Before turning on the system, ensure that chargers and loads are correctly configured, particularly their maximum combined charge and combined discharge currents, to avoid exceeding battery limits.
Maximum charge current
The maximum continuous charge current is 1C. The maximum pulse charging current depends on the battery model. Please refer to the Lithium NG battery datasheet for details.
Tip
For optimal battery performance, a charge current of 0.3C is recommended.
Maximum discharge current
The maximum continuous discharge current is 1C. The maximum pulse discharge current is 2C for a maximum of 10 seconds.
Tip
For optimal battery performance, a discharge current of 0.5C is recommended.
Important
Chargers and loads not controlled by the BMS (via ATC and ATD) can permanently damage the battery.
Maximum battery charge- and discharge currents for 12.8V Lithium NG batteries | ||||
12.8/100 | 12.8/150 | 12.8/200 | 12.8/300 | |
Max continuous discharge current | 100A | 150A | 200A | 300A |
Max pulse discharge current (10s) | 200A | 300A | 400A | 600A |
Max continuous charge current | 100A | 150A | 200A | 300A |
Max pulse charge current (10s) | 200A | 225A | 400A | 450A |
Maximum battery charge- and discharge currents for 25.6V and 51.2V Lithium NG batteries | ||||
25.6/100 | 25.6/200 | 25.6/300 | 51.2/100 | |
Max continuous discharge current | 100A | 200A | 300A | 100A |
Max pulse discharge current (10s) | 200A | 400A | 600A | 200A |
Max continuous charge current | 100A | 200A | 300A | 100A |
Max pulse charge current (10s) | 200A | 400A | 450A | 200A |
The smallBMS NG switches on when the following conditions are met:
Battery connection: The Bat+ and Bat- terminals of the 7-pin terminal block must be connected to Battery Plus and Battery Minus.
Remote on/off wiring:
The wire loop must be placed between Remote L and Remote H of the 7-pin terminal block, or
If a remote on/off switch is used, it must be wired between Remote L and Remote H and switched on.
Once powered up, use the VictronConnect app to configure the BMS settings.
Certain parameters such as Battery capacity, Battery voltage, Number of batteries, Number of batteries in series, Number of batteries in parallel are automatically configured and cannot be changed, but they should still be verified for accuracy.
Battery monitor settings: Unlike other battery monitors, the smallBMS NG has mostly fixed settings that cannot be customised. This is because the smallBMS NG is designed to work exclusively with Victron Lithium NG batteries, where many parameters are predefined based on battery type.
Firmware updates for the BMS and Lithium NG battery are performed via the VictronConnect app.
General notes on firmware updates
Newer isn’t always better – only update if necessary.
If it works, don’t break it – avoid unnecessary updates.
Read the changelog first – available on Victron Professional.
Use this feature with care. Our main advice is not to update a running system unless problems occur or before the first startup.
Notes on updating the smallBMS NG and Lithium NG battery firmware
The firmware update does not cause a full system shutdown.
During the update, the Charge disconnect output opens, preventing battery charging.
If the update fails, the Load disconnect output will open after 120 seconds as a safety measure, allowing time to retry the update.
Updating the firmware via VictronConnect
Please note the following before performing a firmware update via VictronConnect:
Before updating, refer to the firmware update chapter in the VictronConnect manual for detailed instructions.
If a newer firmware version is available, VictronConnect (ensure it’s up to date) will notify you upon connecting to the BMS.