ve.bus:manual_parallel_and_three_phase_systems [2020-08-21 05:40] – [Training Video] guy_stewart | ve.bus:manual_parallel_and_three_phase_systems [2022-11-24 14:48] – [Parallel, split- and three phase VE.Bus systems] mvader | ||
This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example MultiPlus, Quattro and some larger Phoenix inverters. | This manual explains the details of designing, installing and configuring three-phase and parallel systems. It applies to components that use VE.Bus, for example MultiPlus, Quattro and some larger Phoenix inverters. | ||
Line 5: | Line 5: | ||
- | * Note that some parts of the description below apply only to 4xx firmwares. | + | * Note that some parts of the description below apply only firmware version 400 and later. |
* All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | * All units in one system must be the same type and firmware version, this includes same size, system voltage, and feature set. The type is indicated by the first four digits of the firmware version number. For details, see the " | ||
Line 14: | Line 16: | ||
+ | These should | ||
First get experience with smaller systems. If you are new to Victron, please start with simpler designs, so that you become familiar with the necessary training, equipment and software required. | First get experience with smaller systems. If you are new to Victron, please start with simpler designs, so that you become familiar with the necessary training, equipment and software required. | ||
Line 28: | Line 31: | ||
Line 40: | Line 43: | ||
+ | === Main text === | ||
Line 54: | Line 58: | ||
- | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects.\\ | + | === Warning against over-dimensioning the AC wiring === |
- | * Technical background: In a parallel system the AC current should be evenly distributed through all paralleled units. When the resistance in the cabling is very low, a small difference in resistance results in a large relative difference.\\ This results in bad current distribution.\\ An exaggerated example: | + | Note: Do not over-dimension the AC cabling. Using extra thick cabling has negative side effects. |
- | * Using 2 units (A and B) parallel and using extremely good cabling one might achieve a total resistance for Unit_A of 0.0001Ω and a total resistance for Unit_B of 0.0002Ω. This results in Unit_A carrying twice as much current as Unit_B although the resistance difference is very small. | + | |
- | * Using the same 2 units in parallel with bad AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | + | |
- | For units in 3 phase configuration: Our products have been designed | + | Technical background: for a properly working parallel system, the AC current should be evenly |
- | We do not support a delta (Δ) configuration. A delta configuration does not have a distributed neutral | + | |
- | ==== A continuous, unbroken negative link must be maintained between all units ==== | + | |
- | VE.Bus is not isolated on the MultiPlus range and Quattros. | + | An exaggerated example: |
+ | * Using the same 2 units in parallel with, for the sake of this example underdimensioned AC cabling one might end up with a total resistance for Unit_A of 15Ω and a total resistance for Unit_B of 16Ω. This results in a much better current distribution (Unit_A will carry 1.066 times more current than Unit_A) even if the absolute difference in resistance is much bigger than in the previous example (1Ω vs 0.0001Ω). | ||
- | Therefore it is very important to prevent damage to the communications cards that the negative battery terminal | + | A side effect of over dimensioning |
- | If units need to be isolated at both poles, or local wiring requirements demand double pole isolation | + | === Delta configurations not supported === |
- | Double pole isolation of the system is allowed (and sometimes required), as long as it at the battery connection end of the DC bus, and the Multis/ | ||
- | ==== Theory and background information ==== | + | === Theory and background information ==== |
Wiring is further explained here: | Wiring is further explained here: | ||
Line 84: | Line 88: | ||
Line 102: | Line 106: | ||
- | * Input current limits\\ (the effective input current limit is the setted | + | * Input current limits\\ (the effective input current limit is the limit set on the master |
Line 124: | Line 128: | ||
* If you are using a self-consumption assistant, such as ESS, Hub-1 to Hub-4, the assistant will need to be loaded into each unit in the system individually.\\ | * If you are using a self-consumption assistant, such as ESS, Hub-1 to Hub-4, the assistant will need to be loaded into each unit in the system individually.\\ | ||
- | * The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system. | + | * The VE.Bus BMS and the Two-Signal BMS support Assistant also need to be loaded in each unit in the system |
- | (nb: In some cases (depending on the choices made) slaves can be left out, the assistant | + | * For the [[https:// |
- | Tip: a quick way to load Assistants into each unit in the system is to save the settings after configuring the master in L1. Then open VEConfigure for another unit and load that file. VEConfigure will automatically adapt the Assistants for the slaves. (note: In some cases you might get some warnings. Please step through the assistant in that case.) | ||