Quattro (with firmware xxxx400 or higher) Australia
5. Configuration
In this section:
Warning
  • Settings may only be changed by a qualified electrical engineer.
  • Read the instructions thoroughly before implementing changes.
  • During setting of the charger, the DC fuse in the battery connections must be removed.
5.1. Standard settings: ready for use
On delivery, the Quattro is set to standard factory values. In general, these settings are selected for single-unit operation. Settings, therefore, do not require changing in the event of stand-alone use.
Warning
Possibly, the standard battery charging voltage is not suitable for your batteries! Refer to the manufacturer's documentation, or to your battery supplier!
Standard Quattro factory settings
Inverter frequency
50 Hz
Input frequency range
45 - 65 Hz
Input voltage range
180 - 265 VAC
Inverter voltage
230 VAC
Stand-alone / parallel / 3-phase
stand-alone
AES (Automatic Economy Switch)
off
Ground relay
on
Charger on / off
on
Charging characteristics
four-stage adaptive with BatterySafe mode
Charging current
75 % of the maximum charging current
Battery type
Victron Gel Deep Discharge (also suitable for Victron AGM Deep Discharge)
Automatic equalisation charging
off
Absorption voltage
14.4 / 28.8 / 57.6 V
Absorption time
up to 8 hours (depending on bulk time)
Float voltage
13.8 / 27.6 / 55.2 V
Storage voltage
13.2 / 26.4 / 52.8 V (not adjustable)
Repeated absorption time
1 hour
Absorption repeat interval
7 days
Bulk protection
on
Generator (AC-in-1) / shore current (AC-in-2)
50 A/16 A (default setting, adjustable current limit for PowerControl and PowerAssist functions)
UPS feature
on
Dynamic current limiter
off
Weak AC
off
Boost factor
2
Programmable relay (3x)
alarm function
PowerAssist
on
Analog/digital input/output ports
programmable
Frequency shift
off
Built-in Battery Monitor
optional
5.2. Explanation of settings
Settings that are not self-explanatory are described briefly below. For further information, please refer to the help files in the software configuration programs (see Section 5.3).
Inverter frequency
Output frequency if no AC is present at the input.
Adjustability: 50 Hz; 60 Hz
Input frequency range accepted by the Quattro. The Quattro synchronises within this range with the voltage present on AC-in-1 (priority input) or AC-in-2. Once synchronised, the output frequency will be equal to the input frequency.
Adjustability: 45 – 65 Hz; 45 – 55 Hz; 55 – 65 Hz
Input voltage range
Voltage range accepted by the Quattro. The Quattro synchronises within this range with the voltage present on AC-in-1 (priority input) or on AC-in-2. After the back feed relay has closed, output voltage will be equal to input voltage.
Lower limit: 180 – 230 V
Upper limit: 230 – 270 V
Note
The standard lower limit setting of 180 V is intended for connection to a weak mains supply, or to a generator with unstable AC output. This setting may result in a system shut down when connected to a “brushless, self excited, externally voltage regulated, synchronous AC generator” (synchronous AVR generator). Most generators rated at 10 kVA or more are synchronous AVR generators. The shut down is initiated when the generator is stopped and revs down while the AVR simultaneously “tries” to keep the output voltage of the generator at 230 V.
The solution is to increase the lower limit setting to 210 VAC (the output of AVR generators is generally very stable), or to disconnect the Quattro from the generator when a generator stop signal is given (with help of an AC contactor installed in series with the generator).
Inverter voltage
Output voltage of the Quattro in battery operation.
Adjustability: 210 – 245 V
Stand-alone / parallel operation / 2-3 phase setting
Using several devices, it is possible to:
  • increase total inverter power (several devices in parallel)
  • create a split-phase system (only for Quattro units with 120 V output voltage)
  • create a 3-phase system.
To this end, the devices must be mutually connected with RJ45 UTP cables. Standard device settings, however, are such that each device operates in stand-alone operation. Reconfiguration of the devices is therefore required.
If this setting is turned “on”, the power consumption in no-load operation and with low loads is decreased by approx. 20 %, by slightly “narrowing” the sinusoidal voltage. Not adjustable with DIP switches. Applicable in stand-alone configuration only.
