MultiPlus-II GX
13. Technical specifications
In this section:
MultiPlus-II GX 230V
48/4k5/55-32
48/6k5/100-50
PowerControl & PowerAssist
Yes
Transfer switch
32A
50A
Maximum AC input current
32A
50A
Auxiliary output
Yes (32A)
INVERTER
Input voltage range
38 – 60V
Output in inverter mode (1)
Output voltage: 230 VAC ± 2%    Frequency: 50 Hz ± 0.1%
Cont. output power at 25°C (3)
4 kW
6 kW
4000 W
6000 W
Cont. output power at 40
3,7 kW
5,7 kW
Cont. output power at 65°C
3 kW
4,6 kW
Time-limited power 1 (cold start)
4,5 kW/2h
4,5 kW/2h
Time-limited power 2 (cold start)
6 kW/25min
8 kW/1h
Maximum feed-in power
4 kW
6 kW
Peak power
7 kW / 1min
11 kW / 1min
Maximum efficiency
95%
96%
Zero load power
20 W
28 W
Zero load power in AES mode
13 W
18 W
Zero load power in Search mode
8 W
8 W
CHARGER
AC Input
Input voltage range: 187-265 VAC    Input frequency: 45 – 65 Hz
Charge voltage 'absorption'
57,6V
Charge voltage 'float'
55,2V
Storage mode
52,8V
Maximum battery charge current (4)
55A
100A
Battery temperature sensor
Yes
Compatible battery chemistries
Lithium, Lead-acid, Zinc-Bromine and more (3)
GENERAL
Programmable (AUX) relay (5)
Yes
Auxiliary power supply
12V / 100mA
Programmable open collector output
70V / 100mA
Analog-digital aux inputs
Yes, 2x
Temperature sensor
Optional. Order number: ASS000001000
Voltage sense contacts
Yes
Protection (2)
a - g
VE.Bus communication port
For parallel and three-phase operation, remote monitoring and system integration
General purpose communication port
Yes, 2x
Interfaces
VE.Can, USB, Ethernet, VE.Direct, Wi-Fi
External AC current sensor (optional)
100A
Remote on-off
Yes
Operating temperature range
-40 to +65 °C (fan-assisted cooling). Maximum Altitude 2000m
Humidity (non-condensing)
max 95%
ENCLOSURE
Material and colour
Steel, blue RAL 5012
Protection category
IP21
Battery connection
M8 bolts
230VAC connection
Screw terminals 13 mm2 (6 AWG)
Weight
21,4 kg
29,0 kg
Dimensions hxwxd (mm)
590 x 275 x 149 mm
644 x 320 x 150 mm
STANDARDS
Safety
EN-IEC 62019-1, EN-IEC 6201-2, EN-IEC 60335-1, EN-IEC 60335-2-29
Emission / Immunity
EN55014-1, EN 55014-2 EN-IEC 61000-3-2, EN-IEC 61000-3-3
IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-3
Uninterruptible power supply
Certification pending
Anti-islanding
1) Can be adjusted to 60Hz
2) Protection key:
a) output short circuit
b) overload
c) battery voltage too high
d) battery voltage too low
e) temperature too high
f) 230VAC on inverter output
g) input voltage ripple too high
3) Other chemistries are possible as well, providing the charger is configured according to the battery manufacturer’s specification.
4) Non-linear load, crest factor 3:1
5) Up to 25°C ambient