ve.bus:ve.bus_error_codes
ve.bus:ve.bus_error_codes [2019-02-14 20:45] – [Error 24 - Sw simonhackett | ve.bus:ve.bus_error_codes [2024-02-05 07:37] (current) – mvader | ||
====== VE.Bus Error Codes ====== | ====== VE.Bus Error Codes ====== | ||
===== General ===== | ===== General ===== | ||
- | During first installation, | + | During first installation, |
Firmware update instructions: | Firmware update instructions: | ||
- [[updating_firmware: | - [[updating_firmware: | ||
- | - [[ccgx: | + | - [[ccgx: |
+ | **WARNING**: | ||
+ | ==== Network cable quality ==== | ||
+ | Make sure to use industrially made network cabling. Using self crimped RJ45 cables is a known cause of various of below list of errors. | ||
+ | This applies to network cables for split-, three phase and parallel systems as well as connecting a GX Device or other accessory on the VE.Bus network. | ||
===== VE.Bus Error Codes ===== | ===== VE.Bus Error Codes ===== | ||
==== Error 1 - Device is switched off because one of the other phases in the system has switched off ==== | ==== Error 1 - Device is switched off because one of the other phases in the system has switched off ==== | ||
- | One of the phases in a multi-phase system has failed. Commonly because of an Overload or High temperature alarm. When this happens, the other phases will show VE.Bus Error Code 1. | + | One of the phases in a multi-phase system has failed. Commonly because of a Low battery, |
Trouble shooting: | Trouble shooting: | ||
- | Look for the failing phase, which will be the phase that is not showing VE.Bus Error Code 1. And check the LEDs on that phase to find out what the reason was for the shut down. | + | |
+ | __ Diagnosing by LEDs__ | ||
+ | Look for the failing phase, which will be the phase that is not showing VE.Bus Error Code 1. And check the LEDs on that phase to find out what the reason was for the shut down; which is typically Overload, Low battery or Temperature. The other units will indicate a VE.Bus error, indicating that they miss one unit. | ||
+ | Note that, due to the automatic restart, it is required to look at the LEDs while the issue is still present and the system is switched off. | ||
+ | __Diagnosing on a GX Device__ | ||
+ | The GX Device will indicate the VE.Bus Error #1 as well as the alarm status for each of the phases: | ||
+ | Note that, due to the automatic restart, it is required to look at the LEDs while the issue is still present and the system is switched off. Uploading the data to VRM will show a log; see GX manual, section VRM for details; both for systems with internet connection and systems without. | ||
__Diagnosing on VRM__ | __Diagnosing on VRM__ | ||
First make sure that Automatic alarm monitoring is enabled; that is necessary to create the Overload and Temperature errors in the log. You will see Overload and Temperature alarms occurring at the same time as VE.Bus Error 1. | First make sure that Automatic alarm monitoring is enabled; that is necessary to create the Overload and Temperature errors in the log. You will see Overload and Temperature alarms occurring at the same time as VE.Bus Error 1. | ||
- | Note for split- and three-phase systems: VRM, nor the CCGX, will indicate on which phase the overload or the temperature alarm occured. To find out on which unit the error occurs, go to system after it has switched off. And look on the LEDs. The unit with the overload | + | Note for split- and three-phase systems: VRM as well as the GX device |
- | ==== Error 2 - New and old types MK2 are mixed in the system ==== | + | __Recovery: |
+ | ==== Error 2 - New and old type MK2 protocol | ||
+ | __Recovery: | ||
Line 31: | Line 55: | ||
- This error often follows VE.Bus Error 1. Solution: solve the cause for VE.Bus Error 1. Note that when using an older CCGX (version before v1.40), | - This error often follows VE.Bus Error 1. Solution: solve the cause for VE.Bus Error 1. Note that when using an older CCGX (version before v1.40), | ||
- | - Communication cable error: | + | - Communication cable error: |
Line 45: | Line 73: | ||
Line 50: | Line 80: | ||
Line 59: | Line 91: | ||
