ve.bus:ve.bus_error_codes
ve.bus:ve.bus_error_codes [2019-02-14 10:16] – martijncoster | ve.bus:ve.bus_error_codes [2019-02-14 20:45] – [Error 24 - Sw simonhackett | ||
Line 151: | Line 151: | ||
- There is too much AC load connected at the moment the relay needs to switch off. This large current will prevent the relay contacts from opening.\\ \\ Solution: remove excessive load. \\ \\ | - There is too much AC load connected at the moment the relay needs to switch off. This large current will prevent the relay contacts from opening.\\ \\ Solution: remove excessive load. \\ \\ | ||
- The AC input voltage slowly drops before it is being rejected by the Multis. Typically happens in installations with a genset. Especially when combined with AC loads that increase their current draw when the AC voltage drops: at the moment the Multis or Quattros decide to switch off, the current through the relays is too high to open them.\\ \\ Solution: Make the Multis or Quattros disconnect earlier: increase lower limit of AC input voltage in VEConfigure3. For example to 210 VAC. The factory setting is 180 VAC. \\ \\ | - The AC input voltage slowly drops before it is being rejected by the Multis. Typically happens in installations with a genset. Especially when combined with AC loads that increase their current draw when the AC voltage drops: at the moment the Multis or Quattros decide to switch off, the current through the relays is too high to open them.\\ \\ Solution: Make the Multis or Quattros disconnect earlier: increase lower limit of AC input voltage in VEConfigure3. For example to 210 VAC. The factory setting is 180 VAC. \\ \\ | ||
- | - The back-feed relay has a hardware failure | + | - The back-feed relay has a hardware failure \\ \\ Solution: Replace faulty unit. |
__Diagnostic notes for systems showing error 24 where a stuck ' | __Diagnostic notes for systems showing error 24 where a stuck ' | ||
- | In a single | + | In a single |
- | In a three-unit, three-phase cluster | + | This happens because the faulty |
- | You can also determine the faulty | + | To help identify which unit is faulty in this scenario, first un-wire the AC outputs of all the units concerned to prevent cross-feeding of AC energy via the AC outputs. Then apply AC power with all units still set to ' |
- | Where there are multiple units hardwired in parallel (a multi-unit/ | + | If this is not conclusive, try completely disconnecting all suspect |
- | The most conclusive way to determine which unit is faulty in this case is to un-wire the AC outputs of all the units concerned to prevent the cross-feeding of AC energy via the AC outputs. Then apply AC power with all units still set to ' | ||
==== Error 25 - Firmware incompatibility ==== | ==== Error 25 - Firmware incompatibility ==== | ||
Make sure to use the same firmware in all devices. | Make sure to use the same firmware in all devices. |
ve.bus/ve.bus_error_codes.txt · Last modified: 2024-04-24 00:32 by mleeftink