ve.bus:manual_parallel_and_three_phase_systems [2022-11-23 16:37] – [Parallel, split- and three phase VE.Bus systems] mvader | ve.bus:manual_parallel_and_three_phase_systems [2024-02-09 13:07] (current) – Removed “Weak LOM” setting. since that is currently the default jpasop | ||
- | ====== Parallel, split- and three phase VE.Bus systems ====== | + | ====== Parallel, split- and three-phase VE.Bus systems ====== |
- | This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example MultiPlus, Quattro and some larger | + | This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example, MultiPlus, Quattro and some larger |
- | * Note that some parts of the description below apply only to 4xx firmwares. | + | * Note that some parts of the description below apply only to firmware version 400 and later. |
- | * All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | + | * All units in one system must be the same type and firmware version; this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " |
* The same number of units need to be installed on each phase. An example to clarify: 3 units on L1, 3 on L2, and 3 on L3 is OK. But 2 on L1, 3 on L2 and 3 on L3 is not OK. The only way such non-symmetrical installation is supported is when using no monitoring at all, or a Digital Multi Control. Combining such system with any other monitoring device, such as the VE.Bus Smart Dongle or a GX device like the Cerbo is not supported. Numbers and information shown on the GX device as well as VRM portal will or can be wrong, and controlling the system, for example setting input current limits will not always work properly either. | * The same number of units need to be installed on each phase. An example to clarify: 3 units on L1, 3 on L2, and 3 on L3 is OK. But 2 on L1, 3 on L2 and 3 on L3 is not OK. The only way such non-symmetrical installation is supported is when using no monitoring at all, or a Digital Multi Control. Combining such system with any other monitoring device, such as the VE.Bus Smart Dongle or a GX device like the Cerbo is not supported. Numbers and information shown on the GX device as well as VRM portal will or can be wrong, and controlling the system, for example setting input current limits will not always work properly either. | ||
* While VE.Bus System Configurator allows setting up a system using Multis (each having a single AC input), that is configured to have multiple separate AC inputs, such system is not supported by GX devices. | * While VE.Bus System Configurator allows setting up a system using Multis (each having a single AC input), that is configured to have multiple separate AC inputs, such system is not supported by GX devices. | ||
Line 103: | Line 104: | ||
* All charger settings, such as absorption voltage, float voltage and max charge current.\\ (The maximum charge current is multiplied by the number of units in the system: in a 9 unit system set it to 50A to get a 450A maximum charge current.) | * All charger settings, such as absorption voltage, float voltage and max charge current.\\ (The maximum charge current is multiplied by the number of units in the system: in a 9 unit system set it to 50A to get a 450A maximum charge current.) | ||
* System frequency | * System frequency | ||
- | * Whether or not "Weak LOM" is used | ||
* Inverter output voltage | * Inverter output voltage |