battery_compatibility:pylontech_phantom [2018-12-30 16:17] – guy_stewart | battery_compatibility:pylontech_phantom [2023-11-13 14:41] (current) – external edit 127.0.0.1 | ||
- | ====== Victron & Pylontech | + | ====== Victron & Pylontech |
Line 7: | Line 7: | ||
This manual is intended to be used in conjunction with the product manual supplied by Pylontech. It provides additional and specific information regarding integration with Victron systems. | This manual is intended to be used in conjunction with the product manual supplied by Pylontech. It provides additional and specific information regarding integration with Victron systems. | ||
- | The Pylontech includes a Battery Management System (BMS) with each battery module. This interfaces with the Victron [[venus-os: | + | The Pylontech includes a Battery Management System (BMS) with each battery module. This interfaces with the Victron [[venus-os: |
===== 1. Product & system compatibility ===== | ===== 1. Product & system compatibility ===== | ||
Line 13: | Line 13: | ||
- | ^ Battery ^ | + | ^ Battery ^ UP2500* |
- | | Module capacity| | + | | Nominal voltage |
+ | | Module capacity | ||
+ | | Minimum Venus firmware | v2.40 | v2.20 | v2.20 | v2.20 | **imminent** | v2.20 | | ||
+ | * Note that UP2500 came in two versions, UP2500N__A__01V00101 does not have a CANBUS port, and IS NOT supported by Victron. UP2500N__B__01V00101 released April 2020 has the CANBUS port and IS supported. | ||
Line 20: | Line 24: | ||
Victron + Pylontech can be used for the following system types: | Victron + Pylontech can be used for the following system types: | ||
- | * Off-grid | + | * Off-grid |
- | * Grid Backup | + | * Grid Backup |
- | * Energy Storage Systems - Self Consumption ([[ess: | + | * Energy Storage Systems |
+ | === 1.2 A GX-device is required, eg Cerbo GX or Venus GX (VGX) === | ||
- | === 1.2 A Venus-device | + | It is essential to use the CAN-bus connection of the [[venus-os: |
- | It is essential to use the CAN-bus connection of the [[venus-os: | + | For new systems, |
- | The minimum required firmware version for the [[https:// | + | Legacy |
- | In grid connected systems, advanced control functions are configurable in the ESS settings on the [[venus-os: | ||
- | In off-grid systems, the system control functions from the Pylontech Battery Management System (BMS) are built into the latest version of the [[venus-os: | + | === 1.3 All Multi, MultiPlus, MultiGrid and Quattro |
- | === 1.3 All 48V Multi, MultiPlus, MultiGrid | + | As long as you are using the appropriate model for the nominal battery voltage, all VE.Bus inverters |
- | The minimum firmware version is 422. Though updating to the latest firmware is recommended where possible. | + | The minimum firmware version |
+ | Legacy systems installed with VE.Bus firmware 422 can continue to be used without upgrade as long as they do not present any issues. | ||
- | === 1.4 All 48V VE.direct | + | === 1.4 All VE.Direct |
For proper operation, the Pylontech battery needs to be able to control the charge current. Therefor it is recommended to use Victron 48V compatible MPPTs models with VE.Direct port for charging. | For proper operation, the Pylontech battery needs to be able to control the charge current. Therefor it is recommended to use Victron 48V compatible MPPTs models with VE.Direct port for charging. | ||
Line 48: | Line 54: | ||
- | Use of VE.Can MPPT' | + | New Model (2019 and later) VE.Can MPPTs are also supported from firmware version 1.06 and above. Be aware that some GX devices (e.g. CCGX) only have a single CANBus interface, and that is required for the battery communications. So if you use a new VE.Can MPPT, it must also be with a GX device that has more than one CANbus interface, e.g. the Cerbo GX. |
+ | Old model VE.Can MPPTs (pre 2019) are not supported. | ||
===== 2. Minimum Battery Sizing Recommendations | ===== 2. Minimum Battery Sizing Recommendations | ||
- | + | Once DVCC is enabled on the GX device, the charge and discharge rates are managed by the Pylontech battery. | |
- | Each US2000B Plus battery module | + | |
- | The charge and discharge rates are managed | + | |
