ve.bus:ve.bus_error_codes
Next revision Both sides next revision
ve.bus:ve.bus_error_codes [2019-08-19 10:30]
mvader
ve.bus:ve.bus_error_codes [2019-08-24 09:49]
mvader [Error 11 - Relay Test Fault - Installation error or possibly relay failure]
Line 90: Line 90:
 ==== Error 11 - Relay Test Fault - Installation error or possibly relay failure ==== ==== Error 11 - Relay Test Fault - Installation error or possibly relay failure ====
-This error only applies to the MultiGrid, MultiPlus-IIEasySolar-II and other inverter/chargers with a dual backfeed relayAs part of grid-code compliance; the device tests verifies that its internal relays function properly.+Error 11 indicates a failed automatic self-test of the MultiPlus-II or EasySolar-II relaysIt is often a result of an installation or wiring issue, though it can also be triggered by a hardware failures.
-The relays are tested when a grid code is selected in VEConfigure. When the grid-code is set to None, the tests are not performed.+If a grid code is selected in VEConfigure, then the backfeed relays are tested every time before connecting to the mains.
-When VE.Bus error 11 shows, either the back-feed relay test, ground relay test, or measurement redundancy tests has failed. The tests are automatically performed every time before connecting to mains.+The other relay tested by Error 11 is the ground relay. It is tested to be closed during inverter operation. And it is tested to open properly during switchover to mains. The ground relay tests are always performed: with or without a configured grid code.
-The three root causes of the error can be (from most common to least common):+=== Steps to take===
-1) In most cases, when you see Error 11, its due to an installation error:\\  +Step 1: Make sure that the units have been [[updating_firmware:updating_ve.bus_products|updated to the latest firmware version]]There have been various VE.Bus error 11 related improvements in the firmware.
-  * Please verify that the neutral is connected to earth on the supply sideIn many countries this is done by the utility in the transformer cabinet (a TN network). +
-  * Line should be connected to the corresponding Line input on the inverter/charger, same for Neutral. A swapped connection results in Error 11. +
-  * There should be no external connection between N-out and GND+
-2) For Australiacontact your distributor.+Step 2: Verify that system is properly wired to your installation and your local codes. Remember to check the earth connection on the unit AC input. Earth should be grounded according to your local grid rules. Do not connect Earth to Neutral on the unit. This will create a safety hazard and will prevent RCD devices from working. Contact a licensed electrician if in doubt
-3) Hardware defect; contact your distributor for a replacement.+Step 3: Disconnect the wiring from the ACout terminals on each inverter/charger. Which, in case of a parallel or three phase system, isolates the ACout connections for each unit. If the system then starts normally there might be a problem with a connected load (e.g. a leakage between load neutral and ground)
 +Step 4: Check your Neutral-out connection. There should be no external connection from Neutral-out to Neutral-in or to Earth. If your local grid code requires a bypass between Neutral-in and Neutral-out, contact your Victron representative for a solution.
 +Step 5: Neutral and line input might be inverted. Check the input connections, swap them if needed and retry. In this case, “Failing step: 8” will show.
 +=== Unable to solve? ===
 +When the error persists after the all above steps, or when any other Failed step or extra explanation shows, then the unit is most likely faulty. Follow the support procedure.
 +Make sure to provide a photo of the error details shown on the GX Device menu.
 === Detailed diagnosis of Error 11 === === Detailed diagnosis of Error 11 ===
-After updating your VE.Bus inverter/charger to firmware 454 or higher; and running Venus OS v2.23 or later, a detailed VE.Bus Error report can be seen in the GX device menu, under MultiPlus -> Alarm Status -> VE.bus error. The information shown is:+After updating your VE.Bus inverter/charger to firmware 454 or higher; and running Venus OS v2.23 or later, a detailed VE.Bus Error report is available in the GX device menu, under MultiPlus -> Alarm Status -> VE.bus error. The information shown is:
-It shows:
   * A six digit number; which contains all the details   * A six digit number; which contains all the details
   * An error ID (#16 for example). Note that this does not count the the number of VE.Bus errors; its just a unique ID that can help recognizing that a new error has occured.   * An error ID (#16 for example). Note that this does not count the the number of VE.Bus errors; its just a unique ID that can help recognizing that a new error has occured.
Line 119: Line 124:
   * Failing step #8: check that line and neutral have not been swapped. Unlike non-grid code installations; line and neutral need to be wired correctly.   * Failing step #8: check that line and neutral have not been swapped. Unlike non-grid code installations; line and neutral need to be wired correctly.
-  * PE2 open error: check that AC-out Neutral is not wired to Ground. Short circuiting them is not allowed. Also, check that there is no leakage between Neutral and ground, for example because broken consumer. Start by disconnecting all loads: open all the circuit breakers.+  * PE2 open error or GND Relay Error: check that AC-out Neutral is not wired to Ground. Short circuiting them is not allowed. Also, check that there is no leakage between Neutral and ground, for example because broken consumer. Start by disconnecting all loads: open all the circuit breakers.
