ve.bus:manual_parallel_and_three_phase_systems [2017-10-06 17:28] – [Configuration] pba | ve.bus:manual_parallel_and_three_phase_systems [2023-10-10 11:47] – [Parallel, split- and three phase VE.Bus systems] sloges | ||
- | This manual explains the details of designing, installing and configuring three-phase and parallel systems. | + | This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example, MultiPlus, Quattro and some larger VE.Bus inverters. |
+ | **IMPORTANT: | ||
+ | * Always update all units to the latest firmware version during commissioning of the system: ([[updating_firmware: | ||
+ | * Note that some parts of the description below apply only to firmware version 400 and later. | ||
+ | * All units in one system must be the same type and firmware version; this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | ||
+ | * Specify with your [[https:// | ||
+ | ===== Warning ===== | ||
+ | Parallel and Multiphase systems are complex. | ||
+ | Victron is able to provide specific training for these systems to [[https:// | ||
+ | These should all be considered essential before attempting design or installation. | ||
+ | First get experience with smaller systems. If you are new to Victron, please start with simpler designs, so that you become familiar with the necessary training, equipment and software required. | ||
+ | It is also recommended to hire an installer that has experience with these more complex Victron systems, for both the design and the commissioning. | ||
- | IMPORTANT: | ||
- | Always update all units to the latest 400 firmware version([[updating_firmware: | ||
- | Please note that some parts of the description below apply only to 4xx firmwares! | ||
===== Maximum System size ===== | ===== Maximum System size ===== | ||
Line 13: | Line 32: | ||
Line 21: | Line 40: | ||
* maximum single phase system with 10kVA Quattros is 60kVA: six units. | * maximum single phase system with 10kVA Quattros is 60kVA: six units. | ||
- | __Warning__ | ||
- | Do not underestimate the complexity of making such large systems. We do not support untrained and/or inexperienced installers working on these size systems. | ||
- | Before installing system of 60kVA or larger, first install and get experience with smaller systems. Start with single phase single unit, then for example 30 or 60kVA. | ||
- | Or hire an installer that does have experience with these large systems, for both the design and the commissioning. | ||
- | Both the DC and AC wiring needs to be symmetrical per phase: use the same length, type and cross-section | + | |
+ | === Main text === | ||
+ | The VE.Bus cluster maintains a single ' | ||
- | For units in parallel: | + | For units in parallel: |
- | For DC, one fuse per phase is best. If a big single fuse is not available, use one fuse per unit. Same type of fuse due to same resistance. | + | With regards to AC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. Consider using mechanically connected fuses. |
+ | With regards to DC fusing, each unit needs to be fused individually. Make sure to use the same type of fuse on each unit due to same resistance. | ||
+ | Beware of phase rotation between the inverter and AC in. When wired in a rotation that is different to the programming of the Multis, the system will not accept the mains input and only operates in inverter mode. [[https:// | ||
+ | === Warning against over-dimensioning the AC wiring === | ||
+ | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects. | ||
+ | Technical background: for a properly working parallel system, the AC current should be evenly distributed between the paralleled units. The resistance in the cabling helps with that and is needed for that; to overcome small differences between | ||
+ | An exaggerated example: | ||
+ | * Using 2 units (A and B) parallel and using too good cabling, one might achieve a total resistance for Unit_A | ||
+ | * Using the same 2 units in parallel with, for the sake of this example underdimensioned AC cabling one might end up with a total resistance | ||
+ | A side effect of over dimensioning the AC cabling can be faulty Power Assist operation. Out of all units, the phase master is in control and measuring the AC input current. And in case that current is (grossly) unevenly distributed between the paralleled units, the resulting total AC input current can end up being too low (under charging the battery). | ||
+ | === Delta configurations not supported === | ||
+ | === Theory and background information ==== | ||
+ | Wiring is further explained here: | ||
+ | * [[https:// | ||
- | Beware of phase rotation between the inverter and AC in. When wired in the wrong rotation, the system will not accept the mains input and only operates in inverter mode. In that case swap two phases to correct it. | ||
- | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects.\\ | ||
- | * Technical background: In a parallel system the AC current should be evenly distributed through all paralleled units. When the resistance in the cabling is very low, a small difference in resistance results in a large relative difference.\\ This results in bad current distribution.\\ An exaggerated example: | ||
- | * Using 2 units (A and B) parallel and using extremely good cabling one might achieve a total resistance for Unit_A of 0.0001Ω and a total resistance for Unit_B of 0.0002Ω. This results in Unit_A carrying twice as much current as Unit_B although the resistance difference is very small. | ||
- | * Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | ||
+ | Note: Special considerations exist before initial power-up for large systems using Redflow batteries: [[https:// | ||
In the [[https:// | In the [[https:// | ||
* Up to three units: use VE.Bus Quick Configure | * Up to three units: use VE.Bus Quick Configure | ||
Line 63: | Line 107: | ||
- | * Power Assist | + | * PowerAssist |
Note that AES is only operational in stand-alone systems. Not in parallel and multi-phase systems. | Note that AES is only operational in stand-alone systems. Not in parallel and multi-phase systems. | ||
==== Virtual switch ==== | ==== Virtual switch ==== | ||
A unique virtual switch configuration can be configured for each unit in the system. With the exception of the Ignore AC input function: configure that in the master of L1. | A unique virtual switch configuration can be configured for each unit in the system. With the exception of the Ignore AC input function: configure that in the master of L1. | ||
- | * The VE.Bus BMS and the Lynx Ion BMS support Assistant also need to be loaded in each unit in the system. | + | * The VE.Bus BMS and the Two-Signal |
- | (nb: In some cases (depending on the choices made) slaves can left out, the assistant | + | * For the [[https:// |
- | Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for an other unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | ||
- | ===== DISQUS | + | |
- | ~~DISQUS~~ | + | ===== System Monitoring |
+ | It is strongly recommended that a [[venus-os: | ||
+ | Data from [[http:// | ||
+ | ===== Training Video ===== | ||