Search mode
Instead of the AES mode, the search mode can also be chosen (with help of VEConfigure only). If search mode is “on”, the power consumption in no-load operation is decreased by approx. 70 %. In this mode the Quattro, when operating in inverter mode, is switched off in case of no load or very low load, and switches on every two seconds for a short period. If the output current exceeds a set level, the inverter will continue to operate. If not, the inverter will shut down again.
The Search Mode “shut down” and “remain on” load levels can be set with VEConfigure.
The standard settings are:
  • Shut down: 40 Watt (linear load)
  • Turn on: 100 Watt (linear load)
Ground relay (see appendix B)
With this relay (E) the neutral conductor of the AC output is grounded to the casing when the back feed safety relays in the AC-in-1 and the AC-in-2 inputs are open. This ensures the correct operation of earth leakage circuit breakers in the outputs.
  • If a non-grounded output is required during inverter operation, this function must be turned off. (See also Section 4.5)
  • If required an external ground relay can be connected (for a split-phase system with a separate autotransformer). See appendix A.
The standard setting is “Four-stage adaptive with BatterySafe mode”. See Section 2 for a description. This is the best charging characteristic. See the help files in the software configuration programs for other features. “Fixed” mode can be selected with DIP switches.
Battery type
The standard setting is the most suitable for Victron Gel Deep Discharge, Gel Exide A200, and tubular plate stationary batteries (OPzS). This setting can also be used for many other batteries: e.g. Victron AGM Deep Discharge and other AGM batteries, and many types of flat-plate open batteries. Four charging voltages can be set with DIP switches.
This setting is intended for tubular plate traction batteries. During absorption the voltage limit increases to 2,83 V/cell (34 V for a 24 V battery) once the charge current has tapered down to less than 10 % of the set maximum current.
See “tubular plate traction battery charge curve” in VEConfigure.
Absorption time
This depends on the bulk time (adaptive charging characteristic), so that the battery is optimally charged. If the “fixed” charging characteristic is selected, the absorption time is fixed. For most batteries, a maximum absorption time of eight hours is suitable. If an extra high absorption voltage is selected for rapid charging (only possible for open, flooded batteries!), four hours is preferable. With DIP switches, a time of eight or four hours can be set. For the adaptive charging characteristic, this determines the maximum absorption time.
Storage voltage, Repeated Absorption Time, Absorption Repeat Interval
See Section 2. Not adjustable with DIP switches.
Bulk Protection
When this setting is “on”, the bulk charging time is limited to 10 hours. A longer charging time could indicate a system error (e.g. a battery cell short-circuit). Not adjustable with DIP switches.
AC input current limit AC-in-1 (generator) and AC-in-2 (shore/grid supply)
Model
12/5000/220
24/5000/120
48/5000/120
24/8000/200
48/8000/110
48/10000/140
48/15000/200
PowerAssist setting range
4 A - 100 A
11 A - 100 A
11 A - 100 A
15 A - 100 A
Factory setting: 50 A for AC1 and 16 A for AC2.
In case of parallel units the minimum and maximum values have to be multiplied by the number of parallel units.
UPS feature
If this setting is “on” and AC on the input fails, the Quattro switches to inverter operation practically without interruption. The Quattro can then be used as an Uninterruptible Power Supply (UPS) for sensitive equipment such as computers or communication systems.
The output voltage of some small generating sets is too unstable and distorted for using this setting – the Quattro would continually switch to inverter operation. For this reason, the setting can be turned off. The Quattro will then respond less quickly to voltage deviations on AC-in-1 or AC-in-2. The switchover time to inverter operation is consequently slightly longer, but most equipment (computers, clocks or household equipment) is not adversely impacted.
Recommendation: Turn the UPS feature off if the Quattro fails to synchronise, or continually switches back to inverter operation.
Intended for generators, the AC voltage being generated by means of a static inverter (so-called “inverter” generators). In these generators, rotational speed is down-controlled if the load is low: this reduces noise, fuel consumption and pollution. A disadvantage is that the output voltage will drop severely or even completely fail in the event of a sudden load increase. More load can only be supplied after the engine is up to speed.