Using very large solar arrays with battery banks that are too small can exceed the limits of the batteries ability to charge and possibly lead to the BMS triggering over-current alarms. | Using very large solar arrays with battery banks that are too small can exceed the limits of the batteries ability to charge and possibly lead to the BMS triggering over-current alarms. | ||
- | You must have the minimum number of units to supply the potential current | + | You must have the minimum number of battery modules |
+ | It is much more desirable to have the inverter/ | ||
+ | These minimum battery sizings are required for reliable operation. | ||
- | Some suggested | + | An example of minimum system sizing based on the US2000 |
^ Inverter / Charger Model ^ Inv continuous watts @ 25 degrees ^ Inverter peak watts surge rating ^ Number of Pylontech modules ^ Battery continuous discharge watt rating ^ Battery peak discharge watt rating ^ | ^ Inverter / Charger Model ^ Inv continuous watts @ 25 degrees ^ Inverter peak watts surge rating ^ Number of Pylontech modules ^ Battery continuous discharge watt rating ^ Battery peak discharge watt rating ^ | ||
Line 79: | Line 87: | ||
Line 89: | Line 96: | ||
You can connect multiple battery modules together to form a single large battery by connecting the RJ-45 cable supplied by Pylontech using the link ports on the battery. This is shown in more detail in the [[https:// | You can connect multiple battery modules together to form a single large battery by connecting the RJ-45 cable supplied by Pylontech using the link ports on the battery. This is shown in more detail in the [[https:// | ||
- | The batteries will automatically detect | + | The communications for UP2500 can be paralleled up to 20 modules per string (and cannot use the LV-HUB). Other models can connect up to 8 battery modules (see Pylontech data sheets), in those models when using more than 8 parallel units, some limitations, |
- | The battery with the empty link port 0 is the master battery. Using the // | + | The batteries will automatically detect and link to each other, no adjustment |
- | Then, plug a [[https:// | + | The battery with the empty link port 0 is the master battery. |
+ | ** Important note on DIP switches ** | ||
+ | No adjustment to the DIP switches is necessary, unless you are using a LV-Hub to connect a large number of modules. The address DIP-switches must be set to 000 for correct operation, and the GX device will not detect the battery if you use any other setting. Larger batteries using an LV-Hub is discussed later in this document. | ||
+ | **Type A cable** | ||
+ | The Victron //VE.Can to CAN-bus BMS type A Cable//, part number ASS030710018 is used for connection with US2000C / US3000C / UP5000 / US5000 / US5000B / Force-L. | ||
+ | **Type B cable** | ||
+ | The Victron //VE.Can to CAN-bus BMS type B Cable//, part number ASS030720018 is used for connection with US2000 / US3000 / UP2500; | ||
+ | Note you cannot use the comms cable supplied by Pylontech for this connection between the master battery and the GX device. | ||
+ | **Connections** | ||
+ | Plug the communication cable with the side which is labeled Battery BMS into the Pylontech CAN port of the master battery. | ||
+ | Some GX devices (such as the Cerbo GX), have multiple CAN ports. If your GX device has a BMS-Can port, this should be used. If your GX device ONLY has VE.Can ports, you will need to change the VE.Can port profile to CAN-bus BMS (500 kbit/s) for the battery (and then it cannot be used for other VE.Can devices). | ||
+ | Plug the side labeled Victron VE.Can into the [[venus-os: | ||
+ | ===== 4. GX Device Settings ===== | ||
+ | When the Pylontech battery is connected to the BMS-Can port of a GX device (running v2.80 and later) the following DVCC settings will be set and enforced automatically. | ||
+ | If you are running a GX firmware version prior to this, these will need to be manually configured. | ||
+ | === Manual Configuration === | ||
+ | On the [[venus-os: | ||
+ | * If your GX device has a BMS-Can port, the battery should be connected to this. | ||
+ | * If you connect the BMS to the VE.Can port you will need to adjust the port speed. Select the //CAN-bus BMS (500 kbit/s)// CAN-profile in the GX device. Menu path: //Settings -> Services -> VE.CAN port//. | ||
+ | After properly wiring and setting the correct CAN-bus speed, the Pylontech will be visible as a battery in the device list. If you have multiple batteries a single entry will show up, which represents all batteries: | ||
