ac_coupling:start
ac_coupling:start [2016-10-13 14:06] – [3. Sizing the battery] mvader | ac_coupling:start [2020-09-03 10:56] – removed accubank? guy_stewart | ||
Line 2: | Line 2: | ||
===== 1. Introduction to the AC-Coupling concept ===== | ===== 1. Introduction to the AC-Coupling concept ===== | ||
- | Already familiar with the concepts of AC-coupling and regulating PV inverter output power by frequency shifting? Skip to [[: | + | Already familiar with the concepts of AC-coupling and regulating PV inverter output power by frequency shifting? Skip to the requirements and limitations: |
Line 16: | Line 24: | ||
==== 1.2 What is frequency shifting? ==== | ==== 1.2 What is frequency shifting? ==== | ||
- | Frequency shifting is the ability | + | Frequency shifting is used to regulate |
- | How can a VE.Bus product configured | + | For how to configure, see chapter 4. |
- | Several options: | ||
- | - With the Self-consumption Hub-2 v3 assistant | ||
- | - PV Inverter support Assistant | ||
- | - Hub-4 Assistant in combination with the PV Inverter support Assistant | ||
- | - Use the Inverter period time settings on the Virtual switch tab. | ||
- | ===== 2. The 1.0 rule: Max PV power must be equal or less than the VA rating of the Multi ===== | + | ===== 2. The Factor |
+ | **The max PV power must be equal or less than the VA rating of the inverter/ | ||
- | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi = 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etcetera. | + | In both grid-connected and off-grid systems with PV inverters installed on the output of a Multi, Inverter or Quattro, there is a maximum of PV power that can be installed. This limit is called the __factor 1.0 rule__: 3.000 VA Multi >= 3.000 Wp installed solar power. So for a 8.000 VA Quattro the maximum is 8.000 Wp, for two paralleled 8000 VA Quattros the maximum is 16.000 Wp, etc. |
Line 47: | Line 51: | ||
Line 56: | Line 60: | ||
Line 62: | Line 66: | ||
===== 3. Minimum battery capacity ===== | ===== 3. Minimum battery capacity ===== | ||
- | Besides the relation between installed PV Power and the inverter/ | + | Besides the relation between installed PV Power and the inverter/ |
+ | Note that, besides the minimum battery capacity, the mentioned sizes are often also the most economical battery size. In case used for self-consumption purposes that is. In case the goal is to increase autonomy, of course installing a large battery increases the system autonomy in case of a grid failure. | ||
- | 1 kWp installed PV power requires: | + | 1 kWp installed PV power requires |
1,5 kWp installed PV power requires: | 1,5 kWp installed PV power requires: | ||
+ | ===== 4 Requirement of adding DC-Coupling - MPPT Solar Chargers ===== | ||
+ | Not required for Energy Storage Systems in Germany or other reliable grid situations. | ||
+ | Required for offgrid systems as well as backup systems that need to overcome extended grid failures. | ||
+ | Reason: recover from deadlock situation of AC-Coupling only situation. | ||
+ | ===== 5 Software configuration ===== | ||
+ | Multis and Quattros with factory settings will not shift the AC output frequency to regulate charge current. When setting up an AC Coupled system, install either the [[ess: | ||
+ | Other options, __all deprecated__, | ||
+ | - Self-consumption Hub-2 v3 assistant | ||
+ | - Hub-4 Assistant in combination with the PV Inverter support Assistant | ||
+ | - Use the Inverter period time settings on the Virtual switch tab. | ||
+ | See [[ccgx: | ||