Manuel du compteur d’énergie VM-3P5A Victron
9. Annexe
Dans cette section​:
9.1. Modbus UDP Interface
This appendix describes the Modbus UDP interface implemented by the VM-3P75CT and the VM-3P5A energy meters. It is intended for integrators and developers who want to read measurement data or configuration data directly over the network, in addition to the standard GX device and VictronConnect integration described earlier in this manual.
9.2. Overview
Both the VM-3P75CT and the VM-3P5A communicate using Modbus over UDP rather than the more common Modbus TCP. The meter listens on UDP port 502 and only responds to Modbus Unit ID 1. All requests must use MBAP protocol ID 0. Requests that use a different protocol ID or a different Unit ID are ignored.
Modbus UDP uses the same request and response format as Modbus TCP, except that each message is carried in a single UDP datagram instead of a TCP stream. This keeps the protocol simple to implement, but it also means that individual requests or responses can be lost, delayed, or arrive out of order on a poor network. See Compatibility Notes (A.15) for guidance on handling this.
9.3. Connecting to the meter
To exchange Modbus UDP data with the meter:
  1. Connect the client device to the same IP network as the meter.
  2. Find the meter IP address. This can be done in one of two ways: look it up in the DHCP lease table of your router, or discover it using mDNS. The meter advertises itself under the service name _victron-energy-meter._udp.
  3. Send Modbus requests to meter_ip:502 over UDP, using Unit ID 1.
9.4. Supported function codes
The meter supports the following Modbus function codes. Any other function code results in exception 0x01 (Illegal Function).
Function code
Name
0x03
Read Holding Registers
9.5. Exception codes
Code
Meaning
0x01
Illegal Function
0x02
Illegal Data Address
0x03
Illegal Data Value
0x04
Slave Device Failure
9.6. Address space overview
Base address
Size (16 bit registers)
End address
Access
Description
0x1000
12
0x100B
Read
Device info block (product, serial number, firmware, hardware)
0x2000
38
0x2025
Read
Configuration block
0x3000
144
0x308F
Read
Main meter data map (measurements, energies, mirrors)
Note
A single request must stay fully inside one block. A request that spans more than one block is rejected with exception 0x02 (Illegal Data Address).
9.7. Data representation
  • Registers are 16 bit words.
  • 32 bit values are sent as two consecutive registers, high word first, then low word.
  • Text and byte array values are sent as raw bytes, packed two bytes per register.
  • Within each register, the byte order is big endian, as is standard for Modbus.
  • Some registers use fixed sentinel values to mark data that is invalid or not available, for example 0x7FFF, 0xFFFF, or 0x7FFFFFFF.
9.8. Function level limits
Function
Limit
0x03 Read Holding Registers
1 to 125 registers per request
9.9. Device info block (0x1000, read only)
Address
Words
Name
Type
Access
0x1000
1
Product ID
uint16
Read
0x1001
8
Serial number
string (16)
Read
0x1009
2
Firmware version
uint32
Read
0x100B
1
Hardware revision
uint16
Read
9.10. Configuration block (0x2000, read only)
Address
Words
Description
Logical type
Access
Notes
0x2000
1
Phase configuration
uint8 in uint16
Read
0 = SinglePhaseL1
1 = SinglePhaseL2 (if supported)
2 = SinglePhaseL3 (if supported)
3 = ThreePhase
4 = SplitPhase
0x2001
1
Meter role
uint8 in
uint16
Read
0 = Grid
1 = Pv
2 = Generator
3 = AcMeter
4 = EvCharger
5 = HeatPump
6 = WaterPump
7 = WaterHeater
0x2002
32
User description
string (up to 64 bytes)
Read
32 registers, packed byte by byte
0x2022
1
Meter position
uint8 in
uint16
Read
0 = AcInput1
1 = AcOutput
2 = AcInput2
0x2023
1
System instance
uint8 in
uint16
Read
Instance index, 0 to 255
0x2024
2
Meter capabilities
uint32 (high, low)
Read
bit0 grid meter role support
bit1 PV inverter role support
bit2 generator role support
bit3 AC meter role support
bit4 EV charger role support
bit5 heat pump role support
bit6 split phase support
bit7 water pump role support
bit8 water heater role support
bit9 PQ snapshots timeout support
bit10 UDP PQ snapshots support
bit11 single phase L2 support
bit12 single phase L3 support
9.11. Main meter data block (0x3000, read only)
This block contains the live measurements, energy totals, and several mirrored sections that exist for compatibility with existing client software.
