQTT integration before use with Opportunity Loads. See EVCS MQTT migration guide for the required firmware and migration guide.

For Opportunity Loads to take control of a charging session, all of the following conditions must be met:

  • The EVCS is connected to the GX device via MQTT pairing

  • Opportunity Loads is enabled

  • The EVCS is set to Auto mode

  • An EV is connected and ready for charging

  • Either Autostart is enabled on the EVCS, or the user has activated Enable charging on the GX device, or pressed Start via the EVCS web interface or VictronConnect

18.4.2. EVCS built-in surplus charging vs. Opportunity Loads

The EVCS has its own built-in surplus charging algorithm that operates independently using metrics from the GX device. Opportunity Loads, by contrast, performs centralised coordination across all configured devices — multiple EVCS units, Shelly loads, and others — preventing independent controllers from competing for the same available energy.

Auto mode source shows which of the two, Internal (EV Charging Station) or External (Opportunity Loads), is currently controlling the charging session.

screenshot_3_2_NEW.png

18.4.3. EVCS configuration

Navigate to: Settings → System Setup → Opportunity Loads → EV Charging Station

screenshot_3_3_1.png

Maximum charging power

Limits the maximum power the EVCS may use as a controlled load, even if more surplus is available. This can reserve surplus for lower-priority loads, improve parallel operation with other Opportunity Loads, and reduce load fluctuations in smaller systems.

Remember detected EV phases

Stores the previously detected EV phase configuration (1-, 2-, or 3-phase) and reuses it for subsequent sessions, reducing phase-detection delays and improving charging start-up behaviour. Recommended only when a single EV is regularly connected, or when all EVs using the station share the same phase configuration. Enabling this setting with vehicles of different phase configurations may prevent some vehicles from charging correctly.

18.5. Shelly devices

Supported Shelly devices can be configured as Opportunity Loads to control fixed AC consumers such as water heaters, pumps, or other flexible loads.

Warning

Installation: Devices connected directly to mains voltage or fixed wiring (e.g. Shelly Pro models) must be installed only by a qualified electrician, in accordance with applicable electrical codes and safety regulations.

Warning

Operation: All connected devices may switch on or off unexpectedly due to the Opportunity Loads algorithm. Improper installation or use may cause electric shock, fire, injury, or damage.

Note

To ensure reliable operation, it is recommended that ECO mode remain disabled on the Shelly device.

18.5.1. Configuration steps

Steps to configure a Shelly device as an Opportunity Load:

  1. Navigate to Settings → Integrations → Shelly Devices and enable the devices.

  2. In the device list, navigate to the Setup section and configure the Position and Phase Setting.

  3. Navigate to the Switches configuration and set the function to Opportunity load.

  4. The device will now appear as a controllable load under Settings → System Setup → Opportunity Loads, where load parameters can be configured.

screenshot_4_1_1.png
screenshot_4_1_2.png

18.5.2. Auto mode and manual overwrite

When a Shelly device is set to Opportunity load, the Switch Pane on the GX device shows a three-state switch (Off / On / Auto). With Auto enabled, the device is controlled automatically based on available surplus, and the On/Off buttons reflect the current state. To override manually, disable Auto and set the desired state with On or Off.

screenshot_4_2.png

Note

A Shelly device with Auto disabled will appear as No control in the Opportunity Loads device priorities list.

18.5.3. Shelly Configuration Parameters

Navigate to: Settings → System Setup → Opportunity Loads → Shelly Device

screenshot_4_3.png

Expected power consumption

The typical power draw of the connected load while active. The GX device uses this value to estimate available surplus capacity, decide when to activate the load, and coordinate parallel operation. For best results, the load should consume close to the configured value when on, and close to 0 W when off.

If the load's consumption varies within a known range, configure the highest expected value. This ensures the load is not switched off prematurely after its minimum run time. Opportunity Loads will refine its estimate during runtime. Avoid loads with strongly unpredictable consumption, as this reduces control accuracy.

Minimum run duration when turned on

The minimum time the load remains active after being switched on. Prevents excessive switching during fluctuating PV production, reduces short operating cycles, and protects connected equipment. Particularly important for loads with compressors, pumps, heating elements, or mechanical switching components.

Minimum rest duration when turned off

The minimum time the load remains off after being switched off. Reduces rapid switching, protects equipment, and stabilises system operation during changing solar conditions.

Recommendation for multiple loads: Configure longer rest durations for lower-priority loads. When solar power decreases, loads are shed starting from the lowest priority. If lower-priority loads use the same rest duration as higher-priority ones, they may become available again too quickly — only to be turned off again shortly afterwards. Staggered rest durations help avoid unnecessary switching.

18.5.4. Recommendation when having multiple controllable devices

For systems with multiple Opportunity Loads, it is recommended to configure longer rest durations for lower-priority loads.

When available solar power decreases, loads are disabled starting with the lowest-priority load. If multiple loads use the same rest duration, a lower-priority load may become available again too quickly, only to be switched off again shortly afterwards when a higher-priority load becomes available again.

Staggered rest durations help avoid unnecessary switching.

18.6. Operation & Monitoring

18.6.1. How the algorithm works

Once configured, operation is fully automatic. The GX device continuously monitors PV production, battery SoC, AC consumption, and configured Opportunity Loads. Based on available surplus and configured priorities, it dynamically activates, adjusts, or disables controlled loads.

