ve.bus:manual_parallel_and_three_phase_systems [2016-07-12 14:48] – [Configuration] pba | ve.bus:manual_parallel_and_three_phase_systems [2024-02-09 13:07] (current) – Removed “Weak LOM” setting. since that is currently the default jpasop | ||
+ | This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example, MultiPlus, Quattro and some larger VE.Bus inverters. | ||
+ | **IMPORTANT: | ||
+ | * Always update all units to the latest firmware version during commissioning of the system: ([[updating_firmware: | ||
+ | * Note that some parts of the description below apply only to firmware version 400 and later. | ||
+ | * All units in one system must be the same type and firmware version; this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | ||
+ | * Specify with your [[https:// | ||
+ | ===== Warning ===== | ||
+ | Parallel and Multiphase systems are complex. | ||
+ | Victron is able to provide specific training for these systems to [[https:// | ||
+ | These should all be considered essential before attempting design or installation. | ||
+ | First get experience with smaller systems. If you are new to Victron, please start with simpler designs, so that you become familiar with the necessary training, equipment and software required. | ||
+ | It is also recommended to hire an installer that has experience with these more complex Victron systems, for both the design and the commissioning. | ||
+ | ===== Maximum System size ===== | ||
+ | __Three phase systems__ | ||
+ | Using our 15kVA Quattros, the maximum system size is a 180kVA three phase system. Which then consists of four units on each of the three phases: 12 units in total. | ||
+ | When using smaller models, there is a maximum of five units in parallel, on each of the three phases: 15 units in total. For example, using 10kVA Quattros, the maximum system size is a 150kVA three phase system. | ||
+ | __Single phase systems__ | ||
+ | This is the same as above, but then per phase: | ||
+ | * maximum single phase system with 15kVA Quattros is 75kVA: five units. | ||
+ | * maximum single phase system with 10kVA Quattros is 60kVA: six units. | ||
- | This manual explains the details of designing, installing and configuring three-phase and parallel systems. | ||
- | Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section | + | |
+ | === Main text === | ||
+ | The VE.Bus cluster maintains a single ' | ||
- | For units in parallel: use one AC fuse for all units on that phase. | + | For units in parallel: Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section to every unit in the phase. To make this easy, use a bus-bar or power-post before and after the inverter/ |
+ | With regards to AC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. Consider using mechanically connected fuses. | ||
+ | With regards to DC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. | ||
+ | Beware of phase rotation between the inverter and AC in. When wired in a rotation | ||
+ | === Warning against over-dimensioning the AC wiring === | ||
+ | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects. | ||
+ | Technical background: for a properly working parallel system, the AC current should be evenly distributed between the paralleled units. The resistance in the cabling helps with that and is needed for that; to overcome small differences between one inverter/ | ||
+ | An exaggerated example: | ||
+ | * Using the same 2 units in parallel with, for the sake of this example underdimensioned AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | ||
+ | A side effect of over dimensioning the AC cabling can be faulty Power Assist operation. Out of all units, the phase master is in control and measuring the AC input current. And in case that current is (grossly) unevenly distributed between the paralleled units, the resulting total AC input current can end up being too low (under charging the battery). | ||
+ | === Delta configurations not supported === | ||
+ | === Theory and background information ==== | ||
+ | Wiring | ||
+ | * [[https:// | ||
- | For DC, one fuse per phase is best. If a big single fuse is not available, use one fuse per unit. Same type of fuse due to same resistance. | ||
- | Beware of phase rotation between the inverter and AC in. When wired in the wrong rotation, the system will not accept the mains input and only operates in inverter mode. In that case swap two phases to correct it. | ||
- | * All units must be daisy chained with the VE.Bus cable (RJ-45 cat5). The sequence for this is not important. Do not use use terminators in the VE.Bus network. | + | * All units must be daisy chained with the VE.Bus cable (RJ-45 cat5). The sequence for this is not important. Do not use terminators in the VE.Bus network. |
- | * Wire the voltage sense on the master of L1.\\ (If the system has more than 1 AC input, connect it to the Master corresponding to the first AC input. | + | * Wire the voltage sense on the master of L1.\\ (If the system has more than 1 AC input, connect it to the Master corresponding to the first AC input.) \\ All other units ignore their voltage sense input and receive the voltage sense value from the L1 master. |
- | Always update all units to the latest 400 firmware version ([[updating_firmware:updating_ve.bus_products|firmware update instructions]]).\\ | + | |
- | Please note that some parts of the description below apply only to 4xx firmwares! | + | Note: Special considerations exist before initial power-up for large systems using Redflow batteries: |
In the [[https:// | In the [[https:// | ||
Line 34: | Line 106: | ||
- | * Power Assist | + | * PowerAssist |
Line 42: | Line 114: | ||
- | Please note that AES is only operational | + | Charger settings (voltage and current limits) are overridden if DVCC is configured and if a CANBus BMS is active |
+ | A quick way to make settings in all units is the 'send to all units' feature. You'll see the option after making the changes to the first unit. | ||
+ | Note that AES is only operational in stand-alone systems. Not in parallel and multi-phase systems. | ||
==== Virtual switch ==== | ==== Virtual switch ==== | ||
A unique virtual switch configuration can be configured for each unit in the system. With the exception of the Ignore AC input function: configure that in the master of L1. | A unique virtual switch configuration can be configured for each unit in the system. With the exception of the Ignore AC input function: configure that in the master of L1. | ||
- | * The VE.Bus BMS and the Lynx Ion BMS support Assistant also need to be loaded in each unit in the system. | + | * The VE.Bus BMS and the Two-Signal |
+ | * For the [[https:// | ||
- | Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then load that file into all other units. VEConfigure will automatically adapt the Assistants for the slaves. | ||
- | ===== DISQUS | + | |
- | ~~DISQUS~~ | + | ===== System Monitoring |
+ | It is strongly recommended that a [[venus-os: | ||
+ | Data from [[http:// | ||
+ | ===== Training Video ===== | ||
ve.bus/manual_parallel_and_three_phase_systems.1468327713.txt.gz · Last modified: 2016-07-12 14:48 by pba