+ | Next, go to Settings, DVCC, and configure as follows: | ||
+ | ^Venus Settings -> System Setup Parameter ^ Value ^ | ||
+ | |DVCC|ON| | ||
+ | For more information about the behaviour of DVCC, please see the [[https:// | ||
+ | === Additional optional controls === | ||
+ | Note: The "Limit managed battery charge voltage" | ||
+ | The 'limit charge current' | ||
+ | For example if you only wired in 80A capacity wire / fuses through the system, and didn't want the potential combined power delivery of a generator charging as well as a solar charge, you could limit the total system charging (MPPT + MultiPlus) to that lower level, even though the batteries could potentially absorb more. | ||
+ | === Other information === | ||
+ | The parameters option within the battery page shows the battery charge and discharge limits as communicated to the DVCC system by the BMS. | ||
+ | The ' | ||
+ | This parameters page is also a good place to check that all batteries are connected and working properly. The battery data sheet specifies the normal working conditions, e.g. the current limit per cell. For example, If each battery is rated to 25A charge current, and the menu shows a 75A charge current limit ( 75 / 25 = 3 ) means there are 3 Pylontech battery modules connected. | ||
+ | In off-grid systems, the inverter will prioritise running the load, and potentially exceed this Discharge Current Limit. This could lead to the battery shutting down, and why it is important to follow the minimum battery sizing guide. | ||
+ | In grid connected ESS systems, the inverter will do its best to respect the Discharge Current Limit and use the grid to supplement the load if required. | ||
+ | Note that ' | ||
- | It is important to ensure this connection and display of the battery on the [[venus-os: | + | The firmware |
+ | ^ Product ^ Firmware version ^ | ||
+ | | LV HUB | v1.8 | | ||
+ | | US2000B | v2.9 | | ||
+ | | US2000C & US3000C | v2.1 | | ||
+ | | ForceL | v1.4 | | ||
+ | | US5000 & Pelio-L | All firmware versions | | ||
+ | ===== 5. VEConfigure Settings ===== | ||
- | ===== 4. VEConfigure Settings ===== | + | When using the latest firmware on all compatible connected devices, and once the battery module has been detected by the GX device, battery charging parameters (e.g. Maximum Charge Current, Target Battery Voltage, etc) are automatically configured by the Pylontech BMU, and communicated to the rest of the Victron components in the system via [[https:// |
- | You will need the latest firmware on all connected devices. | + | It is possible to override some of these automatic settings to provide additional limitations (e.g. reduce |
This section presumes familiarity with [[https:// | This section presumes familiarity with [[https:// | ||
- | === 4.1 General tab === | + | Voltages shown are for the 48V model, and should be scaled for the 24V model. The 24V model is an 8-series configuration while the 48V model is a 15-series configuration. Voltages should therefore be scaled by 8/15. |
+ | === 5.1 General tab === | ||
* Check the " | * Check the " | ||
- | * Set the battery capacity to the total capacity of the battery: eg 50Ah times the number of battery modules for the 2000B Plus model. | + | * Set the battery capacity to the total capacity of the battery: eg 50Ah times the number of battery modules for the US2000 |
* The other parameters (" | * The other parameters (" | ||
- | === 4.2 Charge Settings === | + | === 5.2 Charge Settings === |
- | | Battery type | Lithium | | + | | Battery type | Lithium | |
- | Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 53.0 V. | + | Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 51.0 V. |
+ | Note For off-grid use: ignore the 'bms assistant required' | ||
- | === 4.3 Inverter Settings === | + | === 5.3 Inverter Settings === |
^VEConfigure Inverter Parameter | ^VEConfigure Inverter Parameter | ||
- | |DC input low shut-down | 47V| | + | |DC input low shut-down | 44V| |
- | |DC input low restart | + | |DC input low restart |
- | |DC input low pre-alarm* | 48.5V| | + | |DC input low pre-alarm* | 48V| |
Line 157: | Line 253: | ||
=== Hardware Protection Points === | === Hardware Protection Points === | ||
