Multi HS19 Solar 15k
1. Safety Instructions
In this section:
Warning
ELECTRIC SHOCK HAZARD
HV safety warning and certified installer only
Please read the installation instructions in the installation manual before installing the Multi HS19 Solar. Connections must always be made in the sequence described in the installation section of this manual.
Do not open any covers of the enclosure; there are no serviceable parts inside. The internals can carry a 1000V DC voltage even when the Multi HS19 Solar is off! All connections are accessible on the front and rear panels of the enclosure.
The Multi HS19 Solar is designed and tested in accordance with international standards. The Multi HS19 Solar should be used for the designated application only. Using the Multi HS19 Solar outside of its specifications may impair its safety protections.
Refer to the specifications provided by the manufacturer of the battery to ensure that the battery is suitable for use with this product. The battery manufacturer's safety instructions should always be observed.
Batteries should only be replaced with the same type and number of modules.
Always follow the manufacturer's instructions for installation and removal of batteries.
Always disconnect all power connections (e.g. the battery isolator, DC solar PV isolator and AC input and output circuit breakers) and wait at least 5 minutes before carrying out work on the product. Input and/or output terminals may still be dangerously energized, even when the equipment is switched off.
Protect the solar modules from incident light during installation, e.g. cover them.
Never touch uninsulated cable ends.
Use only insulated tools.
The installer of the product must provide a means for cable strain relief to prevent the transmission of stress to the connections.
In addition to this manual, the system operation or service manual must include a battery maintenance manual applicable to the type of batteries used. The battery must be placed in a well-ventilated area.
Warning
SELECTION OF WIRE CONDUCTORS
Use flexible multistranded copper cable for the battery and PV connections.
The maximum diameter of the individual strands is 0,4mm/0,125mm² (0.016 inch/AWG26).
A 25mm² cable, for example, should have at least 196 strands (class 5 or higher stranding according to VDE 0295, IEC 60228 and BS6360).
An AWG2 gauge cable should have at least 259/26 stranding (259 strands of AWG26).
Maximum operating temperature: ≥ 90°C.
Example of suitable cable: class 5 “Tri-rated” cable (it has three approvals: American (UL), Canadian (CSA) and British (BS)).
In case of thicker strands the contact area will be too small and the resulting high contact resistance will cause severe overheating, eventually resulting in fire.
Warning
RISK OF INJURY OR DEATH
The product has no internal user-serviceable components. Do not remove the front plate or operate the product if any panels have been removed. All servicing must be undertaken by qualified personnel.
Please read the installation instructions in the installation manual before installing the equipment.
This is a Safety Class I product (supplied with a protective grounding terminal). The chassis must be grounded. Whenever it is likely that the grounding protection has been damaged, the product must be turned off and secured against unintended operation; please contact qualified service staff.
Non-isolated inverters shall be provided with installation instructions that require PV modules that have an IEC 61730 Class A rating.
If the maximum AC mains operating voltage is higher than the PV array maximum system voltage, then the instructions shall require PV modules that have a maximum system voltage rating based upon the AC mains voltage.
Environment and Access
The Multi HS19 Solar is for indoor use only. Ensure that the equipment is used under the correct ambient conditions. Never operate the product in a wet or dusty environment. Never use the product where there is a risk of gas or dust explosions. Ensure there is adequate free space for ventilation above and below the product and check that the ventilation vents are not blocked.
Installation of the Multi HS19 Solar must be in a location that restricts access by persons (including children) with reduced physical, sensory or mental capabilities, or lack of experience and knowledge, unless they have been given supervision or instruction concerning use of the appliance by a person responsible for their safety.
The connections to live parts should be covered after installation.
Encolsure symbols
Caution, risk of electric shock
Refer to the operating instructions
IP20 Protected from touch by fingers and objects greater than 12 millimetres. Protected from condensation.
European conformity
Regulatory compliance mark for Australia & New Zealand