- | ==== Error 7 - VE.Bus BMS detected, but not configured ==== | + | This error can also occur in newer firmwares when a VE.Bus BMS is connected |
- | Solution: configure | + | __Recovery:__ auto-restart once the error is gone. |
+ | ==== Error 7 - External device connected, assistant required ==== | ||
+ | An external device (e.g. a VE.Bus BMS) is connected but there is no Assistant loaded which handles that device. | ||
+ | Solution: configure the Multi/ | ||
+ | ==== Error 8 - Ground relay test failed ==== | ||
+ | This error indicates a failed self-test of the MultiPlus-II or EasySolar-II internal< | ||
+ | | MultiPlus-II 48V 3kVA | ≤ HQ2048 | | ||
+ | | MultiPlus-II 48V 3kVA GX | ≤ HQ2050 | | ||
+ | | MultiPlus-II 24V 3kVA | ≤ HQ2101 | | ||
+ | | MultiPlus-II 48V 5kVA | ≤ HQ2116 | | ||
+ | | MultiPlus-II 48V 5kVA GX | ≤ HQ2122 | | ||
+ | | EasySolar-II 48V 3kVA MPPT 250-70 GX | ≤ HQ2130 | | ||
+ | This issue affects three phase systems only. | ||
This typically happens during a system restart, and is then not a real error; no need to investigate. | This typically happens during a system restart, and is then not a real error; no need to investigate. | ||
- | For example this screenshot from the Color Control | + | For example this screenshot from the GX device: |
Line 74: | Line 201: | ||
Note: System restarts can also be triggered when using Remote VEConfigure. | Note: System restarts can also be triggered when using Remote VEConfigure. | ||
+ | Other possibility: | ||
+ | DC fuse blown of one or more units in the system. When mains is available all units seems to work correctly, but as soon as mains fails, the non powered units are disconnected from the system. | ||
==== Error 11 - Relay Test Fault - Installation error or possibly relay failure ==== | ==== Error 11 - Relay Test Fault - Installation error or possibly relay failure ==== | ||
- | This error only applies to the MultiGrid, | + | Error 11 indicates a failed automatic self-test of the MultiPlus-II |
- | The relays are tested when a grid code is selected in VEConfigure. When the grid-code is set to None, the tests are not performed. | + | If a grid code is selected in VEConfigure, then the backfeed relays are tested every time before connecting |
- | When VE.Bus error 11 shows, either the back-feed relay test, ground relay test, or measurement redundancy tests has failed. The tests are automatically performed every time before connecting | + | === Steps to take: === |
- | The three root causes of the error can be (from most common | + | Step 1: Make sure that the units have been [[updating_firmware: |
- | 1) In most cases, when you see Error 11, its due to an installation error:\\ | + | Step 2: Verify |
- | * Please verify | + | |
- | * Line should be connected | + | |
- | * There should be no external connection between N-out and GND | + | |
- | 2) For Australia: contact your distributor. | + | Step 3: Disconnect the L and N wiring from the ACout terminals on each inverter/ |
- | 3) Hardware defect; contact | + | Step 4: Check your Neutral-out connection. In most cases there should be no external connection between ACin-Neutral to ACout-Neutral, |
+ | In Australia, using grid code AS4777.2: | ||
+ | After configuration, | ||
+ | Step 5: Neutral and line input might be inverted. Check the input connections, | ||
=== Detailed diagnosis of Error 11 === | === Detailed diagnosis of Error 11 === | ||
- | After updating your VE.Bus inverter/ | ||
- | [TODO; add image here] | + | After updating your VE.Bus inverter/ |
- | {{ :ve.bus:error11-ccgx1.jpg? | + | |
- | {{ :ve.bus: | + | Examples of information in the GX Device menus: |
+ | The information shown is: | ||
- | It shows: | ||
* A six digit number; which contains all the details | * A six digit number; which contains all the details | ||
- | * A counter | + | * An error ID (#4 in above screenshot). Note that this does not count the number of VE.Bus errors; its just a unique ID that can help recognizing that a new error has occurred. |
* Flags | * Flags | ||
* The failed step; it counts backwards: step 9 -> 8 -> 7 and so forth. | * The failed step; it counts backwards: step 9 -> 8 -> 7 and so forth. | ||
