Skip to main content

Lynx Smart BMS

11. Appendix

In this section:

11.1. LED indications, warnings, alarm and error codes

LEDs

The Lynx Smart BMS is equipped with two LEDs, the Bluetooth LED and the Status LED. These LEDs will indicate the operation mode and the fault mode in case there is a fault.

Bluetooth LED

Description

Off

No system power or Bluetooth disabled in VictronConnect app. Bluetooth can be disabled in both, VictronConnect and a GX device, but only enabled from a GX device.

Blue on

A Bluetooth device is connected to the Lynx Smart BMS

Blue flashing

Bluetooth is active but no device is connected

Blue flashing at 3 seconds interval

The Lynx Smart BMS is in OFF mode but is still accessible over Bluetooth

Status LED

Description

Off

The Lynx Smart BMS is in OFF mode

Orange on

Initializing or shutdown

Orange blinking

Delayed shutdown due to cooling down the pre-charge circuit

Green on

Running, the contactor is closed

Green blinking

Pre-charging

Green flashing at 3 seconds interval

The Lynx Smart BMS is in Standby mode

Green and red alternating

System in bootloader mode (updating firmware)

Red flashing 1 time every 4 seconds

Warning, see VictronConnect for more information

Red flashing 2 times every 4 seconds

Battery communication error, check battery BMS cables

Red flashing 3 times every 4 seconds

High/low cell voltage or high/low temperature detected

Red flashing 4 times every 4 seconds

High BMS temperature detected

Red flashing 5 times every 4 seconds

Pre-charge time out

Red flashing 6 times every 4 seconds

Pre-charge high current

Red flashing 7 times every 4 seconds

Probably wrong system voltage

Red flashing 8 times every 4 seconds

Contactor current too high

Red flashing 9 times every 4 seconds

Initialization error

Red flashing 10 times every 4 seconds

Safety contactor failure

Red flashing 12 times every 4 seconds

Internal supply error

Red flashing 14 times every 4 seconds

Battery voltage not allowed

Warning, alarm and error codes

Warning, alarm and error codes are also reported via the VictronConnect app or a connected GX device and VRM.

A warning indicates a problem that, if not corrected, will result in a system shutdown, while an alarm indicates the reason for the system shutdown.

Lynx_Distributor_VC_and_GX_fuse_alarm.png

Lynx Smart BMS alarms on the VictronConnect App and a GX device

The following tables list all warning, alarm and error codes:

Warnings: Warnings indicate an issue that when unresolved will lead to a system shutdown

VictronConnect warning code

Message

Instructions / remarks

W-B01

Low cell voltage

Charge the battery or reduce the load to prevent an imminent system shutdown.

W-B02

High current

Reduce the current to prevent an imminent system shutdown. Do this by reducing the load or by turning loads off.

W-B03

High BMS temperature

Check the ambient temperature and check if the BMS fans are running. If the fans are running, reduce the ambient temperature. If the fans are not running, contact your Victron dealer.

W-B04

Warning bad contactor

Reduce the current to prevent an imminent system shutdown. Do this by reducing the load or by turning loads off. Contact your Victron dealer.

W-B06

Load will disconnect

The loads will be turned off in 30 seconds if fault is not resolved. For example low battery voltage. This warning is always in combined the reason why the load will disconnect.

The loads are turned off via the ATD contact and/or via the GX device.

W-B07

Low SoC

Charge battery or reduce load to prevent imminent system shutdown.

W-B10

VE.CAN disconnected

Check communication cabling.

W-D01

Communication with distributor A lost

Check the cable between BMS and Distributor.

W-D02

Communication with distributor B lost

Check the cable between BMS and Distributor.

W-D03

Communication with distributor C lost

Check the cable between BMS and Distributor.

W-D04

Communication with distributor D lost

Check the cable between BMS and Distributor.

W-D05

Communication with distributor E lost

Check the cable between BMS and Distributor.

W-D06

Communication with distributor F lost

Check the cable between BMS and Distributor.

W-D07

Communication with distributor G lost

Check the cable between BMS and Distributor.

W-D08

Communication with distributor H lost

Check the cable between BMS and Distributor.

Alarms: Alarms indicate the reason why the system is shutdown.

VictronConnect alarm code

Message

Instructions / remarks

A-B01

Low cell voltage

Charge battery. The system will turn the loads back on when the battery is sufficiently charged.

