ve.bus:manual_parallel_and_three_phase_systems [2019-09-24 12:54] – guy_stewart | ve.bus:manual_parallel_and_three_phase_systems [2020-05-15 12:43] – [Theory and background information] guy_stewart | ||
Line 17: | Line 17: | ||
This should be considered essential before attempting design or installation. | This should be considered essential before attempting design or installation. | ||
- | First get experience with smaller systems. | + | First get experience with smaller systems. |
It is also recommended to hire an installer that has experience with these more complex Victron systems, for both the design and the commissioning. | It is also recommended to hire an installer that has experience with these more complex Victron systems, for both the design and the commissioning. | ||
Line 39: | Line 39: | ||
Line 45: | Line 44: | ||
- | For units in parallel: | + | For units in parallel: |
- | For DC, one fuse per phase is best. If a big single fuse is not available, use one fuse per unit. Same type of fuse due to same resistance. | + | With regards to AC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. Consider using mechanically connected fuses. |
- | Beware of phase rotation between the inverter and AC in. When wired in the wrong rotation, the system will not accept the mains input and only operates in inverter mode. In that case swap two phases to correct it. | + | With regards to DC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. |
+ | Beware of phase rotation between the inverter and AC in. When wired in a rotation | ||
Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects.\\ | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects.\\ | ||
Line 56: | Line 59: | ||
* Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | * Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | ||
==== A continuous, unbroken negative link must be maintained between all units ==== | ==== A continuous, unbroken negative link must be maintained between all units ==== | ||
Line 64: | Line 69: | ||
If units need to be isolated at both poles, or local wiring requirements demand double pole isolation for each unit, the communications cables must be removed first AND appropriate safety signage needs to clearly explain this. | If units need to be isolated at both poles, or local wiring requirements demand double pole isolation for each unit, the communications cables must be removed first AND appropriate safety signage needs to clearly explain this. | ||
- | Double pole isolation of the system is allowed (and sometimes required), as long as it at the battery connection end of the DC bus, and the Quattros remain with continuous negative between themselves. | + | Double pole isolation of the system is allowed (and sometimes required), as long as it at the battery connection end of the DC bus, and the Multis/Quattros remain with continuous negative between themselves. |
- | Theory and background information | + | ==== Theory and background information |
+ | Wiring | ||
Line 95: | Line 102: | ||
Line 102: | Line 109: | ||
Line 110: | Line 119: | ||
* The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system. | * The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system. | ||
Line 118: | Line 130: | ||
Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for another unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for another unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | ||
Line 126: | Line 137: | ||
- | ===== DISQUS | + | ===== Training Video ===== |
- | ~~DISQUS~~ | + | |