If this setting is “on”, the Quattro will start supplying extra power at a low generator output level and gradually allow the generator to supply more, until the set current limit is reached. This allows the generator engine to get up to speed. This setting is also often used for “classical” generators that respond slowly to sudden load variation.
WeakAC
Strong distortion of the input voltage can result in the charger hardly operating or not operating at all. If WeakAC is set, the charger will also accept a strongly distorted voltage, at the cost of greater distortion of the input current.
Recommendation: Turn WeakAC on if the charger is hardly charging or not charging at all (which is quite rare!). Also turn on the dynamic current limiter simultaneously, and reduce the maximum charging current to prevent overloading the generator if necessary.
Note
When WeakAC is on, the maximum charge current is reduced by approximately 20 %.
BoostFactor
Change this setting only after consulting with Victron Energy or with an engineer trained by Victron Energy! Not adjustable with DIP switches.
Three programmable relays
The Quattro is equipped with 3 programmable relays. The relays can be programmed for all kinds of other applications, for example as a starter relay for a generating set. The default setting of the relay in position I (see appendix A, upper right corner) is “alarm”. Not adjustable with DIP switches.
Two programmable analog/digital input/output ports
The Quattro is equipped with 2 analog/digital input/output ports.
These ports can be used for several purposes. One application is communication with the BMS of a lithium-ion battery.
Frequency shift
When solar inverters are connected to the output of a Quattro, the excess solar energy is used to recharge the batteries. Once the absorption voltage is reached, the Quattro will shut down the solar inverter by shifting the output frequency 1 Hz (from 50 Hz to 51 Hz for example). Once battery voltage has dropped slightly, the frequency returns to normal and the solar inverters will restart. Not adjustable with DIP switches.
Built-in Battery Monitor (optional)
The ideal solution when Quattro units are part of a hybrid system (diesel generator, inverter/chargers, storage battery, and alternative energy). The built-in battery monitor can be set to start and stop the generator:
  • Start at a preset % discharge level, and/or
  • start (with a preset delay) at a preset battery voltage, and/or
  • start (with a preset delay) at a preset load level.
  • Stop at a preset battery voltage, or
  • stop (with a preset delay) after the bulk charge phase has been completed, and/or
  • stop (with a preset delay) at a preset load level.
5.3. Configuration by computer
All settings can be changed by means of a computer.
The most common settings can be changed by means of DIP switches (see Section 5.5).
Note
This manual is intended for products with firmware xxxx400 or higher (with x any number)
The firmware number can be found on the microprocessor, after removing the front panel.
It is possible to update older units, as long as that same 7 digit number starts with either 26 or 27. When it starts with 19 or 20 you have an old microprocessor and it is not possible to update to 400 or higher.
For changing settings with the computer, the following is required:
5.3.1. VE.Bus Quick Configure Setup
VE.Bus Quick Configure Setup is a software program with which systems with a maximum of three Quattro units (parallel or three phase operation) can be configured in a simple manner. VEConfigureII forms part of this program. The software can be downloaded free of charge at www.victronenergy.com .
For connection to the computer, a RJ45 UTP cable and the MK3-USB interface is required.
5.3.2. VE.Bus System Configurator
For configuring advanced applications and/or systems with four or more Quattro units, VE.Bus System Configurator software must be used. The software can be downloaded free of charge at www.victronenergy.com . VEConfigureII forms part of this program.
5.4. Configuration with a VE.Net panel
To this end, a VE.Net panel and the VE.Net to VE.Bus converter is required.
With VE.Net all parameters are accessible, with the exception of the multi-functional relay and the VirtualSwitch.
5.5. Configuration with DIP switches
Introduction
A number of settings can be changed using DIP switches (see appendix A, position M).
Note
When changing settings with dipswitches in a parallel or split-phase/3-phase system one should be aware that not all settings are relevant on all Quattro units. This because some settings will be dictated by the Master or Leader. Some settings are only relevant in the Master/Leader (ie they are not relevant in a slave or in a follower). Other settings are not relevant for slaves but are relevant for followers.