A-B02

High current

Reduce charging current or turn off some loads. The system will try to re-enable chargers or loads in 5 minutes.

A-B06

Load disconnected

The loads have been turned off via the ATD contact and/or via the GX device. Resolve this alarm by charging the battery. If not resolved, eventually the contactor will open and the DC system will be disconnected.

A-B07

Low SoC

Charge battery. The system will turn the loads back on when the battery is sufficiently charged.

Error codes

VictronConnect error code

Message

Instructions / remarks

E-B01

Battery init failure

Check that all batteries are properly connected.

E-B02

No battery found

Verify that the BMS cable loop is closed.

E-B05

Invalid number of batteries

Check that all batteries are properly connected.

E-B09

Battery voltage not allowed

The battery voltage is too high or too low. Check the battery voltage and check the battery settings in the VictronConnect app.

This error occurs when the battery voltage is outside all system voltage ranges (9V > Vbat > 60V)

E-B11

Hardware error

Contact your Victron dealer.

E-B25

Pre-charge error

The load resistance is too low to pre-charge the loads. Disconnect or reduce some DC loads.

E-B26

Contactor error

Contact your Victron dealer.

E-B32

BMS cable error

Check the battery M8 cabling.

E-B34

Wrong system voltage

Check battery voltage settings in the VictronConnect app.

E-B35

Pre-charge timeout

The load capacity is too high to pre-charge. Disconnect some DC loads.

E-B36

ATC/ATD failure

Check ATC/ATD wiring and make sure that all loads and chargers are controlled by ATC or ATD.

E-B116

Calibration data lost

Contact your Victron dealer.

E-B119

Settings data lost

Settings data is corrupt. Go to the settings page and reset to defaults.

Alarm codes Lynx Distributor related

VictronConnect alarm code

Message

Instruction / remarks

A-F01

Fuse "Fuse_1" is blown

Check your system and replace fuse.

A-F02

Fuse "Fuse_2" is blown

A-F03

Fuse "Fuse_3" is blown

A-F04

Fuse "Fuse_4" is blown

A-F05

Fuse "Fuse_5" is blown

A-F06

Fuse "Fuse_6" is blown

A-F07

Fuse "Fuse_7" is blown

A-F08

Fuse "Fuse_8" is blown

A-F09

Fuse "Fuse_9" is blown

A-F10

Fuse "Fuse_10" is blown

A-F11

Fuse "Fuse_11" is blown

A-F12

Fuse "Fuse_12" is blown

A-F13

Fuse "Fuse_13" is blown

A-F14

Fuse "Fuse_14" is blown

A-F15

Fuse "Fuse_15" is blown

A-F16

Fuse "Fuse_16" is blown

A-F17

Fuse "Fuse_17" is blown

A-F18

Fuse "Fuse_18" is blown

A-F19

Fuse "Fuse_19" is blown

A-F20

Fuse "Fuse_20" is blown

A-F21

Fuse "Fuse_21" is blown

A-F22

Fuse "Fuse_22" is blown

A-F23

Fuse "Fuse_23" is blown

A-F24

Fuse "Fuse_24" is blown

A-F25

Fuse "Fuse_25" is blown

A-F26

Fuse "Fuse_26" is blown

A-F27

Fuse "Fuse_27" is blown

A-F28

Fuse "Fuse_28" is blown

A-F29

Fuse "Fuse_29" is blown

A-F30

Fuse "Fuse_30" is blown

A-F31

Fuse "Fuse_31" is blown

A-F32

Fuse "Fuse_32" is blown

* If the fuse name is not set, the default name is used. If it is set, the name configured in VictronConnect for the Lynx Distributor is used.

11.2. Supported NMEA 2000 PGNs

Description

PGN

Product Information

126996

DC detailed Status

127506

DC/Battery Status

127508

Switch Bank Status

  • Status 1: Contactor

  • Status 2: Alarm

  • Status 3: Battery voltage low

  • Status 4: Battery voltage high

  • Status 5: Programmable relay status

127501

Class and function:

  • N2K device class: Electrical generation

  • N2K device function: Battery

For more information see the NMEA2000 & MFD integration guide.

