9. Technical specifications
9.1. Specifications 150/60 and 150/70
MPPT 150/60 | MPPT 150/70 | ||
|---|---|---|---|
Battery voltage | 12/24/48V Auto select, 36V: manual select | ||
Maximum battery current | 60A | 70A | |
Nominal PV power, 12V 1a,b | 860W | 1000W | |
Nominal PV power, 24V 1a,b | 1720W | 2000W | |
Nominal PV power, 36V 1a,b | 2580W | 3000W | |
Nominal PV power, 48V 1a,b | 3440W | 4000W | |
Max. PV short circuit current 2 | 50A | 50A | |
Maximum PV open circuit voltage | 150V absolute maximum coldest conditions 145V start-up and operating maximum | ||
Peak efficiency | 98% | ||
Self-consumption | 12V: less than 35mA / 48V: less than 20mA | ||
Charge voltage 'absorption' | Default setting: 14.4V / 28.8V / 43.2V / 57.6V | ||
Charge voltage 'float' | Default setting: 13.8V / 27.6V / 41.4V / 55.2V | ||
Charge voltage 'equalization' 3 | Default setting: 16.2V / 32.4V / 48.6V / 64.8V | ||
Charge algorithm | Multi-stage adaptive (eight pre-programmed algorithms) or user defined algorithm | ||
Temperature compensation | -16mV/°C / -32mV/°C / -64mV/°C | ||
Protection | PV reverse polarity / Output short circuit / Over temperature | ||
Operating temperature | -30°C to +60°C (full rated output up to 40°C) | ||
Humidity | 95%, non-condensing | ||
Maximum altitude | 5000m (full rated output up to 2000m) | ||
Environmental condition | Indoor type 1, unconditioned | ||
Pollution degree | PD3 | ||
Data communication | VE.Direct port 4 | ||
Remote on/off | Yes, 2 pole terminal | ||
Programmable relay | SPDT AC rating: 4A up to 240Vac / DC rating: 4A up to 35Vdc, 1A up to 60Vdc | ||
Parallel operation | Yes, but not synchronized | ||
ENCLOSURE | |||
Colour | Blue (RAL 5012) | ||
PV terminals | Tr models: 35 mm² / AWG2 MC4 models: 2 pairs of MC4 connectors 5 | ||
Battery terminals | 35 mm² / AWG2 | ||
Protection category | IP43 (electronic components), IP22 (connection area) | ||
Weight | 3kg | ||
Dimensions h x w x d | Tr models: 185 x 250 x 95mm MC4 models: 215 x 250 x 95mm | ||
STANDARDS | |||
Safety | EN/IEC 62109-1, UL 1741, CSA C22.2 | ||
1a) The solar charger will limit input power if more PV power is connected. 1b) The PV voltage must exceed Vbat + 5V for the controller to start. Thereafter the minimum PV voltage is Vbat + 1V. 2) A higher short circuit current may damage the solar charger in case of reverse polarity connection of the PV array. 3) Equalization is by default disabled. 4) For more information on data communication see the data communication paper in the Technical information section on our website. 5) MC4 models: several splitter pairs may be needed to parallel the strings of solar panels. Maximum current per MC4 connector is 30A. The MC4 connectors are internally parallel connected to a single MPPT tracker. | |||
9.2. Dimension drawings
9.2.1. Dimensions 60A-MC4 and 70A-MC4 BlueSolar

9.2.2. Dimensions 60A-Tr and 70A-Tr BlueSolar