ac_coupling:start
ac_coupling:start [2019-11-05 23:39] – external edit 127.0.0.1 | ac_coupling:start [2020-06-18 16:13] – [2.4 Should you look at the total PV array, or the PV inverter rating?] marmour | ||
Line 24: | Line 24: | ||
Line 38: | Line 38: | ||
**The max PV power must be equal or less than the VA rating of the inverter/ | **The max PV power must be equal or less than the VA rating of the inverter/ | ||
- | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi = 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etc. | + | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi >= 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etc. |
Line 51: | Line 51: | ||
Line 60: | Line 60: | ||
And for an undersized PV array, where the total Wp of installed PV panels is less than the installed PV grid inverter, you use the Wp from the PV panels in your calculation. | And for an undersized PV array, where the total Wp of installed PV panels is less than the installed PV grid inverter, you use the Wp from the PV panels in your calculation. |