battery_compatibility:lg_chem_resu
| battery_compatibility:lg_chem_resu [2018-02-07 09:26] – martijncoster | battery_compatibility:lg_chem_resu [2025-06-02 07:37] (current) – [Compatible Victron products] guy_stewart | ||
| Line 1: | Line 1: | ||
| ====== Victron & LG Chem Resu ====== | ====== Victron & LG Chem Resu ====== | ||
| - | ==== Compatible Victron products | + | ==== Compatibility |
| - | The MultiPlus 48/ | + | **NOTE - This document is now End-of-Life and for archive purposes only.** |
| + | LG no longer supports the Resu models that were previously compatible. | ||
| + | The only Victron inverter/ | ||
| + | === A GX device is required (either Color Control GX (CCGX) or the VENUS GX) === | ||
| + | It is essential to use the CAN-bus connection of the [[venus-os: | ||
| + | The minimum required firmware version for the [[https:// | ||
| - | And always a [[https:// | ||
| ==== Notes ==== | ==== Notes ==== | ||
| Line 11: | Line 20: | ||
| * It can only be used in On-grid systems, for self-consumption. Not for off-grid systems. | * It can only be used in On-grid systems, for self-consumption. Not for off-grid systems. | ||
| * Derating, based on the dynamic LG Resu charge- and discharge limits: | * Derating, based on the dynamic LG Resu charge- and discharge limits: | ||
| - | * Minimum CCGX version is v1.72 | + | * Minimum CCGX version is v2.15 |
| * The derating mechanism is not very precise yet. In other words, do not expect a discharge limit of 30A to result in a precise discharge of 30A. | * The derating mechanism is not very precise yet. In other words, do not expect a discharge limit of 30A to result in a precise discharge of 30A. | ||
| * Actual charge- and discharge limits are visible in the Parameters page. See screenshot below. | * Actual charge- and discharge limits are visible in the Parameters page. See screenshot below. | ||
| - | * LG batteries | + | * LG batteries |
| * LG battery policy is to only charge the battery to 97% or 98%. It is normal for the battery not to charge to 100%. | * LG battery policy is to only charge the battery to 97% or 98%. It is normal for the battery not to charge to 100%. | ||
| - | ==== ColorControlGX or VenusGX | + | ==== GX device |
| - | To use the LG Chem Resu and Victron equipment, it is necessary to use a CCGX or VenusGX. It takes care of sending the necessary canbus keep-a-live message to the LG Resu. Without it, the LG Resu will open its internal circuitbreaker after 10 minutes. | + | To use the LG Chem Resu and Victron equipment, it is necessary to use a [[venus-os: |
| + | Do not attempt firmware updates using the LG Chem battery for power until you can confirm that the battery is connected and showing on the [[venus-os: | ||
| ==== Wiring of communication cables ==== | ==== Wiring of communication cables ==== | ||
| - | se the //VE.Can to CAN-bus BMS type B Cable//, part number ASS030720018. Plug the side which is labeled Battery BMS into the LG Chem Resu BMS. Plug the side labeled Victron VE.Can into the Venus-device. | + | Use the //VE.Can to CAN-bus BMS type B Cable//, part number ASS030720018. Plug the side which is labeled Battery BMS into the LG Chem Resu BMS. Plug the side labeled Victron VE.Can into the [[venus-os: |
| Then, plug a [[https:// | Then, plug a [[https:// | ||
| Line 36: | Line 47: | ||
| === General tab === | === General tab === | ||
| - Check " | - Check " | ||
| - | - Set the battery capacity to 50Ah times the number of battery modules. | ||
| - Enter the battery capacity: | - Enter the battery capacity: | ||
| - Resu 6.4 - 126 Ah | - Resu 6.4 - 126 Ah | ||
| Line 50: | Line 60: | ||
| | Battery type | Lithium | | Battery type | Lithium | ||
| | Charge curve | Fixed | Fixed | | | Charge curve | Fixed | Fixed | | ||
| - | | Absorption voltage | + | | Absorption voltage |
| - | | Float voltage | + | | Float voltage |
| | Absorption time | 1 Hr | 1 Hr | | | Absorption time | 1 Hr | 1 Hr | | ||
| Note: make sure to double check the float voltage after completing Assistants. | Note: make sure to double check the float voltage after completing Assistants. | ||
| - | === Hub-4 Assistant === | + | === ESS Assistant === |
| Select the fourth battery type: | Select the fourth battery type: | ||
| Line 63: | Line 73: | ||
| Then: | Then: | ||
| - Sustain voltage: 50V | - Sustain voltage: 50V | ||
| - | - Do not change the dynamic cut-off values, | + | - The dynamic cut-off values |
| - | - Same for the restart offset | + | - Leave the default |
| ==== Color Control GX Configuration ==== | ==== Color Control GX Configuration ==== | ||
| Line 90: | Line 99: | ||
| - Restore the battery top cover again. | - Restore the battery top cover again. | ||
| - Switch the Multis/ | - Switch the Multis/ | ||
| ===== DISQUS ===== | ===== DISQUS ===== | ||
| ~~DISQUS~~ | ~~DISQUS~~ | ||
battery_compatibility/lg_chem_resu.1517995619.txt.gz · Last modified: by martijncoster