A note on used terminology:
A system in which more than one Quattro is used to create a single AC phase is called a parallel system. In this case one of the Quattro units will control the whole phase, this one is called the master. The others, called slaves, will just listen to the master to determine their action.
It is also possible to create more AC phases (split-phase or 3-phase) with 2 or 3 Quattro units. In this case the Quattro in Phase L1 is called the Leader. The Quattro in phase L2 (and L3 if available) will generate the same AC frequency but will follow L1 with a fixed phase shift. These Quattro units are called followers.
If more Quattro units are used per phase in a split-phase or 3-phase system (for instance 6 Quattro units are used to build a 3-phase system with 2 Quattro units per phase) then the Leader of the system is also the Master of phase L1. The Followers in phase L2 and L3 will also take the Master role in phase L2 and L3. All others will be slaves.
Setting up parallel or split-phase/3-phase systems should be done by software, see paragraph 5.3.
Tip
If you don’t want to bother about a Quattro being a master/slave/follower then the easiest and most straight forward way is to set all settings identically on all Quattro units.
General procedure:
Turn the Quattro on, preferably unloaded and without AC voltage on the inputs. The Quattro will then operate in inverter mode.
  1. Set the DIP switched for:
    -The required current limitation of the AC input - (not relevant for slaves).
    -Limitation of the charging current - (only relevant for Master/Leader).
    Press the 'Up' button for 2 seconds (upper button to the right of the DIP switches, see appendix A, position K) to store the settings after the required values have been set. You can now re-use the DIP switches to apply the remaining settings (step 2).
  2. Other settings, set the dipswitches for:
    -Charge voltages - (only relevant for Master/Leader)
    -Absorption time - (only relevant for Master/Leader)
    -Adaptive charging - (only relevant for Master/Leader)
    -Dynamic current limiter - (only relevant for Slaves)
    -UPS function - (only relevant for Slaves)
    -converter voltage - (only relevant for Slaves)
    -converter frequency - (only relevant for Master/Leader)
    Press the “Down” button for 2 seconds (lower button to the right of the DIP switches) to store the settings after the dipswitches have been set in the correct position. You can now leave the DIP switches in the selected positions, so that the “other settings” can always be recovered.
Note
The DIP switch functions are described in 'top to bottom' order. Since the uppermost DIP switch has the highest number (8), descriptions start with the switch numbered 8.
5.5.1. Detailed instructions
Step 1
  1. Current limitation AC inputs (default: AC-in-1: 50 A, AC-in-2: 16 A)
    If the current demand (Quattro load + battery charger) threatens to exceed the set current, the Quattro will first reduce its charging current (PowerControl), and subsequently supply additional power from the battery (PowerAssist), if needed.
    The AC-in-1 current limit (the generator) can be set to eight different values by means of DIP switches. The AC-in-2 current limit can be set to two different values by means of DIP switches. With a Multi Control Panel, a variable current limit can be set for the AC-in-2 input.
    Procedure
    AC-in-1 can be set using DIP switches ds8, ds7 and ds6 (default setting: 50A). Procedure: set the DIP switches to the required value:
    ds8
    ds7
    ds6
    off
    off
    off
    6,3 A (PowerAssist 11 A, PowerControl 6 A)
    off
    off
    on
    10 A (PowerAssist 11 A, PowerControl 10 A)
    off
    on
    off
    12 A (2.8 kVA at 230 V)
    off
    on
    on
    16 A (3.7 kVA at 230 V)
    on
    off
    off
    20 A (4.6 kVA at 230 V)
    on
    off
    on
    25 A (5,7 kVA at 230 V)
    on
    on
    off
    30 A (6,9 kVA at 230 V)
    on
    on
    on
    50 A (11,5 kVA at 230 V)
    More than 50 A: use VEConfigure software
    Note
    Manufacturer-specified continuous power ratings for small generators are sometimes inclined to be rather optimistic. In that case, the current limit should be set to a much lower value than would otherwise be required on the basis of manufacturer-specified data.
