ve.bus:manual_parallel_and_three_phase_systems [2019-11-27 12:27] – guy_stewart | ve.bus:manual_parallel_and_three_phase_systems [2023-05-22 07:58] – [Parallel, split- and three phase VE.Bus systems] guy_stewart | ||
This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example MultiPlus, Quattro and some larger Phoenix inverters. | This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example MultiPlus, Quattro and some larger Phoenix inverters. | ||
Line 5: | Line 5: | ||
- | * Note that some parts of the description below apply only to 4xx firmwares. | + | * Note that some parts of the description below apply only firmware version 400 and later. |
* All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | * All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | ||
Line 14: | Line 17: | ||
+ | These should | ||
First get experience with smaller systems. If you are new to Victron, please start with simpler designs, so that you become familiar with the necessary training, equipment and software required. | First get experience with smaller systems. If you are new to Victron, please start with simpler designs, so that you become familiar with the necessary training, equipment and software required. | ||
Line 28: | Line 32: | ||
Line 40: | Line 44: | ||
+ | === Main text === | ||
- | For units in parallel: Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section to every unit in the phase. To make this easy, use a bus-bar or power-post before and after the inverter/ | + | For units in parallel: Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section to every unit in the phase. To make this easy, use a bus-bar or power-post before and after the inverter/ |
- | For units in parallel: use one AC fuse for all units on that phase. Both on the input, and on the output. Multiple fuses which are mechanically connected | + | With regards to AC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. Consider using mechanically connected |
- | For DC, one fuse per phase is best. If a big single fuse is not available, use one fuse per unit. Same type of fuse due to same resistance. | + | With regards to DC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. |
- | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects.\\ | + | === Warning against over-dimensioning the AC wiring === |
- | * Technical background: In a parallel system the AC current should be evenly distributed through all paralleled units. When the resistance in the cabling is very low, a small difference in resistance results in a large relative difference.\\ This results in bad current distribution.\\ An exaggerated example: | + | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects. |
- | * Using 2 units (A and B) parallel and using extremely good cabling one might achieve a total resistance for Unit_A of 0.0001Ω and a total resistance for Unit_B of 0.0002Ω. This results in Unit_A carrying twice as much current as Unit_B although the resistance difference is very small. | + | |
- | * Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | + | |
- | ==== A continuous, unbroken negative link must be maintained between all units ==== | + | |
- | VE.Bus is not isolated | + | Technical background: for a properly working parallel system, the AC current should be evenly distributed between the paralleled units. The resistance in the cabling helps with that and is needed for that; to overcome small differences between one inverter/ |
- | Therefore it is very important to prevent damage to the communications cards that the negative battery terminal | + | An exaggerated example: |
+ | * Using 2 units (A and B) parallel and using too good cabling, one might achieve a total resistance for Unit_A | ||
+ | * Using the same 2 units in parallel with, for the sake of this example underdimensioned AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance | ||
- | If units need to be isolated at both poles, or local wiring requirements demand double pole isolation for each unit, the communications cables must be removed first AND appropriate safety signage needs to clearly explain this. | + | A side effect of over dimensioning the AC cabling can be faulty Power Assist operation. Out of all units, the phase master is in control and measuring the AC input current. And in case that current is (grossly) unevenly distributed between the paralleled units, the resulting total AC input current can end up being too low (under charging the battery). |
- | Double pole isolation of the system is allowed (and sometimes required), as long as it at the battery connection end of the DC bus, and the Multis/ | + | === Delta configurations not supported === |
- | ==== Theory and background information ==== | ||
- | wiring | + | |
+ | === Theory and background information ==== | ||
+ | Wiring | ||
Line 79: | Line 89: | ||
Line 97: | Line 107: | ||
Line 104: | Line 114: | ||
Line 112: | Line 124: | ||
- | * The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system. | + | * The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system |
- | (nb: In some cases (depending on the choices made) slaves can be left out, the assistant | + | * For the [[https:// |
- | Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for another unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | ||
Line 128: | Line 141: | ||
Line 134: | Line 147: | ||
===== Training Video ===== | ===== Training Video ===== | ||
- | There is an advanced training video and competency exam for 3 phase and parallel installation and commissioning available on [[https:// | + | There is an advanced training video and competency exam for 3 phase and parallel installation and commissioning available on [[https:// |