ess:design-installation-manual [2019-04-03 13:27] – guy_stewart | ess:design-installation-manual [2019-05-27 14:33] – [6.5 ESS Battery Status Code Numbers] guy_stewart | ||
Line 349: | Line 349: | ||
Set to ' | Set to ' | ||
+ | Please note that when enabling this option, the DVCC charge current limit configured under Settings -> Limit charge current won't be active. The Solar charger will operate at full power for maximum feed-in into the grid. It's advisable to configure a safe limit on the solar chargers when used with a small battery bank. | ||
=== 4.3.5 Phase compensation === | === 4.3.5 Phase compensation === | ||
Line 606: | Line 608: | ||
(This 0.1 V is the threshold for 12 V systems; for 24 V the threshold is 0.2 V above; and for 48 V it is 0.4V above.) | (This 0.1 V is the threshold for 12 V systems; for 24 V the threshold is 0.2 V above; and for 48 V it is 0.4V above.) | ||
- | ==== 6.5 ESS Battery Status Code Numbers ==== | + | ==== 6.5 ESS Battery Status |
In addition to the charger states (Bulk/ | In addition to the charger states (Bulk/ | ||
Line 896: | Line 898: | ||
The same applies to other solutions where the wiring is not protected against accidental removing, for example a simple cable with end-user removable plug, such as a portable power supply. | The same applies to other solutions where the wiring is not protected against accidental removing, for example a simple cable with end-user removable plug, such as a portable power supply. | ||
+ | ===== Troubleshooting ===== | ||
+ | - Start with checking firmware versions (needs to be latest). And when asking questions; report the exact firmware versions that are used. | ||
+ | - Check battery type/brand. If lead then it might be unsuitable and probably broken because of the heavy cycling. | ||
+ | - If some unknown or unsupported CANbus battery; change the battery to a supported type. | ||
+ | Then; if PV is not used enough to power loads; | ||
+ | - Check for the # reason codes; see CODE KEY in this manual. | ||
+ | - Check wiring: lots of voltage drop between MPPT and multi will prevent the system from effectively powering AC loads from solar power. | ||
+ | - Test with and without SVS enabled. | ||
+ | - Next, check MPPT charge current limit during the time that it is not used enough. MPPT CCL is supposed to be high always; even when battery full. Unless there is a temperature issue. | ||
+ | - Now check MPPT Charge Voltage Setpoint. It is supposed to be above actual battery voltage. | ||
+ | Note that those last two setpoints are determined by software; and calculated based on the setpoints sent by the (CANbus connected) lithium battery: you can't change change them manually. Looking at them however does help understanding why certains things are happening; | ||
~~DISQUS~~ | ~~DISQUS~~ |