battery_compatibility:exide
battery_compatibility:exide [2022-07-18 12:13] – created dfaber | battery_compatibility:exide [2022-08-15 13:45] (current) – dfaber | ||
- | ====== | + | ====== Victron & Exide ===== |
+ | **This combination depends on Venus OS v2.90 or above, which is scheduled to be released later in 2022. Or the latest beta (see [[ccgx: | ||
The combination of Victron products with the Exide battery has been tested and certified by the R&D departments. The combination is actively supported by both companies. | The combination of Victron products with the Exide battery has been tested and certified by the R&D departments. The combination is actively supported by both companies. | ||
Compatible models: | Compatible models: | ||
- | * LIBM0480050-G01 as of firmware v1.10 | + | * Sonnenschein Module Pro LIBM0480050-G01 as of firmware v1.10 |
Line 11: | Line 15: | ||
All 48V Multis and Quattros. And always a [[venus-os: | All 48V Multis and Quattros. And always a [[venus-os: | ||
- | === 1.2 Notes === | ||
- | === 1.3 System diagram === | ||
==== 2. GX device needed ==== | ==== 2. GX device needed ==== | ||
- | To use the Exide ESS in Victron system, it is necessary to use a Color Control GX or Venus GX. On first commissioning an external power supply (Not the 48V from the Exide-Battery) is needed. The GX device | + | To use the Exide ESS in Victron system, it is necessary to use a GX-device such as a Color Control GX, a Venus GX or a Cerbo GX. The GX device |
==== 3. Wiring of communication cables ==== | ==== 3. Wiring of communication cables ==== | ||
- | Use the //VE.Can to CAN-bus | + | A cable for the CAN-bus |
+ | [[venus-os: | ||
- | Then, plug a [[https:// | + | Exide batteries come with a CAN-bus terminator |
- | More information about the cable can be found in [[battery_compatibility: | + | |
Without properly connecting this cable, the battery will stop charging/ | Without properly connecting this cable, the battery will stop charging/ | ||
+ | * Check the " | ||
+ | * Set the battery capacity to the total capacity of the battery: the Ah capacity per module multiplied by the number of battery modules. | ||
+ | * The other parameters (" | ||
+ | === 4.2 Charge Settings === | ||
+ | === Charger tab === | ||
+ | ^ Parameter | ||
+ | | Battery type | Lithium | | ||
+ | | Charge curve | Fixed | ||
+ | | Absorption voltage | ||
+ | | Float voltage | ||
+ | | Absorption time | 1 Hr | | ||
+ | Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 50.8 V. | ||
+ | === 4.3 Inverter Settings === | ||
+ | In the Inverter tab of VEConfigure | ||
+ | ^VEConfigure Inverter Parameter | ||
+ | |DC input low shut-down | 42V| | ||
+ | |DC input low restart | ||
+ | |DC input low pre-alarm* | 45V| | ||
+ | * The pre-alarm setting is dependent on your preference and on site specific requirements. You may wish for this to be activated earlier in an off grid situation to allow time to start a backup generator. | ||
+ | === 4.4 ESS System Settings === | ||
+ | If you are using the battery as part of a [[ess: | ||
+ | The settings that are specific to the EXIDE battery in the VEConfigure ESS Assistant are below: | ||
+ | Select the externally managed Lithium battery option | ||
+ | ^ ESS Parameter ^ Settings ^ | ||
+ | |Sustain voltage. | ||
+ | |Dynamic cut-off values | set all values to 43.5V.| | ||
+ | |Restart offset: | ||
+ | Due to the reliability of the grid supply and the behaviour of the sustain voltage threshold in ESS; you may wish to suppress the low voltage pre-alarm warning so that it does not trigger every day on its regular deep cycle. See [[https:// | ||
==== 5. GX device Configuration ==== | ==== 5. GX device Configuration ==== | ||
Line 34: | Line 78: | ||
* After properly wiring and setting up, the Exide ESS will be visible as a battery in the device list:{{ : | * After properly wiring and setting up, the Exide ESS will be visible as a battery in the device list:{{ : | ||
- | * The parameters option within the battery page shows the actual battery charge and discharge limits:{{ : | + | * The parameters option within the battery page shows the actual battery charge and discharge limits:{{ : |
+ | Next, go to Settings, DVCC, and configure as follows: | ||
+ | ^Venus Settings -> System Setup Parameter ^ Value ^ | ||
+ | |DVCC|ON| | ||
+ | ===== 6. MPPT Settings ===== | ||
+ | In normal operation the MPPT charge characteristics are governed by the [[venus-os: | ||
+ | This section presumes familiarity with [[victronconnect: | ||
+ | The settings below can be set as a precautionary measure, should the MPPT ever end up in standalone mode. | ||
+ | ^MPPT Parameter ^ Setting ^ | ||
+ | |Battery voltage. | ||
+ | |Absorption voltage |