ve.bus:manual_parallel_and_three_phase_systems [2019-10-27 02:23] – [A continuous, unbroken negative link must be maintained between all units] guystewart | ve.bus:manual_parallel_and_three_phase_systems [2020-08-21 05:40] – [Training Video] guy_stewart | ||
Line 17: | Line 17: | ||
This should be considered essential before attempting design or installation. | This should be considered essential before attempting design or installation. | ||
- | First get experience with smaller systems. | + | First get experience with smaller systems. |
It is also recommended to hire an installer that has experience with these more complex Victron systems, for both the design and the commissioning. | It is also recommended to hire an installer that has experience with these more complex Victron systems, for both the design and the commissioning. | ||
Line 44: | Line 44: | ||
- | For units in parallel: Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section to every unit in the phase. To make this easy, use a bus-bar or power-post before and after the inverter/ | + | For units in parallel: Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section to every unit in the phase. To make this easy, use a bus-bar or power-post before and after the inverter/ |
- | For units in parallel: use one AC fuse for all units on that phase. Both on the input, and on the output. Multiple fuses which are mechanically connected | + | With regards to AC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. Consider using mechanically connected |
- | For DC, one fuse per phase is best. If a big single fuse is not available, use one fuse per unit. Same type of fuse due to same resistance. | + | With regards to DC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. |
Line 56: | Line 58: | ||
* Using 2 units (A and B) parallel and using extremely good cabling one might achieve a total resistance for Unit_A of 0.0001Ω and a total resistance for Unit_B of 0.0002Ω. This results in Unit_A carrying twice as much current as Unit_B although the resistance difference is very small. | * Using 2 units (A and B) parallel and using extremely good cabling one might achieve a total resistance for Unit_A of 0.0001Ω and a total resistance for Unit_B of 0.0002Ω. This results in Unit_A carrying twice as much current as Unit_B although the resistance difference is very small. | ||
* Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | * Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | ||
==== A continuous, unbroken negative link must be maintained between all units ==== | ==== A continuous, unbroken negative link must be maintained between all units ==== | ||
Line 69: | Line 74: | ||
==== Theory and background information ==== | ==== Theory and background information ==== | ||
- | wiring | + | Wiring |
Line 97: | Line 102: | ||
Line 104: | Line 109: | ||
Line 112: | Line 119: | ||
* The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system. | * The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system. | ||
Line 120: | Line 130: | ||
Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for another unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for another unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | ||
Line 128: | Line 137: | ||
- | ===== DISQUS | + | ===== Training Video ===== |
- | ~~DISQUS~~ | + | |
