- | **Generator Sizing** | ||
- | 5 kVa - 3000VA Multi | + | ==== Operation ==== |
- | 8 kVa - 5000VA Multi | ||
- | **Operation** | ||
Line 41: | Line 45: | ||
Line 77: | Line 82: | ||
Line 85: | Line 99: | ||
+ | ===== Example configuration in VEConfigure ===== | ||
Line 93: | Line 121: | ||
- | ===== 2.1 Load impact limitation ===== | ||
- | **Dynamic current limiter** : (default = disabled) | + | ===== 2.1 Dynamic current limiter |
+ | (default = disabled) | ||
This feature is intended to reduce load impacts on low-power generators, such as portable inverter technology models. These generators may be unable to respond to sudden load impacts. | This feature is intended to reduce load impacts on low-power generators, such as portable inverter technology models. These generators may be unable to respond to sudden load impacts. | ||
By activating the limiter, the **PowerAssist®** function of the MultiPlus will absorb the change in load and transfer it smoothly to the generator, giving it time to react. | By activating the limiter, the **PowerAssist®** function of the MultiPlus will absorb the change in load and transfer it smoothly to the generator, giving it time to react. | ||
+ | ===== 2.2 AC Input Current Limit ===== | ||
+ | The charger on the Multiplus is very powerful. If you have an existing generator that is not able to supply the maximum charging current of the Multi, you will need to adjust the AC Input Current Limit in the General Tab of VE-Configure. | ||
+ | A reasonable starting point for the AC Current input limit is 80% of the generator capacity in Watts. For example: | ||
+ | a 5kVA generator typically provides about 4 kW | ||
+ | 80% of 4 kW is 3200 W | ||
+ | 3200 W / 230 V volts = 13.9 A | ||
+ | Set the AC Current Input Limit to 13 A | ||
+ | If you find the generator is still overloading, | ||
+ | There is another additional setting in the Charger Tab for DC current limiting. | ||
+ | The AC input current should be adjusted first, as it also takes into account the PowerAssist functionality. | ||
+ | The Multi is able to synchronise the generator waveform with it's own and provide power to the loads from the generator as well charging the battery. This means it still possible to overload the generator with a low 'DC Charger current limit' if the AC input limit is not also set correctly to the size of the generators output. | ||