   * AC0/AC1 mismatch and UMains error: there has been a fix for that in VE.Bus inverter/charger firmware version 455.   * AC0/AC1 mismatch and UMains error: there has been a fix for that in VE.Bus inverter/charger firmware version 455.
-In all other casescontact your Victron representative for supportPlease provide a photo of the error; and otherwise at least the 6 digit number at the top.+Other shown error details, listed below, are not related to any known installation issue and can be caused by a faulty unit or configuration issue. In any casealso when one of below errors shows, to go through all the above steps for any error 11 issue.
 +  * Failing steps #2-7.
 +  * AC0 /AC1 mismatch.
 +  * Communication error.
 +  * UMains mismatch.
 +  * Period Time mismatch.
 +  * Drive of BF relay mismatch.
 +  * PE2 open error.
 The report is found by navigating to the Device list (top level menu), then going in to the Multi or Quattro inverter/charger page, then to the bottom, Alarm Status, then to the bottom again, in to the menu VE.Bus Error 11 report. The report is found by navigating to the Device list (top level menu), then going in to the Multi or Quattro inverter/charger page, then to the bottom, Alarm Status, then to the bottom again, in to the menu VE.Bus Error 11 report.
 Now you will see a list of all devices in the system; and their latest VE.Bus Error 11 details. Enter the menu for an explanation of the code. Now you will see a list of all devices in the system; and their latest VE.Bus Error 11 details. Enter the menu for an explanation of the code.
 +Examples of information in the GX Device menus:
 {{ :ve.bus:error11-ccgx3.jpg?nolink |}} {{ :ve.bus:error11-ccgx3.jpg?nolink |}}
 {{ :ve.bus:error11-ccgx4.jpg?nolink |}} {{ :ve.bus:error11-ccgx4.jpg?nolink |}}
 +==== Error 12 - Config mismatch with 2nd mcu ====
 +Some Multi models (e.g. MultiPlus-II) have two microcontrollers.
 +Certain configuration settings, as done with VEConfigure, have to be stored in both microcontrollers.
 +In very rare situations it can happen that the stored configurations do not match and that the mismatch cannot be handled automatically. In this case error E12 will be generated.
 +To solve this error, connect the device to VEConfigure 3, verify/correct the settings and press 'Send Settings'.
 +Make sure to select the option 'all settings' instead of 'modified settings'.
 ==== Error 14 - Device cannot transmit data ==== ==== Error 14 - Device cannot transmit data ====
Line 143: Line 167:
 ==== Error 17 - Phase master missing ==== ==== Error 17 - Phase master missing ====
-Error 17 will only appear on slaves. They report this error when the communication with the phase-master has timed out.+Error 17 shows on slaves (only)The slaves in a system will report this error when the communication with the phase-master has timed out.
 This error can only occur on systems with multiple devices installed per phase. For example a single phase installation with two or more devices in parallel, or a three-phase installation with six or more devices.  This error can only occur on systems with multiple devices installed per phase. For example a single phase installation with two or more devices in parallel, or a three-phase installation with six or more devices.
Line 153: Line 177:
   - Update firmware and Assistants of the inverter/chargers. And of the GX Device. \\ __Solution__: [[updating_firmware:updating_ve.bus_products|Update the Inverter/charger firmware]] - [[assistants:how_to_update_an_assistant|Update the Assistants]] - [[ccgx:firmware_updating|Update the GX Device firmware]].   - Update firmware and Assistants of the inverter/chargers. And of the GX Device. \\ __Solution__: [[updating_firmware:updating_ve.bus_products|Update the Inverter/charger firmware]] - [[assistants:how_to_update_an_assistant|Update the Assistants]] - [[ccgx:firmware_updating|Update the GX Device firmware]].
-If after all above steps you are still experiencing a VE.Bus Error 17, contact your dealer whom will contact Victron repairs; please provide photos of the installation and network cabling. Depending on the situation, they might advice to replace the [[venus-os:start|GX device]] and the inverter/chargers. We advise to replace only the GX device first since that is less work.+=== Systems with multiple slaves per phase ===
 +Error 17 can show on one or more slaves in a phase (visible by looking at the LEDs, not on VRM or GX Device). If the slaves can still communicate with each other; then the error will only show on one slave: all slaves that can see on the network that another slave is already showing Error 17 will not show the error as well.
 +=== Unable to solve it? ===
 +If after all above steps you are still experiencing a VE.Bus Error 17, contact your dealer whom will contact Victron repairs; please provide photos of the installation and network cabling. Depending on the situation, they might advice to replace the [[venus-os:start|GX device]] and the inverter/chargers. We advise to first replace cables, and if that doesn't help then thereafter only the GX device at firstsince that is less work than replacing the inverter/chargers.
 ==== Error 18 - AC Over-voltage on the output of a slave while switched off ==== ==== Error 18 - AC Over-voltage on the output of a slave while switched off ====
ve.bus/ve.bus_error_codes.txt · Last modified: 2020-06-08 04:09 by guy_stewart