8. Technical Specifications
MultiPlus-II | 12/3000/120-50 2x 120 | 24/3000/70-50 2x 120 | |||
PowerControl & PowerAssist | Yes (on L1 input) | ||||
Transfer switch | 50 A | ||||
Maximum AC input current | 50 A (each leg) | ||||
INVERTER | |||||
DC Input voltage range | 9,5 – 17 V | 19 - 33 V | |||
Output when in inverter mode | Output voltage: 120 VAC ± 2% Frequency: 60 Hz ± 0,1% (1) | ||||
Cont. output power at 25°C (3) | 3000 VA | ||||
Cont. output power at 25°C | 2400 W | ||||
Cont. output power at 40°C | 2200 W | ||||
Cont. output power at 65°C | 1700 W | ||||
Maximum apparent feed-in power | 2500 VA | ||||
Peak power | 5500 W | ||||
Maximum efficiency | 93% | 94% | |||
Zero load power | 15 W | 11 W | |||
Zero load power in AES mode | 10 W | 8 W | |||
Zero load power in Search mode | 4 W | 4 W | |||
Maximum output current | 60A peak, 50Arms for 1sec. | ||||
CHARGER | |||||
AC Input | Split phase: 180-280 VAC 45 – 65 Hz Single phase: 90-140 VAC 45 – 65 Hz | ||||
Charge voltage 'absorption' | 14.4 V | 28.8 V | |||
Charge voltage 'float' | 13.8 V | 27.6 V | |||
Storage mode | 13.2 V | 26.4 V | |||
Maximum battery charge current (4) | 120 A | 70 A | |||
Battery temperature sensor | Yes | ||||
GENERAL | |||||
Auxiliary output | Yes (50 A) | ||||
External AC current sensor (optional) | 100 A | ||||
Programmable relay (5) | Yes | ||||
Protection (2) | a – g | ||||
VE.Bus communication port | For parallel and three phase operation, remote monitoring and system integration | ||||
General purpose com. port | Yes, 2x | ||||
Remote on-off | Yes | ||||
Operating temperature range | -40 to +65°C (-40 - 150°F) fan assisted cooling | -40 to +60°C (-40 - 140°F) fan assisted cooling | |||
Humidity (non-condensing) | max 95% | ||||
ENCLOSURE | |||||
Material & Colour | Steel, blue RAL 5012 | ||||
Protection category | IP22 | ||||
Battery-connection | 2x2 M8 bolts | 2 M8 bolts | |||
120/240 V AC-connection | Screw terminals 21 mm² (4 AWG) | ||||
Weight | 22 kg (48 lb) | ||||
Dimensions (hxwxd) mm | 578 x 275 x 148 (23 x 11 x 6 inch) | 578 x 275 x 148 (23 x 11 x 6 inch) | |||
STANDARDS | |||||
Safety | EN-IEC 60335-1, EN-IEC 60335-2-29, UL 458 | EN-IEC 60335-1, EN-IEC 60335-2-29, UL 458 | |||
Emission, Immunity | EN 55014-1, EN 55014-2 EN-IEC 61000-3-2, EN-IEC 61000-3-3 IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-3 | ||||