MultiPlus-II 12V/24V/48V 3kVA 120V
8. Technical Specifications
In this section:
MultiPlus-II
12/3000/120-50
24/3000/70-50
48/3000/35-30
PowerControl & PowerAssist
Yes
Transfer switch
50 A
Maximum AC input current
50 A
INVERTER
DC Input voltage range
9,5 – 17 V
19 - 33 V
38 - 66 V
Output when in inverter mode
Output voltage: 120 VAC ± 2%
Frequency: 60 Hz ± 0,1% (1)
Cont. output power at 25°C (3)
3000 VA
2400 W
Cont. output power at 40°C
2200 W
Cont. output power at 65°C
1700 W
Maximum apparent feed-in power
2500 VA
Peak power
5500 W
Maximum efficiency
93%
94%
95%
Zero load power
13 W
13 W
11 W
Zero load power in AES mode
9 W
9 W
7 W
Zero load power in Search mode
3 W
3 W
2 W
Maximum output current
85 A peak, 70Arms for 1sec.
CHARGER
AC Input
Single phase: 90-140 VAC 45 – 65 Hz
Charge voltage 'absorption'
14.4 V
28.8 V
57.6 V
Charge voltage 'float'
13.8 V
27.6 V
55.2 V
Storage mode
13.2 V
26.4 V
52.8 V
Maximum battery charge current (4)
120 A
70 A
35 A
Battery temperature sensor
Yes
GENERAL
Auxiliary output
Yes (32 A)
External AC current sensor (optional)
100 A
Programmable relay (5)
Yes
Protection (2)
a – g
VE.Bus communication port
For parallel, split phase and three phase operation, remote monitoring and system integration
General purpose com. port
Yes, 2x
Remote on-off
Yes
Operating temperature range
-40 to +65°C (-40 - 150°F) fan assisted cooling
Humidity (non-condensing)
max 95%
ENCLOSURE
Material & Colour
Steel, blue RAL 5012
Protection category
IP22
Battery-connection
M8 bolts
M8 bolts
M8 bolts
120/240 V AC-connection
Screw terminals 13 mm² (6 AWG)
Weight
19 kg (42 lb)
Dimensions (hxwxd) mm
578 x 277 x 148
(23 x 11 x 6 inch)
536 x 277 x 147
(21 x 11 x 6 inch)
536 x 277 x 147
(21 x 11 x 6 inch)
STANDARDS
Safety
EN-IEC 60335-1, EN-IEC 60335-2-29
Emission, Immunity
EN 55014-1, EN 55014-2
EN-IEC 61000-3-2, EN-IEC 61000-3-3
IEC 61000-6-1, IEC 61000-6-2, IEC 61000-6-3
  1. Can be adjusted to 50 Hz
  2. Protection key:
    1. output short circuit
    2. overload
    3. battery voltage too high
    4. battery voltage too low
    5. temperature too high
    6. 120 VAC on inverter output
    7. input voltage ripple too high
  1. Non-linear load, crest factor 3:1
  2. At 75°F / 25°C ambient
  3. Programmable relay which can be set for general alarm, DC under voltage or genset start/stop function. AC rating: 120V / 4A, DC rating: 4A up to 35VDC and 1A up to 60VDC
  4. A. o. to communicate with a Lithium-Ion battery BMS
  5. The auxiliary output of an early production batch of this product was rated at 35A instead of 50A. This batch has serial numbers starting with HQ2107. Later batches, with 50A aux. output have serial numbers starting with HQ2114 or higher.