11.3. List of battery monitor settings

Description

default value

adjustable

fixed

automatic

Battery capacity

200Ah

Yes

No

No

Charged voltage

14.0V/28.0V/56.0V*

Yes

No

No

Tail current

4%

Yes

No

No

Zero current calibration

---

No

No

Yes (at power up)

Peukert exponent

1.05

No

Yes

No

Charge efficiency factor

99%

No

Yes

No

Current threshold

0.05A

No

Yes

No

Low SoC warning level

15%

Yes

No

No

Discharge floor

10%

Yes

No

No

Delta T

1

No

Yes

No

SoC Cycle end

90%

No

Yes

No

SoC Cycle

65%

No

Yes

No

SoC full discharge

5%

No

Yes

No

* for a 12V/24V/48V system

11.4. Multiconnector pin-out and overview

Pin

Name

Type

Function

1

AUX voltage output +

System voltage positive

The positive connection to power auxiliary devices, like a GX device.

2

AUX voltage output -

System voltage negative

The negative (ground) connection to power auxiliary devices, like a GX device.

3

Allow to charge

Potential free contact

Turns chargers on or off via a wired signal. Pin 3 can be used as the signal input for pin 4 and wired e. g. from AUX + or AUX -. See system examples for correct wiring.

When charging is allowed, the contacts are closed and when not allowed, the contacts are open.

4

5

Allow to discharge

Potential free contact

Turns loads on or off via a wired signal. Pin 5 can be used as the signal input for pin 6 and wired, e. g. from AUX + or AUX -. See system examples for correct wiring.

When discharging is allowed, the contacts are closed and when not allowed, the contacts are open.

6

7

Programmable relay NC

Potential free contact

The programmable relay is used to either control an alternator or as an alarm relay. For details, see chapter Programmable relay wiring.

8

Programmable relay COM

Potential free contact

9

Programmable relay NO

Potential free contact

10

Remote on/off H

Pull-up resistor

To remotely turn the Lynx Smart BMS on or off. For full functionality, see chapter Wiring the Remote on/off.

11

Remote on/off L

Pull-down resistor

12

TEMP +

Sensor

Positive Input for external temperature sensor (1000A only, not supported, future use)

13

TEMP -

Sensor

Negative Input for external temperature sensor (1000A only, not supported, future use)

11.5. Lynx Smart BMS related menu structure of the GX device

This is an overview of the Lynx Smart BMS related menu structure of the GX device. To see all menu items shown here, Venus OS v2.90 or later is required.

Menu item

Default value / unit

Description and / or possible values

Lynx Smart BMS

Shows SoC, voltage and current in the device list

Switch

On

Soft switch to manually switch the Lynx Smart BMS to Standby or On mode

State

Running

Possible states: Initialising, Pre-charging, Running, Shutdown, Standby

Error

#0 - No error

Error state

Battery

Voltage, current, power

Shows current battery monitor data

State of charge

%

State of charge in percent

Consumed AmpHours

Ah

Displays the consumed AH since the battery was last fully charged

Time-to-go

Days / Hours

Displays the estimated time, based on the current load and discharge floor setting

Alarms

High internal temperature

Ok

Low cell voltage

Ok

Low SoC

Ok

History

Deepest discharge

Ah

The deepest discharge since last history reset

Total charge cycles

0

Number of charge cycles since last history reset

Number of full discharges

0

A full discharge is accounted for after SoC falls below 5%

Cumulative Ah drawn

Ah

Cumulative Ah drawn since last history reset

Minimum voltage

V

Minimum voltage since last history reset

Maximum voltage

V

Maximum voltage since last history reset

Synchronisation count

0

Cumulative number of battery monitor synchronisations

Discharged energy

kWh

Cumulative number of discharged energy since last history reset

Charged energy

kWh

Cumulative number of charged energy since last history reset

Clear history

Press to clear

Clears all history data

Diagsnostics

Diagnostics

Shows last known errors

Fuses

Distributor A

Ok

Possible states: Ok, Fuse blown

Fuse 1..4

Ok

Possible states: Ok, Not used, Blown

Distributor B

Ok

Possible states: Ok, Fuse blown

Fuses 1..4

Ok

Possible states: Ok, Not used, Blown

IO

System switch

Enabled

Status of the system switch

Allow to charge

Yes

Status of the ATC signal

Allow to discharge

Yes

Status of the ATD signal

Device

Device related parameters and custom name setting

Parameters

Charge Voltage Limit (CVL)

