ve.bus:virtual-switch-generator-start-stop
ve.bus:virtual-switch-generator-start-stop [2019-01-28 06:40] – [1.1 MultiPlus and Quattro models of 3000VA and above] guy_stewartve.bus:virtual-switch-generator-start-stop [2019-09-13 14:03] (current) – [1.2 MultiPlus-II models] marmour
 ===== Virtual switch - Generator start/stop ===== ===== Virtual switch - Generator start/stop =====
-This document explains one of the ways to automatically start and stop a generator. See [[auto-generator-start-stop:start|here]] for the other options.+This document explains how to make a MultiPlus, Quattro, or other VE.Bus enabled inverter/charger, automatically start and stop a generator, by configuring the Virtual Switch option in VEConfigure. This is one of the available options to automatically start and stop a generator. See the [[auto-generator-start-stop:start|]] document for an overview of all options.
-More generator information about  using a generator in combination with Victron is available [[:multiplus_faq|here]].+More general information about  using a generator in combination with Victron is available [[:multiplus_faq|here]].
 ===== 1. Wiring ===== ===== 1. Wiring =====
Line 11: Line 11:
 ==== 1.1 MultiPlus and Quattro models of 3000VA and above ==== ==== 1.1 MultiPlus and Quattro models of 3000VA and above ====
-To do the wiring easily; be aware that its detachable: you can pull the block off; do the wiring; and then push it back on.+Be aware that this relay block is detachable. You can pull the block off, removing it from the board. This makes it easier to wire connections, and then push it back on.
 Note that there are three contacts; left to right: Normally Closed (NC) , Normally Open (NO), Common (COM). Note that there are three contacts; left to right: Normally Closed (NC) , Normally Open (NO), Common (COM).
Line 21: Line 21:
 ==== 1.2 MultiPlus-II models ==== ==== 1.2 MultiPlus-II models ====
-The connector is J in the picture. Left to right: NO, NC, COM.+The contact order for MultiPlus-II is left to right: NO, NC, COM.
-{{ :ve.bus:capture2.gif?600 |}}+{{:ve.bus:victron_multi2_relay.jpg?direct&600|}}
 ==== 1.3 MultiPlus 500VA to 1600VA models ==== ==== 1.3 MultiPlus 500VA to 1600VA models ====
-And, on our Multi 500, 800, 1200 and coming 1600, is contact E; here:+On our Multi 500, 800, 1200 and coming 1600, the order from left to right is COM, NC, NO.
 +Contact is here:
 +{{:ve.bus:victron_multi_relay_small.jpg?direct&600|}}
-{{ :ve.bus:capture3.gif?600 |}}
 ==== 1.4  MultiPlus Compact models ==== ==== 1.4  MultiPlus Compact models ====
-{{ :ve.bus:multiplus-compact.png?600 |}}+This relay block is also removable (by pulling) for easier wiring.
 +Contact order is NO, COM, NC
 +{{:ve.bus:victron_multicompact_relay_3.jpg?direct&600|}}
 +{{:ve.bus:victron_multicompact_relay_3_close.jpg?direct&600|}}
 ===== 2. Configuration ===== ===== 2. Configuration =====
-==== 2.1 enable the feature ====+==== 2.1 Enable the feature ====
 Open VEConfigure, navigate to the Virtual Switch, and there select 'dedicated generator control'. Open VEConfigure, navigate to the Virtual Switch, and there select 'dedicated generator control'.
Line 43: Line 51:
 {{ :ve.bus:veconfigure.png |}} {{ :ve.bus:veconfigure.png |}}
-==== 2.2 configure the feature ====+==== 2.2 Configure the feature ====
 Note that below are just example values; configure them to the match the type of batteries and rest of system. Note that below are just example values; configure them to the match the type of batteries and rest of system.
Line 50: Line 58:
 {{ :ve.bus:veconfigure2.png |}} {{ :ve.bus:veconfigure2.png |}}
ve.bus/virtual-switch-generator-start-stop.1548654023.txt.gz · Last modified: 2019-01-28 06:40 by guy_stewart