The algorithm accounts for AC-coupled and DC-coupled PV, DC-to-AC conversion efficiency, phase balancing, feed-in permissions, and whether the system is grid-connected or off-grid. It processes loads in priority order, applies Priority-Aware Best Fit to avoid wasting surplus, and rebalances active loads automatically as conditions change — for example when cloud cover reduces PV output, a large household load switches on, or battery charging requirements increase.

18.6.2. Behaviour during AC input loss

When the grid or AC generator connection is lost, controlled loads are shed as much as possible to support system stability. After approximately one minute, Opportunity Loads may resume if sufficient surplus is available and system conditions are stable. If Pause Opportunity Loads if no AC input is connected is enabled, loads remain paused until AC input returns.

18.6.3. BatteryLife interaction

In ESS setups using BatteryLife, Opportunity Loads automatically pauses when the active SoC limit reaches 85% (if that preference is enabled) and resumes once the battery has sufficiently charged and BatteryLife lowers the active SoC limit again. This prioritises a full battery charge during periods of poor solar yield.

18.6.4. Daytime control and nighttime release

While PV production is available, Opportunity Loads actively enforces the expected state of controlled devices. If a device is manually switched on externally (e.g. via a Shelly app or physical button) when Opportunity Loads expects it to be off, the system will switch it off again. To take manual control temporarily, disable Auto — Opportunity Loads will release control immediately and not resume until Auto is re-enabled.

During periods without meaningful PV production, Opportunity Loads enters an inactive state and releases control of all devices. This allows devices to follow their own local schedules or configurations overnight — for example, a Shelly-controlled boiler can run a local schedule to reach a target temperature during the night if it was not reached during the day due to poor solar yield.

18.6.5. Battery usage and SoC probing

Opportunity Loads is designed to use surplus solar energy, but brief battery usage can occur — for example when a load cannot be switched off immediately due to its minimum run time, or when PV production drops suddenly. In critical situations (e.g. sudden loss of AC-coupled PV combined with high inverter load), inverter/charger protection mechanisms may enforce immediate load shedding regardless.

SoC probing is used in off-grid and zero-feed-in systems where excess PV cannot be exported. When the battery nears 100% SoC, the system must curtail PV generation, masking the solar array's true output. To determine actual available surplus, Opportunity Loads temporarily allows the battery to discharge to approximately 97% SoC by activating controlled loads. This unthrottles PV, revealing the full available power. The system returns to normal solar-only operation once the SoC decreases.

Notice

SoC probing is not used in grid-connected systems without feed-in restrictions, where excess PV is exported to the grid and the available surplus is directly measurable via the grid meter.

18.6.6. Manual Override

Opportunity Loads can be manually overridden at any time via the GX device New UI or VRM:

  • EV Charging Station: switch to manual charging via the Control Pane

  • Shelly devices: disable Auto mode and control the relay via the Switch Pane

When a manual override is active, the device no longer follows the Opportunity Loads algorithm until automatic control is re-enabled. This allows a load to be operated immediately even when insufficient solar surplus is available.

18.6.7. Monitoring on the GX Device

Configured controllable loads are visible in the Overview page drill-downs alongside other system loads. Tap the AC Loads or Essential Loads tile (the latter appears in some configurations using a grid meter) to see each device's name, current status, and power consumption.

screenshot_5_7_2.png

18.6.8. Monitoring in VRM

Opportunity Loads can be monitored remotely through VRM, including live control of supported devices (EVCS via the Control Pane, Shelly devices via the Switch Pane). Configuration of priorities, battery settings, preferences, and device parameters is only available on the GX device itself or via Remote Console.

VRM also provides:

  • System Overview chart: displays actual and forecasted energy consumption alongside PV production, broken down by category (base load, EV charging, AC loads, heating), helping visualise how solar energy is distributed throughout the day.

  • Consumption dashboard: shows energy consumption by source (solar, battery, grid, generator) over time, allowing users to quantify the improvement in self-consumption and reduction in grid dependency.

Opportunity_Loads_VRM_1.png
Opportunity_Loads_VRM_2.png

18.6.9. Troubleshooting

This chapter describes warnings and error messages that may appear in the system, and what they mean.

System incompatible with Opportunity Loads

This warning appears when one or more of the following conditions are present for longer than 60 seconds:

  • Battery state of charge unavailable: The system does not provide a State of Charge (SoC) value. Opportunity Loads requires a battery with a BMS that reports SoC.

  • System type cannot be determined: Opportunity Loads cannot determine the required system characteristics, such as the phase configuration, grid connection type, or feed-in policy. This may occur when no Inverter/Charger is available.

  • Inverter set to Inverter Only while AC-in loads are present:

    The inverter is configured in Inverter Only mode, but the system reports loads on AC-in. This configuration is not supported.

Note

While the warning is active, Opportunity Loads is paused. Operation resumes automatically when all incompatible conditions have been resolved.

18.6.10. Glossary

Acronym

Meaning

ESS

Energy Storage System

PV

Photovoltaic

SoC

State of Charge

VRM

Victron Remote Management

EVCS

EV Charging Station

GX device

Victron Energy communication centre running Venus OS (e.g. Cerbo GX, Ekrano GX, MultiPlus-II GX, EasySolar-II GX)

Venus OS

Victron Energy operating system for GX devices