- | In normal operation, the charge parameter limits are set by the Pylontech battery and communicated through the system by the [[venus-os: | + | In normal operation, the charge parameter limits are set by the Pylontech battery and communicated through the system by the [[venus-os: |
* Low Voltage: When the battery discharges to 44.5V or less, battery protection will turn on. | * Low Voltage: When the battery discharges to 44.5V or less, battery protection will turn on. | ||
Line 164: | Line 260: | ||
* Charging temperature range is from 0 to 50 degrees celsius. | * Charging temperature range is from 0 to 50 degrees celsius. | ||
* Discharge Current Limit set to 0A at 47V, inverter will turn off. | * Discharge Current Limit set to 0A at 47V, inverter will turn off. | ||
+ | * Over-charge and Over-discharge Current Limit 102A for 15 seconds, 200A for 0.1 seconds and 400A short circuit current. | ||
If operation is attempted outside the operating range, the battery will disconnect to protect itself. | If operation is attempted outside the operating range, the battery will disconnect to protect itself. | ||
- | ===== 5. Venus-device Settings ===== | ||
- | On the [[venus-os: | ||
- | ^Venus Settings -> System Setup Parameter ^ Value ^ | + | ===== 6. VE.Direct MPPT Settings ===== |
- | |DVCC|ON| | + | |
- | |Shared Voltage Sense |OFF| | + | |
- | * Select the //CAN-bus BMS (500 kbit/s)// CAN-profile in the CCGX. Menu path: //Settings -> Services -> CAN-profile// | + | |
- | * After properly wiring and setting up, the Pylontech will be visible as a battery in the device list. If you have multiple batteries a single entry will show up, which represents all batteries: | + | |
- | * The parameters option within the battery page shows the actual battery charge and discharge limits | + | |
- | This parameters page is also a good place to check that all batteries are connected and working properly. In normal working conditions, the current limit is 25A per cell. For example, 75A charge current limit ( 75 / 25 = 3 ) means there are 3 Pylontech battery modules connected. | + | |
- | ===== 6. VE-Direct MPPT Settings ===== | + | |
- | In normal operation the MPPT charge characteristics are governed by the [[venus-os: | + | In normal operation the MPPT charge characteristics are governed by the [[venus-os: |
- | The settings below are a precautionary measure. | + | The settings below can be set as a precautionary measure. |
^MPPT Parameter ^ Setting ^ | ^MPPT Parameter ^ Setting ^ | ||
- | |Absorption voltage | + | |Absorption voltage |
+ | Note for MPPT RS - the Remote Mode in VictronConnect must be set to Remote on/off, not BMS. | ||
===== 8. Troubleshooting ===== | ===== 8. Troubleshooting ===== | ||
+ | When the grid is connected there are two software controls to sustain voltage. The Minimum SOC (while grid is connected) set in the GX device, and the sustain voltage (set in the ESS assistant). | ||
+ | The GX device will remain on, as there is still DC voltage provided by the batteries for a while. | ||
- | As a safety precaution, | + | If instead |
- | You can then start the inverter/ | + | If you then reconnect a DC charge source, or AC input supply (grid or generator), after approximately 2 minutes |
- | === Step 1. Check that the Pylontech battery is visible on the Venus-device list === | + | === Step 1. Check that the Pylontech battery is visible on the GX device list === |
Line 218: | Line 307: | ||
* CAN-bus communication cabling between Pylontech and Victron system. Make sure that it is in the right way around. | * CAN-bus communication cabling between Pylontech and Victron system. Make sure that it is in the right way around. | ||
* Pylontech system is up and running (LEDs are on) | * Pylontech system is up and running (LEDs are on) | ||
Line 224: | Line 313: | ||
=== Step 2. Check that the Pylontech battery is ready for use === | === Step 2. Check that the Pylontech battery is ready for use === | ||
=== Step 3. Check the Pylontech manual === | === Step 3. Check the Pylontech manual === | ||
The Pylontech manual contains additional diagnostic and troubleshooting information, | The Pylontech manual contains additional diagnostic and troubleshooting information, | ||
- | ===== 9. FAQ ===== | ||
- | **The maximum charge and discharge current is limited to 25A, but the data sheet tells me the maximum is 100A.** | + | ===== 9. FAQ and Known Issues===== |
