ve.bus:virtual-switch-generator-start-stop
Virtual switch - Generator start/stop
This document explains how to make a MultiPlus, Quattro, or other VE.Bus enabled inverter/charger, automatically start and stop a generator, by configuring the Virtual Switch option in VEConfigure. This is one of the available options to automatically start and stop a generator. See the Automatic Generator start/stop document for an overview of all options.
More general information about using a generator in combination with Victron is available here.
1. Wiring
The relay and connector block that needs to be wired to the generator control input is named the Alarm relay; in the various manuals.
1.1 MultiPlus and Quattro models of 3000VA and above
Be aware that this relay block is detachable. You can pull the block off, removing it from the board. This makes it easier to wire connections, and then push it back on.
Note that there are three contacts; left to right: Normally Closed (NC) , Normally Open (NO), Common (COM).
1.2 MultiPlus-II models
The contact order for MultiPlus-II is left to right: NO, NC, COM.
1.3 MultiPlus 500VA to 1600VA models
On our Multi 500, 800, 1200 and coming 1600, the order from left to right is COM, NC, NO. Contact is here:
1.4 MultiPlus Compact models
This relay block is also removable (by pulling) for easier wiring.
Contact order is NO, COM, NC
2. Configuration
2.1 Enable the feature
Open VEConfigure, navigate to the Virtual Switch, and there select 'dedicated generator control'.
2.2 Configure the feature
Note that below are just example values; configure them to the match the type of batteries and rest of system.
The ‘stop generator when AC2 available’ feature is for Quattros; used in a backup system with generator. Wire the generator to AC-in 1; and mains to AC-in 2. With that box checked; the system will automatically stop the generator once mains is available again.
ve.bus/virtual-switch-generator-start-stop.txt · Last modified: 2019-09-13 14:03 by marmour