ess:design-installation-manual [2019-07-01 13:23] – [4.3 Venus-device - ESS Settings] mvader | ess:design-installation-manual [2019-09-16 08:45] – pop | ||
Line 5: | Line 5: | ||
=== What is ESS? === | === What is ESS? === | ||
- | An Energy Storage System (ESS) is a specific type of power system that integrates a power grid connection with a Victron Inverter/ | + | An Energy Storage System (ESS) is a specific type of power system that integrates a power grid connection with a Victron Inverter/ |
It allows for time shifting power, charging from solar, providing grid support, and exporting power back to the grid. | It allows for time shifting power, charging from solar, providing grid support, and exporting power back to the grid. | ||
Line 11: | Line 11: | ||
When an ESS system is able to produce more power than it can use and store, it can sell the surplus to the grid; and when it has insufficient energy or power, it automatically buys it from from the grid. | When an ESS system is able to produce more power than it can use and store, it can sell the surplus to the grid; and when it has insufficient energy or power, it automatically buys it from from the grid. | ||
- | In the ESS system, there must at least be one inverter/ | + | In the ESS system, there must at least be one inverter/ |
Line 36: | Line 36: | ||
Configuring ESS in a system which uses a diesel generator as backup - for extended mains failures - can be achieved. Grid code and Loss of Mains configuration will need special attention, see [[ve.bus: | Configuring ESS in a system which uses a diesel generator as backup - for extended mains failures - can be achieved. Grid code and Loss of Mains configuration will need special attention, see [[ve.bus: | ||
- | And on the [[venus-os: | + | And on the [[venus-os: |
=== When not to use ESS === | === When not to use ESS === | ||
Line 70: | Line 70: | ||
+ | === Energy Storage System introduction, | ||
+ | A seperate document that provides further introductory information, | ||
=== Advanced control options === | === Advanced control options === | ||
Line 97: | Line 102: | ||
Note that ESS can only be installed on Multis and Quattros which feature the 2nd generation microprocessor (26 or 27). All new systems shipped have 2nd generation chips. | Note that ESS can only be installed on Multis and Quattros which feature the 2nd generation microprocessor (26 or 27). All new systems shipped have 2nd generation chips. | ||
- | === Venus-device === | + | === GX device === |
The system is managed by the [[https:// | The system is managed by the [[https:// | ||
Line 141: | Line 146: | ||
For a full or partial grid-parallel installation an Energy Meter can be installed in the main distribution panel between the grid and the installation. | For a full or partial grid-parallel installation an Energy Meter can be installed in the main distribution panel between the grid and the installation. | ||
- | https:// | + | https:// |
A grid meter is only // | A grid meter is only // | ||
Line 301: | Line 306: | ||
* When using a VE.Bus BMS and a Multi Compact, check the DIP switches: DIP switch 1 must be on, and DIP switch 2 must be off. | * When using a VE.Bus BMS and a Multi Compact, check the DIP switches: DIP switch 1 must be on, and DIP switch 2 must be off. | ||
- | ==== 4.3 Venus-device - ESS Settings ==== | + | ==== 4.3 GX device - ESS Settings ==== |
Navigate to Settings -> ESS, to see this menu: | Navigate to Settings -> ESS, to see this menu: | ||
Line 416: | Line 421: | ||
- | ==== 4.4 Venus-device - Scheduled Charging ==== | + | ==== 4.4 GX device - Scheduled Charging ==== |
=== 4.4.1 Introduction === | === 4.4.1 Introduction === | ||
- | The Scheduled Charging setting is located in the ESS menu of the [[venus-os: | + | The Scheduled Charging setting is located in the ESS menu of the [[venus-os: |
If the target state of charge is reached, and it is still within the period of time set, the battery will stop charging but will not discharge (unless there is grid outage). This optimises battery cycling and still allows room in the battery for PV charging. | If the target state of charge is reached, and it is still within the period of time set, the battery will stop charging but will not discharge (unless there is grid outage). This optimises battery cycling and still allows room in the battery for PV charging. | ||
Line 426: | Line 431: | ||
=== 4.4.2 Configuration === | === 4.4.2 Configuration === | ||
- | Scheduled charging is available as part of ESS. It is accessible on the [[venus-os: | + | Scheduled charging is available as part of ESS. It is accessible on the [[venus-os: |
You can see at a glance what is configured, with a summary of the start day, time and duration shown for each. | You can see at a glance what is configured, with a summary of the start day, time and duration shown for each. | ||
Line 460: | Line 465: | ||
The first matching schedule takes priority. If the two schedules have different SOC limits, the limit of the second matching scheduled charge window takes effect after the first scheduled charge window ends. | The first matching schedule takes priority. If the two schedules have different SOC limits, the limit of the second matching scheduled charge window takes effect after the first scheduled charge window ends. | ||
- | ==== 4.5 Venus-device - Other settings ==== | + | ==== 4.5 GX device - Other settings ==== |
=== 4.5.1 Settings -> System setup -> AC Input types === | === 4.5.1 Settings -> System setup -> AC Input types === | ||
Line 858: | Line 863: | ||
=== Q7: How do the charge states work in ESS? === | === Q7: How do the charge states work in ESS? === | ||
- | * The MPPTs are always in the `ESS` state. This indicates that the MPPT is being controlled by the Multi or Quattro via the Venus-device. To view the system state, look at the VE.Bus State. | + | * The MPPTs are always in the `ESS` state. This indicates that the MPPT is being controlled by the Multi or Quattro via the GX device. To view the system state, look at the VE.Bus State. |
* While discharging, | * While discharging, | ||
* When in Float, the system will begin a new charge cycle when the battery voltage has been below the restart-voltage for a certain length of time. This voltage depends on the chosen battery type selected on the charger tab in VEConfigure: | * When in Float, the system will begin a new charge cycle when the battery voltage has been below the restart-voltage for a certain length of time. This voltage depends on the chosen battery type selected on the charger tab in VEConfigure: |
