venus-os:gx_solaredge
venus-os:gx_solaredge [2019-05-22 00:03] – [2. How to configure] mvader | venus-os:gx_solaredge [2019-05-26 19:52] – [2. How to configure] mvader | ||
Line 5: | Line 5: | ||
You can connect your [[venus-os: | You can connect your [[venus-os: | ||
- | * Zero Feed-in for SolarEdge is not available when used with a Victron System, | + | * Zero Feed-in for SolarEdge is not available when used with a Victron System. |
* Frequency shift power control, as required in a [[ac_coupling: | * Frequency shift power control, as required in a [[ac_coupling: | ||
Line 11: | Line 11: | ||
In other sorts of systems, for example Off-grid systems, or ESS systems in areas where grid feed-in is not allowed, using a SolarEdge PV solution is not supported by Victron. | In other sorts of systems, for example Off-grid systems, or ESS systems in areas where grid feed-in is not allowed, using a SolarEdge PV solution is not supported by Victron. | ||
+ | Note that its not possible to use the SolarEdge Wattnode meter when used in a Victron ESS System. In laymans terms, doing so will put to captains on the same ship, both trying to regulate the power flow at the utility connection, which will fail / be unstable. | ||
===== 2. How to configure ===== | ===== 2. How to configure ===== | ||
- Ensure that the GX Device and the SolarEdge system are both on the same LAN or WiFi network. | - Ensure that the GX Device and the SolarEdge system are both on the same LAN or WiFi network. | ||
- Enable ModbusTCP support on your SolarEdge system. Consult the SolarEdge documentation for that. | - Enable ModbusTCP support on your SolarEdge system. Consult the SolarEdge documentation for that. | ||
+ | - The Modbus Device id has to be set at 126. Some SE inverters might have that by default. Changing it is done in the SE inverter menu, configuration, | ||
- On the GX Device, navigate to Settings -> PV Inverters. Search for the Solar Edge and complete the configuration. | - On the GX Device, navigate to Settings -> PV Inverters. Search for the Solar Edge and complete the configuration. | ||
+ | RS485-1 menu on the Solar Edge, showing the Device ID setting: | ||
Details: | Details: | ||
- | - The SE2200H - SE6000H range (HD-wave) was specifically tested, though others | + | - The SE2200H - SE6000H range (HD-wave) was specifically tested, though |
- | - The unit id is 126. | + | |
- During testing, we found that the SolarEdge PV Inverter accepts just one concurrent TCP connection. Additional connections are rejected. | - During testing, we found that the SolarEdge PV Inverter accepts just one concurrent TCP connection. Additional connections are rejected. |
venus-os/gx_solaredge.txt · Last modified: 2021-09-21 16:22 by fjlacock