    AC-in-2 can be set in two steps using DIP switch ds5 (default setting: 16 A). Procedure: set ds5 to the required value:
    ds5
    AC input 2 current
    off
    16A
    on
    30A
    More than 30 A: use VEConfigure software or Digital Multi Control Panel
  2. Charge current limitation (default setting 75 %)
    For maximum battery life, a charge current of 10 % to 20 % of the capacity in Ah should be applied.
    Example: optimal charge current of a 24 V/500 Ah battery bank: 50 A to 100 A.
    The temperature sensor automatically adjusts the charging voltage to the battery temperature.
    If faster charging – and a subsequent higher current – is required:
    - the temperature sensor should be fitted to the battery, since fast charging can lead to a considerable temperature rise of the battery bank. The charging voltage is adapted to the higher temperature (i.e. lowered) by means of the temperature sensor.
    - the bulk charging time will sometimes be so short that a fixed absorption time would be more satisfactory (“fixed” absorption time, see ds5, step 2).
    Note
    The temperature sensor is not supplied with 48V models.
    It can be ordered separately. Order number: ASS000001000
    Procedure
    The battery charging current can be set in four steps, using DIP switches ds4 and ds3 (default setting: 75 %).
    ds4
    ds3
    % of battery capacity
    off
    off
    25%
    off
    on
    50%
    on
    off
    75%
    on
    on
    100%
    Note
    When WeakAC is on, the maximum charge current is reduced from 100 % to approximately 80 %.
  3. DIP switches ds2 and ds1 are not used during step 1.
    Note
    IMPORTANT If the last 3 digits of the Quattro firmware is in the 100 range (so the firmware number is xxxx1xx (with x any number)) then ds1 & ds2 are used to set a Quattro in stand-alone, parallel or three-phase. Please consult the appropriate manual.
  4. Examples of settings:
    ds8 AC-In-1
    on
    ds7 AC-In-1
    on
    ds6 AC-In-1
    on
    ds5 AC-In-2
    on
    ds4 Charging current
    on
    ds3 Charging current
    off
    ds2 Stand-alone
    off
    ds1 Stand-alone
    off
    ds8
    on
    ds7
    on
    ds6
    on
    ds5
    off
    ds4
    on
    ds3
    on
    ds2
    off
    ds1
    off
    ds8
    off
    ds7
    on
    ds6
    on
    ds5
    off
    ds4
    on
    ds3
    on
    ds2
    off
    ds1
    off
    ds8
    on
    ds7
    on
    ds6
    off
    ds5
    on
    ds4
    off
    ds3
    on
    ds2
    off
    ds1
    off
    Step 1, stand-alone
    Example 1 (factory setting):
    ds8, ds7, ds6 AC-In-1: 50 A
    ds5 AC-In-2: 30 A
    ds4, ds3 Charge current: 75%
    ds2, ds1 Stand-alone mode
    Step 1, stand-alone
    Example 2:
    ds5 AC-In-2: 16 A
    ds4, ds3 Charge: 100%
    Step 1, stand-alone
    Example 3:
    ds8, ds7, ds6 AC-In-1: 16 A
    ds5 AC-In-2: 16 A
    Step 1, stand-alone
    Example 4:
    ds8, ds7, ds6 AC-In-1: 30 A
    ds5 AC-In-2: 30 A
    ds4, ds3 Charge: 50%
    To store the settings after the required values have been set: press the “Up” button for 2 seconds (upper button to the right of the DIP switches, see appendix A, position K). The overload and low-battery LED’s will flash to indicate acceptance of the settings.
    We recommend making a note of the settings, and filing this information in a safe place.
The DIP switches can now be used to apply the remaining settings (step 2).
Step 2
  1. Other settings
    The remaining settings are not relevant for slave units.
