multiplus_faq
multiplus_faq [2017-10-01 01:49] – [2.2 AC Input Current Limit] guystewart | multiplus_faq [2023-02-16 01:50] (current) – guy_stewart | ||
Line 2: | Line 2: | ||
- | ---- | + | __ |
- | Some generators are more suitable than others for use with inverter/ | + | |
+ | Some generators are more suitable than others for use with inverter/ | ||
Line 17: | Line 18: | ||
- | **Generator Sizing** | ||
- | 5 kVa - 3000VA Multi | + | If you do want an inverter based generator (eg for noise reasons under lower loading), get one that is at least 30% larger than required than an equivalent AVR based model to help prevent nuisance overloads. |
- | 8 kVa - 5000VA Multi | + | It is also important to look at the DUTY CYCLE rating of the generator. Some generators are marketed for their peak output, but may only be designed to sustain 50% of that peak load rating for longer periods of time. |
+ | ==== Operation ==== | ||
- | **Operation** | ||
Line 41: | Line 52: | ||
- | **Software | + | ==== Software |
Line 54: | Line 66: | ||
Line 77: | Line 89: | ||
Line 88: | Line 109: | ||
+ | ===== 1.5 Loss of mains detection (LOM) (Only applicable to ESS systems) ===== | ||
- | ====== 2. In the “General” tab of VE-Configure: ====== | + | This part is only applicable on systems where a grid-code is selected (generally only ESS systems) on an off-grid system a grid code should not be used and in the selection box for grid code, ' |
+ | **Disabling LOM** | ||
+ | **Example configuration in VEConfigure** | ||
+ | ====== 2. In the “General” tab of VEConfigure: ====== | ||
Line 104: | Line 150: | ||
a 5kVA generator typically provides about 4 kW | a 5kVA generator typically provides about 4 kW | ||
80% of 4 kW is 3200 W | 80% of 4 kW is 3200 W | ||
3200 W / 230 V volts = 13.9 A | 3200 W / 230 V volts = 13.9 A | ||
Set the AC Current Input Limit to 13 A | Set the AC Current Input Limit to 13 A | ||
Line 121: | Line 171: | ||
+ | Effectively, | ||
+ | The [[https:// | ||
+ | https:// | ||
- | ===== Disqus ===== | ||
