ModbusTCP FAQ
Introduction
ModbusTCP is a feature on our GX devices eg Color Control GX, and also the Venus GX. ModbusTCP is an industry standard protocol, that can be used to interface PLCs or other equipment with Victron products. For example to enable a heat pump when there is excess solar power, or create a fully integrated glass bridge on a yacht.
Through the ModbusTCP interface you can read and write date to the chargers, battery monitors, inverter/chargers and other products connected to the GX device. The unit-id combined with the register address is used as a device-selector: selecting for example from which device you want to read its battery voltage measurement.
Besides reading this FAQ, make sure to also read the ModbusTCP section in our Data communication whitepaper.
Supported ModbusTCP function codes
The supported function codes are:
- ReadHoldingRegisters = 3
- ReadInputRegisters = 4
- WriteSingleRegister = 6
- WriteMultipleRegisters = 16
Note that there is no difference between function code 3 and 4.
Product categories and registers
The ModbusTCP Registerlist xlsx file contains a column named 'dbus-service-name'. Consult this document to find out which set of registers are available for a product.
Note that besides device-specific registers, there is also a set of registers that represent the entire system: com.victronenergy.system. This service is also where the System Overview pages in the GUI, and the VRM Dashboard get their data.
| Device class | Product types | Registers |
| com.victronenergy.vebus | Inverters (VE.Bus), Multis, and Quattros | 3 to 60 |
| com.victronenergy.solarcharger | Solar chargers (both VE.Can and VE.Direct connected) | 771 to 790 |
| com.victronenergy.pvinverter | Grid-tie PV Inverters (Fronius, or Energy Meter) | 1026 to 1039 |
| com.victronenergy.battery | BMVs, CAN-Bus BMS connected batteries Extra parameter set for Lynx Ion and Lynx BMS product family | 259 to 319 1282 to 1301 |
| com.victronenergy.charger | Skylla-i and Skylla-IP44 | 2307 to 2322 |
| com.victronenergy.inverter | Inverters (with a VE.Direct connection) | 3100 to 3128 |
| com.victronenergy.tank | Tank levels | 3000 to 3005 |
| com.victronenergy.grid | Energy meters configured to measure the grid | 2600 to 2609 |
| com.victronenergy.gps | GPS | 2800 to 2807 |
| com.victronenergy.tank | Tank sensors | 3000 to 3007 |
| com.victronenergy.genset | Generators | 3200 to 3223 |
| com.victronenergy.temperature | Temperature sensors (1) | 3300 to 3305 |
| com.victronenery.meteo | IMT solar irradiation sensors | 3600 to 3603 |
(1): Check for compatible GX devices (eg Venus GX) that provide temperature sensor inputs. The battery temperature as measured by a sensor connected to a VE.Bus device is not available. And the battery temperature as measured by a sensor connected to a BMV battery monitor is available under the com.victronenergy.battery register set.
General note: not all list registers are available for each device. For example a BMV Battery Monitor has lots of readings: historical data such as maximum/minimum, for example. A canbus-connected lithium battery might not have those parameters available.
Error codes
| Code | Name | Description |
| 0x01 | IllegalFunction | The requested function is not supported. |
| 0x02 | IllegalDataAddress | The unit-id is available, but one or more of the requested register(s) does not exist. |
| 0x03 | IllegalDataValue | The requested quantity of registers is invalid. See the modbus specs, http://www.modbus.org/specs.php, for the limits per function code. |
| 0x0A | GatewayPathUnavailable | Unit-id is defined in the mapping list, but there is no device found on the mapped port. Double check the unit-id mapping list in the excel sheet, and make sure that the device is properly connected to the CCGX, switched on, and that its data is available on the CCGX display. |
| 0x0B | GatewayTargetDeviceFailedToRespond | Requested unit-id not found in the mapping list. Double check the unit id mapping list in the excel sheet. |
Mapping example
The purpose of this example is to show how to interpret the information in the worksheets of the excel sheet containing the modbustcp mapping. This excel sheet is available for download from our website on the Color Control page.
To request the input voltage of a Multi or Quattro, connected to the VE.Bus sockets on the CCGX, use the following settings: unit-id 246, and set the data address of the first request register to 3.
The ModbusTCP reply will contain 2302. Divide it by 10, as specified in cell E3, and then you have the voltage: 230.2 Volts AC.
Enabling ModbusTCP on the CCGX
By default, ModbusTCP is disabled. To enable it, go into the settings menu, scroll down to 'Services', and then enable the ModbusTCP service.
What is a unit-id and what do I need to set it to?
The unit-id, sometimes called ‘slave address’, specifies how a product connected to the CCGX needs to be addressed. Since Venus 2.40, this information is available on the CCGX under Settings → Services → Modbus/TCP → Available services.
Additionally this information is also documented on the ‘Unit ID mapping’ tab in the Modbus-TCP excel sheet.
For the overall system data, look for com.victronenergy.system in the excel sheet, and use unit-id 100.
Note that both unit-id 0 and unit-id 100 map to the same internal address. We recommend to use id 100, since many ModbusTCP clients and PLCs do not work with id 0.
Which products can be interfaced via Modbus TCP?
All products that can be connected to the Color Control GX.
Can I change a configuration setting in a Multi - for example: the absorption voltage?
No.
Can I request multiple registers at the same time?
Yes, you can! Though make sure not to include non existing registers in your query. Querying register 1 to 100 for example will not work, since registers 1 and 2 do not exist.
Can I implement more features myself?
Yes, you can! We are, slowly, making the Color Control code open source, and the Modbus-TCP sources are already available on https://github.com/victronenergy.
In a parallel or three-phase system, how can I address a single unit?
You cannot interface with them individually if they are configured for parallel-working; or as a three-phase system. Neither is it necessary to address units individually as ModbusTCP provides system-totals as well as 'per phase' information.
Will unit-id's change after a reboot or loss of power?
It may change in the case of VEdirect Devices connected via USB - but even then our experience is that it will only change in the first reboot.
Unit-id's for products not connected via USB will not change.
Advanced debugging
If all unit-id's and register-addresses have been checked and re-checked, and still the connection doesn't work, you could try looking at the modbustcp log file on the GX device.
Follow these steps:
- Login with SSH (use for example Putty in Windows - or simply type ssh root@[ip address here] on a Linux or Mac terminal console.
- List the latest log file:
cat /log/dbus-modbustcp/current | tai64nlocal
In case of any errors, the output will look like this:
2016-01-08 16:34:24.658248500 INFO 2016-01-08T16:34:24.657 [Server] New connecion: "141.138.140.60:41792" 2016-01-08 16:34:24.695846500 ERROR 2016-01-08T16:34:24.689 "Error processing function code 3, unit id 247, start address 258, quantity 42 :" "Unit id is available, but start address does not exist" 2016-01-08 16:34:24.753921500 INFO 2016-01-08T16:34:24.753 [Server] Disconnected: "141.138.140.60:41792"
In most cases the problem will be found in either the unit's id address; or the register addresses. Double check the numbers shown in the output with the numbers as used in your modbustcp software or PLC.
Does Modbus TCP support ESS?
Yes. See the ESS mode 2 and 3 manual for more details.
Add this page to your book
Manage book (
Help