+ | ==== The maximum charge and discharge current is limited to 25A, but the data sheet tells me the maximum is 100A. ==== | ||
The maximum current is limited to keep the battery healthy and reach the 10 year guarantee. In off-grid, the inverter can draw more than the 25A limit to run the loads, make sure you have sufficient batteries installed to keep the load per battery around this limit. | The maximum current is limited to keep the battery healthy and reach the 10 year guarantee. In off-grid, the inverter can draw more than the 25A limit to run the loads, make sure you have sufficient batteries installed to keep the load per battery around this limit. | ||
- | **After charging the battery the charge current often changes between 0A and 25A.** | + | ==== After charging the battery the charge current often changes between 0A and 25A. ==== |
This is caused by cell balancing inside the battery. This happens with new batteries and after a deep discharge. | This is caused by cell balancing inside the battery. This happens with new batteries and after a deep discharge. | ||
+ | ==== My system isn't charging at the rated capacity, or my PV is shutting down ==== | ||
+ | Pylontech' | ||
+ | You can confirm if this is affecting your installation be entering the Pylontech Battery menu on your GX device, and then the Parameters Menu. This will report the Charge Current Limit (CCL) and Discharge Current Limit (DCL). This information is also logged in the advanced section of the VRM monitoring portal. | ||
+ | ==== My system only charges the battery to 52.4V ==== | ||
+ | When DVCC is enabled, the battery (via the CAN-bms) is responsible for the charge voltage. The Pylontech battery requests a charge voltage of 53.2V. We have however found that in practice this is too high. | ||
+ | The Pylontech battery has 15 cells in series, so 53.2V equates to 3.55V per cell. This is very highly charged and makes the system prone to go overvoltage. | ||
+ | It should also be noted that a LiFePO4 cell stores very little additional energy above 3.45V. | ||
+ | For this reason we opted to override the BMS and cap the voltage at 52.4V. This sacrifices almost none of the capacity and greatly improves the stability of the system. | ||
+ | ==== The battery won't charge to 100% ==== | ||
+ | Also see the question above. The state of charge of the battery is estimated based on the overall voltage and on how well balanced the internal cells are. Because we cap the battery voltage at 52.4V, the state of charge will sometimes rise very slowly once it reaches the mid-90s. This is normal and usually resolves over time. | ||
+ | The ' | ||
+ | ==== 'High voltage' | ||
+ | The 'high voltage' | ||
+ | In an ESS system, set it to 'keep batteries charged', | ||
+ | After sufficient time to balance the batteries, try increasing this value until it can be disabled again for normal operation. | ||
+ | If it is not possible to raise the voltage over time, and eventually disable this manual override: | ||
+ | 1: If you have 2 or more batteries in your system, you can try shutting down the system once it is as close to fully charged as possible, and then physically connecting the batteries in smaller groups (or even individually) so that balancing can occur on each individual battery without it being masked by the others connected in parallel. It may help you to see the indicator lights on the battery (if available on that model) to find which battery might be out of balance with the others. | ||
+ | 2: Contact your Pylontech dealer for further assistance (they can provide additional software to see individual cell level data), or assist with other potential solutions. | ||
Line 245: | Line 369: | ||
Further community discussion about installing and using Pylontech and Victron can found at [[https:// | Further community discussion about installing and using Pylontech and Victron can found at [[https:// | ||
+ | === LV-Hub specific information === | ||
+ | Please discuss large Pylontech systems that require the LV-Hub with your experienced Pylontech agent FIRST. These additional LV-Hub references are provided without any support or endorsement from Victron, and should not be assumed to be up to date. Defer to your experienced dealers recommendations. | ||
~~DISQUS~~ | ~~DISQUS~~ |
battery_compatibility/pylontech_phantom.1546183058.txt.gz · Last modified: 2018-12-30 16:17 by guy_stewart
