8. Technical Specifications
MultiPlus-II | 12/3000/120-32 | 24/3000/70-32 | 48/3000/35-32 |
PowerControl / PowerAssist | Yes | ||
AC input | Input voltage range: 187-265 VAC Input frequency: 45 – 65 Hz | ||
Maximum feed through current | 32 A | ||
INVERTER | |||
Input voltage range | 9.5 – 17 V 19 – 33 V 38 – 66 V | ||
Output (1) | Output voltage: 230 VAC ± 2 % Frequency: 50 Hz ± 0,1 % | ||
Cont. output power at 25 °C / 77 °F (3) | 3000 VA | ||
Cont. output power at 25 °C / 77 °F | 2400 W | ||
Cont. output power at 40 °C / 104 °F | 2200 W | ||
Cont. output power at 65 °C / 150 °F | 1700 W | ||
Maximum feed-in power | 3000 VA | ||
Peak power | 5500 W | ||
Maximum efficiency | 93 % | 94 % | 95 % |
Zero-load power | 13 W | 13 W | 11 W |
Zero-load power in AES mode | 9 W | 9 W | 7 W |
Zero-load power in Search mode | 3 W | 3 W | 2 W |
CHARGER | |||
AC input | Input voltage range: 187-265 VAC Input frequency: 45 – 65 Hz Power factor: 1 | ||
Charge voltage 'absorption' | 14.4 / 28.8 / 57.6 V | ||
Charge voltage 'float' | 13.8 / 27.6 / 55.2 V | ||
Storage mode | 13.2 / 26.4 / 52.8 V | ||
Charge current house battery (4) | 120 A | 70 A | 35 A |
GENERAL | |||
Auxiliary output | Yes (32 A) Default setting: switches off when in inverter mode | Yes (50 A) Default setting: switches off when in inverter mode | |
External AC current sensor (optional) | 50 A | ||
Programmable relay (5) | Yes | ||
Protection (2) | a - g | ||
VE.Bus communication port | For parallel and three phase operation, remote monitoring and system integration | ||
General purpose com. port | Yes, 2x | ||
Common Characteristics | Operating temp.: -40 to +65 °C (-40 – 150 °F) (fan assisted cooling) Humidity (non-condensing): max 95 % | ||
ENCLOSURE | |||
Material & Colour | Steel, blue RAL 5012 Protection category: IP22 Pollution degree 2, OVC3 | ||
Battery-connection | M8 bolts | ||
230 VAC-connections | Screw terminals 13 mm² (6 AWG) | ||
Weight | 20 kg | 19 kg | 19 kg |
Dimensions (hxwxd) mm | 546 x 275 x 147 | 499 x 268 x 141 | 499 x 268 x 141 |
STANDARDS | |||
Safety | EN 60335-1, EN 60335-2-29, IEC62109-1, IEC62109-2 | ||
Emission / Immunity | EN 55014-1, EN 55014-2, EN-IEC 61000-3-2, EN-IEC 61000-3-3, IEC 61000-6-1, EN 61000-6-2, EN 61000-6-3 | ||
Uninterruptible power supply | Please consult the certificates on our website. | ||
Anti-islanding | Please consult the certificates on our website. |
MultiPlus-II | 24/5000/120-50 | 48/5000/70-50 | 48/8000/110-100/100 | 48/10000/140-100/100 | ||
PowerControl / PowerAssist | Yes | Yes | ||||
AC input | Input voltage range: 187-265 VAC Input frequency: 45 – 65 Hz | Input voltage range: 187-265 VAC Input frequency: 45 – 65 Hz | ||||
Maximum feed through current | 50 A | 100 A | ||||
INVERTER | ||||||
Input voltage range | 19 – 33 V 38 – 66 V | 38 – 66 V | 38 – 66 V | |||
Output (1) | Output voltage: 230 VAC ± 2% Frequency: 50 Hz ± 0,1% | Output voltage: 230 VAC ± 2% Frequency: 50 Hz ± 0,1% | ||||
Cont. output power at 25°C / 77°F (3) | 5000 VA | 8000 VA | 10000 VA | |||
Cont. output power at 25°C / 77°F | 4000 W | 6400 W | 8000 W | |||
Cont. output power at 40°C / 104°F | 3700 W | 5500 W | 7000 W | |||
Cont. output power at 65°C / 150°F | 3000 W | 4000 W | 6000 W | |||
Maximum feed-in power | 5000 VA | 8000 VA | 10000 VA | |||
Peak power | 9000 W | 15000 W | 18000 W | |||
Maximum efficiency | 96 % | 95 % | 96 % | |||
Zero-load power | 18 W | 29 W | 38 W | |||
Zero-load power in AES mode | 12 W | 19 W | 27 W | |||
Zero-load power in Search mode | 2 W | 3 W | 4 W | |||
CHARGER | ||||||
AC input | Input voltage range: 187-265 VAC Input frequency: 45 – 65 Hz Power factor: 1 | Input voltage range: 187-265 VAC Input frequency: 45 – 65 Hz Power factor: 1 | ||||