Common causes: | Common causes: | ||
* Failing step #8: check that line and neutral have not been swapped. Unlike non-grid code installations; | * Failing step #8: check that line and neutral have not been swapped. Unlike non-grid code installations; | ||
- | * PE2 open error: | + | * AC0/AC1 mismatch and UMains |
+ | Other shown error details, listed below, are not related | ||
+ | * Failing steps #2-7. | ||
+ | * AC0 /AC1 mismatch. | ||
+ | * Communication error. | ||
+ | * UMains mismatch. | ||
+ | * Period Time mismatch. | ||
+ | * Drive of BF relay mismatch. | ||
+ | === Unable to solve? === | ||
+ | When the error persists after the all above steps, or when any other Failed step or extra explanation shows, then the unit may be faulty. Follow the [[https:// | ||
+ | ==== Error 12 - Config mismatch with 2nd mcu ==== | ||
+ | Some Multi models (e.g. MultiPlus-II) have two microcontrollers. | ||
+ | Certain configuration settings, as done with VEConfigure, | ||
+ | In very rare situations it can happen | ||
+ | To solve this error, connect the device to VEConfigure 3, verify/ | ||
+ | Make sure to select the option 'all settings' | ||
+ | __Recovery:__ auto-restart once the error is gone. | ||
- | In all other cases, contact your Victron representative for support. Please provide a photo of the error; and otherwise the 6 digit number at the top. | ||
Line 121: | Line 286: | ||
+ | A combination error of VE.Bus products, firmware versions or commands has occurred | ||
+ | * An Interface-1140 with old firmware is combined with a new Multi firmware | ||
+ | * When external BMS commands are send while a VE.Bus BMS is connected | ||
+ | * The connected VE.Bus product firmware versions are incompatible. (This can in most cases be solved by updating the firmware.) | ||
Line 127: | Line 304: | ||
- | ==== Error 17 - Original Master Missing | + | __Recovery: |
+ | ==== Error 17 - Phase master missing | ||
+ | Error 17 shows on slaves (only). The slaves in a system will report this error when the communication with the phase-master has timed out. | ||
This error can only occur on systems with multiple devices installed per phase. For example a single phase installation with two or more devices in parallel, or a three-phase installation with six or more devices. | This error can only occur on systems with multiple devices installed per phase. For example a single phase installation with two or more devices in parallel, or a three-phase installation with six or more devices. | ||
- | Error 17 will only appear | + | Steps to take: |
+ | - In some cases this error can be seen temporarily while using Remote VEConfigure to write a new configuration. \\ __Solution__: | ||
+ | - The most likely cause is a cable-related communication issue on the VE.Bus network: \\ __Solution__: | ||
+ | - DC fuse blown. In this case, all units can in some situations seem fine and work well as long as mains is available. And then when there is no longer | ||
+ | - Update firmware and Assistants of the inverter/ | ||
- | * In some cases this error can be seen temporarily while using Remote VEConfigure to write a new configuration. | + | === Systems with multiple slaves per phase === |
- | * Otherwise, the most likely cause is bad cabling/ | + | Error 17 can show on one or more slaves in a phase (visible by looking at the LEDs, not on VRM or GX Device). If the slaves can still communicate with each other; then the error will only show on one slave: all slaves that can see on the network that another slave is already showing Error 17 will not show the error as well. |
+ | === Unable to solve it? === | ||
+ | If after all above steps you are still experiencing a VE.Bus | ||
+ | ==== Error 19 - Slave does not have AC input! ==== | ||
+ | Common cause - System is configured with multiple synchronised inverter/ | ||
+ | Solution: Either connect the AC input to all units, or change the configuration of the synchronised units in VE.Bus System Configurator (note not VEConfigure), | ||
- | There is a back-feed (or ' | ||
- | Error 24 is raised when a Multi or Quattro detects | + | This error indicates that one or more units report feeding back a significant |