V

Shows the voltage target send to DVCC compatible chargers (for a 12V battery: 13.50V or 14.20V)

Charge Current Limit (CCL)

A

Maximum allowed charge current limit send to DVCC compatible chargers

Discharge Current Limit (DCL)

A

Maximum allowed discharge current limit

11.6. Reversed power distribution

WARNING: Electrical shock and fire hazard

Disable and remove all voltage sources before opening the enclosure or performing any service operations. Use a voltmeter to ensure that there is no residual voltage from internal capacitors, batteries or the like. Failure to observe this instruction may result in burns or fire.

11.6.1. Introduction

This guide describes how to configure the Lynx Smart BMS and Lynx Smart BMS NG for reversed power distribution.

By default, power flows from left to right: DC power sources connect to the left-hand side, and DC loads to the right. This guide is intended for cases where this arrangement needs to be reversed. It applies to all models and hardware revisions of the Lynx Smart BMS.

11.6.2. Models and variants

There are currently two models and two variants of the Lynx Smart BMS.

The models differ by current rating:

  • 500 A version with one power contactor

  • 1000 A version with two power contactors

The variants are distinguished by enclosure marking:

  • NG (New Generation)

  • Non-NG (original design)

Lynx_Smart_BMS_500_open.png
Lynx_Smart_BMS_NG_open.png

11.6.3. Technical background

The primary function of the Lynx Smart BMS is to monitor system and battery voltages, as well as the currents flowing through the device, thereby protecting the battery from under- and overcharging.

Before closing the main power contactor, the BMS performs a short-circuit check on the load side by pre-charging any connected loads. It also monitors the current through the busbar’s shunt to prevent over-current situations that could damage cables or the battery.

Reversing the power distribution requires specific configuration changes, as the load and source connections - and the current flow through the shunt - are reversed. The current shunt is a low-ohmic resistor, precisely factory-calibrated. User modifications to the shunt are not permitted, as even minor changes can introduce contact resistance and invalidate the calibration.

To compensate for the reversed current flow, a dedicated software setting is available. This must be configured via Bluetooth using the VictronConnect app, available from the Victron Energy website.

Caution

Without these modifications, the Lynx Smart BMS will not function as intended.

11.6.4. Wiring adjustment procedure

This procedure involves relocating the voltage sense wires on either side of the power contactor:

Voltage sense wires involved:

  • Red wire = Source voltage

  • White wire = Load voltage

Steps

  1. Access the wiring area

    • Remove the fan bracket from its holder and set it aside

      Do not disconnect the fan cables; the connector has limited mating cycles.

  2. Swap the wires

    • Move the white wire to the left side

      Note

      For the Lynx BMS 1000A: On units with serial numbers before HQ2530, the white wire may be too short and will need to be extended.

    • Move the red wire to the right side

    Use a 2.5 mm Allen key to loosen the screws, reposition the wires, and re-tighten them.

  3. Secure the wiring

    • Ensure screws are snug, but do not overtighten.

    • Route the wires neatly along the bottom corner of the power contactor to avoid obstructing the fan bracket.

    • Refit the fan bracket.

  4. Check clearance

    • Ensure the now-crossed wires do not block the internal light pipes.

  5. Close the unit

    • Refit the enclosure cover and tighten all screws before applying power.

Modification.png

Source and load voltage sense

Modification_2.png

Swapped wires for reversed power distribution

11.6.5. Configuring the reversed current setting

Follow these steps after completing the voltage sense wire swap:

  1. Open the VictronConnect app

  2. Select your Lynx Smart BMS from the device list

  3. Tap the cogwheel icon in the top-right corner

  4. Select Current measurement direction

  5. Set it to Reversed

Caution

Without applying both the wiring and software modifications, the Lynx Smart BMS will not function as intended.

VC_Current_Measurement_Direction.PNG

Revere current setting in VictronConnect

11.6.6. Final check

Before leaving the installation unattended:

  • Power on the unit and properly test and verify the unit's functionality

  • Confirm correct operation

  • Ensure all protective functions are active

If you are not confident in performing the procedure, contact your local Victron representative for assistance.

11.7. Enclosure dimensions

DimensionDrawing_Lynx_Smart_BMS_500__M10_-rev00.pdf