7. Technical data
7.1. Technical specifications
Multi HS19 Solar 15k | ||
Max. AC input and pass-through current | 32A | |
INVERTER | ||
Inverter apparent / rated power | 15kVA / 15kW | |
Continuous output power up to 40°C (1) | 15kW | |
Peak Power (2) | 22kW (5s) | |
Inverter peak AC current (2) | 32A (5s) | |
Continuous AC current per phase (1) | 22A RMS | |
AC voltage | 400Vac ± 10% 3-phase | |
AC frequency (range) | 50/60 Hz (45 - 65 Hz) | |
Total harmonic distortion | <3% | |
Maximum efficiency (3) | 98% | |
No load power at 650V battery voltage | 50W | |
AC connections | L1, L2, L3, N, PE | |
Number of AC inputs | 1 | |
Number of AC outputs | 2 | |
SOLAR | ||
Maximum open circuit voltage | 600V | |
Maximum short circuit current per string | 20A | |
Maximum MPP current per string | 13.5A | |
Number of strings | 4 | |
Number of independent trackers | 4 | |
MPPT operating voltage | 100 - 600V | |
Minimum solar voltage for wake-up (4) | 300V | |
Maximum total power per string (1) | 8kW (32kW total) | |
Maximum efficiency | 99% | |
BATTERY | ||
Operating voltage range | 650 - 1000V | |
Maximum discharge current | 25A | |
Maximum charge current | 41A | |
Communication | CAN | |
Supported batteries (5) | Batteries supporting Victron HV Protocol | |
FEATURES & PROTECTION | ||
Parallel operation (7) | No | |
Overvoltage category | PV II / AC III | |
Environment condition | Indoor, conditioned | |
Protections | PV overvoltage / PV overcurrent / DC insulation resistance / Residual current monitoring unit / AC overcurrent | |
GENERAL | ||
Weight | 26.5kg | |
19" rack height | 4U | |
Depth | 71cm | |
AC connectors | Push-in spring connectors: Rigid cable 0.2mm2 to 10mm2 Flexible cable 0.25mm2 to 6mm2 | |
DC connectors | 5.7mm Surlok | |
Solar PV connectors | MC4 Female: Staubli (Multi-Contact) PV-ADBP4-S2-UR-2,5 MC4 Male: Staubli (Multi-Contact) PV-ADSP4-S2-UR-2,5 | |
Operating temperature | 0 to +60°C (full rated operation up to 40°C) | |
Cooling | Forced air | |
Maximum altitude | 2000m | |
Humidity (non-condensing) | 95% | |
Protection grade | IP 20 | |
Programmable relay (6) | Yes, (3A, up to 30Vdc) | |
Data communication | 1x battery CAN port, 1x VE.Can port, VE.Direct port and Bluetooth | |
Remote on/off terminal | Yes | |
STANDARDS | ||
Electrical safety | EN-IEC 62109-1, EN-IEC 62109-2, Pollution degree 2 | |
Emission / Immunity | EN-IEC 61000-3-11, EN-IEC 61000-3-12 IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-4 | |
1) When both the inverter and solar are running at full power, derating on the solar and, in more severe cases, on the inverter can occur. 2) Peak power and duration depend on start temperature of heatsink. Mentioned times are with cold unit. 3) Efficiency reduces with higher battery voltages. 4) Minimum voltage for communication to start when the Multi HS19 is only powered by solar. 5) Check the manual for the full list of supported batteries. 6) Programmable relay which can be set for general alarm, DC under voltage or genset start/stop function. 7) Future hardware revisions will support parallel operation. | ||
7.2. Dimensions
7.3. Internal block diagram
Warning
The battery is not galvanically isolated from the internal DC bus.
The battery terminals, PV MPPT inputs and inverter AC inputs and outputs ultimately all share a common internal DC bus and are not galvanically isolated from each other.
7.4. Example wiring diagram
Caution
Follow the battery manufacturer's guidance for battery overcurrent protection.
Caution
Ensure that the grounding requirements for your particular region are followed.
7.5. Compliance
EU & UK DECLARATION OF CONFORMITY
Manufacturer: | Victron Energy B.V. |
Address: | PO Box 50016, 1305 AA Almere, The Netherlands | ||
Product: | Multi HS19 Solar | ||
Models: | 15k | ||
Directives: | 2014/53/EU and S.I. 2017/1206 | ||
Hereby, Victron Energy B.V declares that the equipment types stated above are in compliance with Directive 2014/53/EU and S.I. 2017:1206. | Rev 01 - 06/2026 | ||
The complete product manual and the official EU & UK Declaration of Conformity can be downloaded from the Multi HS19 Solar 15k product page (scan the QR code or visit https://ve3.nl/7q), under 'Downloads' > 'Manuals' or 'Certificates'. | |||
UK PSTI STATEMENT OF COMPLIANCE: We, Victron Energy B.V., confirm that our product Multi HS19 Solar 15k meets the security requirements for manufacturers outlined in Schedule 1 of the Product Security and Telecommunications Infrastructure (PSTI) Regulations 2023 No. 1007. For a full statement of compliance, visit https://ve3.nl/7q. | |||