- | This should not occur in a correctly installed and sized system. Possible causes | + | What is the back-feed relay? It is the relay that closes when connecting to the grid or generator. And which opens when there is no power available, ie when the system is in island- or invert-mode. |
- | - There is too much AC load connected at the moment the relay needs to switch off. This large current will prevent the relay contacts from opening.\\ \\ Solution: remove excessive load. \\ \\ | + | Error 24 is raised when a Multi or Quattro detects |
- | - The AC input voltage slowly drops before it is being rejected by the Multis. Typically happens in installations with a genset. Especially when combined with AC loads that increase their current draw when the AC voltage drops: at the moment the Multis | + | |
- | - The back-feed relay has a hardware failure \\ \\ Solution: Replace faulty unit. | + | |
- | __Diagnostic notes for systems showing error 24 where a stuck 'on' | + | - The relay did not open. |
+ | - The related current measurement circuit is faulty. | ||
+ | - A multiplus II is used with an external current sensor connected, but the option | ||
- | In a single phase installation with two or more devices | + | Error 24 is a very rare error. Possible causes |
- | This happens because the faulty unit will be (incorrectly) supplying AC energy | + | * (only on MP II models |
+ | * There is too much AC load connected at the moment the relay needs to switch | ||
+ | * The AC input voltage slowly drops before it is being rejected by the Multis. Typically happens in installations with a generator. Especially when combined with AC loads that increase | ||
+ | * The back-feed relay has a hardware failure \\ __Solution__: | ||
+ | * The related current measurement circuit is faulty. \\ __Solution__: | ||
- | To help identify which unit is faulty in this scenario, first un-wire the AC outputs of all the units concerned to prevent cross-feeding of AC energy via the AC outputs. Then apply AC power with all units still set to ' | + | __Diagnosing a parallel, multi or split-phase system?__ |
- | If this is not conclusive, try completely disconnecting | + | Error 24 will always appear on all units at the same time. There is unfortunately no indication, |
+ | Do make sure to first, always double check option 1 and 2 in above list. Those are the common causes. In case that doesn' | ||
+ | Execute this procedure right after the error occurred; do not first reset the system. | ||
+ | __Step 1__ | ||
+ | Start with making a video of all units and their LED code. Do not first reset the system; and do not reset it after making the video either. | ||
+ | __Step 2__ | ||
+ | Completely disconnect | ||
+ | __Step 3__ | ||
+ | Now, with an ohm-meter, measure the resistance between the neutral terminals on AC-input and the AC-output, A working unit will show no connection between these terminals. | ||
+ | A faulty unit will measure zero or close to zero resistance. | ||
+ | Good units will measure discontinuity between the Line in and out terminals. And measure | ||
==== Error 25 - Firmware incompatibility ==== | ==== Error 25 - Firmware incompatibility ==== | ||
Line 168: | Line 399: | ||
Solution: update all devices to the latest available firmware. Instructions [[updating_firmware: | Solution: update all devices to the latest available firmware. Instructions [[updating_firmware: | ||
Should not occur. Switch all equipment off, and then on again; it will then resume operation. Contact Victron Energy if the problem persists. | Should not occur. Switch all equipment off, and then on again; it will then resume operation. Contact Victron Energy if the problem persists. | ||
+ | ==== Error 128 - Connect prevented by failing relay test ==== | ||
+ | Relay test that keeps failing for more than 5 minutes, | ||
+ | If a grid code is selected in VEConfigure, | ||
+ | Error 128 indicates that the relay test keeps failing for more than 5 minutes, and the Quattro-II there for cannot connect to grid. | ||
- | ~~DISQUS~~ | ||
ve.bus/ve.bus_error_codes.1550173516.txt.gz · Last modified: 2019-02-14 20:45 by simonhackett