9.11.1. Primary live data and totals (0x3000 to 0x303F)
Address
Words
Description
Type
Access
Notes
0x3000
1
L1 voltage
int16
Read
0.01 V
0x3001
1
L1 current
int16
Read
0.01 A - VM-3P75CT only
0x3002
2
L1 real power
int32 (high, low)
Read
1 W
0x3004
2
L1 apparent power
int32 (high, low)
Read
1 VA
0x3006
2
L1 forward energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3008
2
L1 reverse energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x300A
4
Reserved
Read
Always 0
0x300E
2
Reserved
Read
Always 0
0x3010
1
L2 voltage
int16
Read
0.01 V
0x3011
1
L2 current
int16
Read
0x3012
2
L2 real power
int32 (high, low)
Read
1 W
0x3014
2
L2 apparent power
int32 (high, low)
Read
1 VA
0x3016
2
L2 forward energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3018
2
L2 reverse energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x301A
4
Reserved
Read
Always 0
0x301E
2
Reserved
Read
Always 0
0x3020
1
L3 voltage
int16
Read
0.01 V
0x3021
1
L3 current
int16
Read
0x3022
2
L3 real power
int32 (high, low)
Read
1 W
0x3024
2
L3 apparent power
int32 (high, low)
Read
1 VA
0x3026
2
L3 forward energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3028
2
L3 reverse energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x302A
4
Reserved
Read
Always 0
0x302E
2
Reserved
Read
Always 0
0x3030
2
Total real power
int32 (high, low)
Read
1 W
0x3032
1
Grid frequency
uint16
Read
0.01 Hz
0x3033
1
PE to N voltage
int16
Read
0.01 V
0x3034
2
Total forward energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3036
2
Total reverse energy
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3038
1
Error code
uint8 in uint16
Read
0x3039
1
Neutral current
int16
Read
0.01 A
0x303A
1
Total power factor
int16
Read
0.001
0x303B
1
Phase sequence
uint8 in
uint16
Read
0 = L1L2L3
1 = L1L3L2
0xFF = Invalid
0x303C
2
Alarms and warnings
uint32 (high, low)
Read
bits 1 to 0: phase rotation level
0 = Unsupported
1 = Ok
2 = Warning
3 = Alarm
Bits 31 to 2 reserved.
0x303E
1
Grid frequency (mHz resolution)
uint16
Read
0.001 Hz
0x303F
1
Reserved
Read
Always 0
9.11.2. Mirror and per phase auxiliary map (0x3040 to 0x305F)
Address
Words
Description
Type
Access
Notes
0x3040
1
L1 voltage (mirror)
int16
Read
0.01 V
0x3041
1
L1 current (mirror)
int16
Read
0x3042
2
L1 forward energy (mirror)
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3044
2
L1 reverse energy (mirror)
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3046
1
L1 line to line voltage
uint16
Read
0.01 V
0x3047
1
L1 power factor
int16
Read
0.001
0x3048
1
L2 voltage (mirror)
int16
Read
0.01 V
0x3049
1
L2 current (mirror)
int16
Read
0x304A
2
L2 forward energy (mirror)
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x304C
2
L2 reverse energy (mirror)
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x304E
1
L2 line to line voltage
uint16
Read
0.01 V
0x304F
1
L2 power factor
int16
Read
0.001
0x3050
1
L3 voltage (mirror)
int16
Read
0.01 V
0x3051
1
L3 current (mirror)
int16
Read
0x3052
2
L3 forward energy (mirror)
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3054
2
L3 reverse energy (mirror)
uint32 (high, low)
Read
0.01 kWh (10 Wh)
0x3056
1
L3 line to line voltage
uint16
Read
0.01 V
0x3057
1
L3 power factor
int16
Read
0.001
0x3058
2
L1 high range current
int32 (high, low)
Read
0.01 A - VM-3P5A only
0x305A
2
L2 high range current
int32 (high, low)
Read
0x305C
2
L3 high range current
int32 (high, low)
Read
0x305E
2
Reserved
Read
Always 0
Addresses 0x3060 to 0x307F (32 registers) are reserved and always read back as 0.
9.11.3. Power mirror map (0x3080 to 0x308F)
Address
Words
Description
Type
Access
Notes
0x3080
2
Total real power (mirror)
int32 (high, low)
Read
1 W
0x3082
2
L1 real power (mirror)
int32 (high, low)
Read
1 W
0x3084
2
L1 apparent power (mirror)
int32 (high, low)
Read
1 VA
0x3086
2
L2 real power (mirror)
int32 (high, low)
Read
1 W
0x3088
2
L2 apparent power (mirror)
int32 (high, low)
Read
1 VA
0x308A
2
L3 real power (mirror)
int32 (high, low)
Read
1 W
0x308C
2
L3 apparent power (mirror)
int32 (high, low)
Read
1 VA
0x308E
2
Reserved
Read
Always 0
9.12. Recommended polling strategy
  1. Read the static identification data once, from the 0x1000 block.
  2. Read the configuration snapshot from the 0x2000 block on startup, and again whenever a configuration change is expected.
  3. Poll the live values in the 0x3000 block at a fixed interval suited to your application.
  4. Treat reserved addresses as always 0.
  5. Apply the scaling given in this appendix, for example 0.01 V, 0.01 A, 0.01 Hz, or 0.001 for power factor.
  6. Treat sentinel values and 0xFFFF fallback words as not available or invalid.
9.13. Important Compatibility Notes
  • This is UDP, so requests and responses are connectionless and may be lost or reordered on a poor network.
  • The register map includes mirrored addresses to remain compatible with existing client software.