Charge voltage 'absorption' | 28,8 / 57,6 V | 28,8 / 57,6 V | ||||
Charge voltage 'float' | 27,6 / 55,2 V | 27,6 / 55,2 V | ||||
Storage mode | 26,4 / 52,8 V | 26,4 / 52,8 V | ||||
Charge current house battery (4) | 120 A | 70 A | 110 A | 140 A | ||
GENERAL | ||||||
Auxiliary output | Yes (32 A) Default setting: switches off when in inverter mode | Yes (50 A) Default setting: switches off when in inverter mode | ||||
External AC current sensor (optional) | 100 A | |||||
Programmable relay (5) | Yes | Yes | ||||
Protection (2) | a - g | a - g | ||||
VE.Bus communication port | For parallel and three phase operation, remote monitoring and system integration | Three phase operation, remote monitoring and system integration | ||||
General purpose com. port | Yes, 2x | Yes, 2x | ||||
Common Characteristics | Operating temp.: -40 to +65°C (-40 – 150°F) (fan assisted cooling) Humidity (non-condensing): max 95% | Operating temp.: -40 to +65°C (-40 – 150°F) (fan assisted cooling) Humidity (non-condensing): max 95% | ||||
ENCLOSURE | ||||||
Material & Colour | Steel, blue RAL 5012 Protection category: IP22 Pollution degree 2, OVC3 | Steel, blue RAL 5012 Protection category: IP22 Pollution degree 2, OVC3 | ||||
Battery-connection | M8 bolts | Four M8 bolts (2 plus and 2 minus connections) | ||||
230 VAC-connections | Screw terminals 13 mm² (6 AWG) | Bolts M6 | Bolts M6 | |||
Weight | 30 kg | 30 kg | 41.2 kg | 48.8 kg | ||
Dimensions (hxwxd) | 607 x 330 x 149 | 565 x 320 x 149 | 642 x 363 x 206 | 677 x 363 x 206 | ||
STANDARDS | ||||||
Safety | EN 60335-1, EN 60335-2-29, IEC62109-1, IEC62109-2 | EN 60335-1, EN 60335-2-29, IEC62109-1, IEC62109-2 | ||||
Emission / Immunity | EN 55014-1, EN 55014-2, EN-IEC 61000-3-2, EN-IEC 61000-3-3 IEC 61000-6-1, EN 61000-6-2, EN 61000-6-3 | EN 55014-1, EN 55014-2, EN-IEC 61000-3-2, EN-IEC 61000-3-3 IEC 61000-6-1, EN 61000-6-2, EN 61000-6-3 | ||||
Uninterruptible power supply | Please consult the certificates on our website. | Please consult the certificates on our website. | ||||
Anti-islanding | Please consult the certificates on our website. | Please consult the certificates on our website. | ||||
MultiPlus-II | 48/15000/200-100 | |
Maximum feed through current | 100 A | |
INVERTER | ||
Input voltage range | 38 – 66 V | |
Output (1) | Output voltage: 230 VAC ± 2% Frequency: 50 Hz ± 0,1% | |
Cont. output power at 25 °C / 77 °F (3) | 15000 VA | |
Cont. output power at 25 °C / 77 °F | 12000 W | |
Cont. output power at 40 °C / 104 °F | 10000 W | |
Cont. output power at 65 °C / 150 °F | 7000 W | |
Maximum feed-in power | 15000 VA | |
Peak power | 27000 W | |
Maximum efficiency | 95% | |
Zero-load power | 55 W | |
Zero-load power in AES mode | 39 W | |
Zero-load power in Search mode | 6 W | |
CHARGER | ||
Charge voltage 'absorption' | 28,8 / 57,6 V | |
Charge voltage 'float' | 27,6 / 55,2 V | |
Storage mode | 26,4 / 52,8 V | |
Charge current house battery (4) | 200 A | |
GENERAL | ||
Auxiliary output | Yes (50 A) | |
VE.Bus communication port | Three phase operation, remote monitoring and system integration | |
Common Characteristics | Operating temp.: -40 to +65°C (-40 – 150°F) (fan assisted cooling) Humidity (non-condensing): max 95% | |
ENCLOSURE | ||
Battery-connection | Four M8 bolts (2 plus and 2 minus connections) | |
230 VAC-connections | Bolts M6 | |
Weight | 80 kg | |
Dimensions (h x w x d) mm | 810 x 405 x 217 | |
STANDARDS | ||
Safety | EN-IEC 60335-1, EN-IEC 60335-2-29, EN-IEC 62109-1, EN-IEC 62109-2 | |
Emission / Immunity | EN 55014-1, EN 55014-2 EN-IEC 61000-3-2, EN-IEC 61000-3-3 IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-3 | |
Anti-islanding | Please consult the certificates on our website. | |