    Some of the remaining settings are not relevant for followers (L2, L3). These settings are imposed on the whole system by the leader L1. If a setting is irrelevant for L2, L3 devices, this is mentioned explicitly.
    ds8-ds7: Setting charging voltages (not relevant for L2, L3).
    ds8
    ds7
    Absoption voltage
    Float voltage
    Storage voltage
    Suitable for
    off
    off
    14.1
    28.2
    56.4
    13.8
    27.6
    55.2
    13.2
    26.4
    52.8
    Gel Victron Long Life (OPzV)
    Gel Exide A600 (OPzV)
    Gel MK battery
    off
    on
    14.4
    28.8
    57.6
    13.8
    27.6
    55.2
    13.2
    26.4
    52.8
    Gel Victron Deep Discharge
    Gel Exide A200
    AGM Victron Deep Discharge
    Stationary tubular plate (OPzS)
    on
    off
    14.7
    29.4
    58.8
    13.8
    27.6
    55.2
    13.2
    26.4
    52.8
    Tubular plate (OPzS) batteries in semi-float mode
    AGM spiral cell
    on
    on
    15.0
    30.0
    60.0
    13.8
    27.6
    55.2
    13.2
    26.4
    52.8
    Tubular plate (OPzS) batteries in cyclic mode
    ds6: absorption time 8 or 4 hours (not relevant for L2, L3).
    ds6
    Absorption time
    off
    4 hours
    on
    8 hours
    ds5: adaptive charging characteristic (not relevant for L2, L3).
    ds5
    Adaptive charging charactaristic
    off
    Inactive (fixed absorption time)
    on
    Active
    ds4: dynamic current limiter
    ds4
    off
    Inactive
    on
    Active
    ds3: UPS function
    ds3
    UPS function
    off
    on
    Active
    ds2: converter voltage
    ds2
    Converter voltage
    off
    240 V / 115 V
    on
    230 V / 120 V
    ds1: converter frequency (not relevant for L2, L3). (the wide input frequency range (45-55 Hz) is 'on' by default)
    ds1
    Converter frequency
    off
    60 Hz
    on
    50 Hz
    Note
    • If “adaptive charging algorithm” is on, ds6 sets the maximum absorption time to 8 hours or 4 hours.
    • If “adaptive charging algorithm” is off, the absorption time is set to 8 hours or 4 hours (fixed) by ds6.
  2. Exemplary settings
    Example 1 is the factory setting (since factory settings are entered by computer, all DIP switches of a new product are set to “off” and do not reflect the actual settings in the microprocessor).
    ds8 Charge voltage
    off
    ds7 Charge voltage
    on
    ds6 Absorption time
    on
    ds5 Adaptive charge
    on
    ds4 Dyn. Curr. Limit
    off
    ds3 UPS function
    on
    ds2 Voltage
    on
    ds1 Frequency
    on
    ds8
    off
    ds7
    off
    ds6
    on
    ds5
    on
    ds4
    off
    ds3
    off
    ds2
    on
    ds1
    on
    ds8
    on
    ds7
    off
    ds6
    on
    ds5
    on
    ds4
    on
    ds3
    off
    ds2
    off
    ds1
    on
    ds8
    on
    ds7
    on
    ds6
    off
    ds5
    off
    ds4
    off
    ds3
    on
    ds2
    off
    ds1
    off
    Step 2
    ds8, ds7 GEL 14.4 V
    ds6 Absorption time: 8 hours
    ds5 Adaptive charging: on
    ds4 Dyn. Curr. Limit: off
    ds3 UPS function: on
    ds2 Voltage: 230 V
    ds1 Frequency: 50 Hz
    Step 2
    Example 2:
    ds8, ds7 GEL 14.1 V
    ds3 UPS function: off
    ds2 Voltage: 230 V
    Step 2
    Example 3:
    ds8, ds7 AGM 14.7 V
    ds4 Dyn. Curr. Limit: on
    ds2 Voltage: 240 V
    Step 2
    Example 4:
    ds8, ds7 Tubular plate 15 V
    ds6 Absorption time: 4 h
    ds5 Fixed absorption time
    ds2 Voltage: 240 V
    ds1 Frequency: 60 Hz
    To store the settings after the required values have been set: press the 'Down' button for 2 seconds (lower button to the right of the DIP switches). The temperature and low-battery LEDs will flash to indicate acceptance of the settings.
    The DIP switches can be left in the selected positions, so that the “other settings” can always be recovered.