ess:ess_mode_2_and_3
ess:ess_mode_2_and_3 [2020-02-17 09:55] – [1.3 - Mode 3] iburger | ess:ess_mode_2_and_3 [2020-07-08 15:48] – [2.1 Available control points] iburger | ||
Line 5: | Line 5: | ||
The here described functionality builds on top of the normal standalone operation, see [[ess: | The here described functionality builds on top of the normal standalone operation, see [[ess: | ||
+ | WARNING & DISCLAIMER: whilst publically available, Victron Energy does not offer support in professional customers or end-users that implement features using the here documented functionality, | ||
===== 1. Overview of ESS operating modes ===== | ===== 1. Overview of ESS operating modes ===== | ||
Line 33: | Line 34: | ||
=== Mode 3 with a managed battery === | === Mode 3 with a managed battery === | ||
When using Mode 3 with a managed battery, please note that the maximum discharge current sent by the battery will be ignored. The implemented control loop should take care of discharge limits communicated by the battery. | When using Mode 3 with a managed battery, please note that the maximum discharge current sent by the battery will be ignored. The implemented control loop should take care of discharge limits communicated by the battery. | ||
- | The exception to the above rule is a zero discharge limit. If a managed battery requests a zero discharge limit, the Multi will stop discharging the battery. | ||
- | * If grid power is available, the Multi will go into passthru. | ||
- | * If grid power is not available, the Multi will switch off. | ||
The maximum charge current sent by a managed battery is however always heeded and cannot be overruled by the setpoint. | The maximum charge current sent by a managed battery is however always heeded and cannot be overruled by the setpoint. | ||
Line 64: | Line 61: | ||
Note that this settings has a higher priority than the //Grid power setpoint//. | Note that this settings has a higher priority than the //Grid power setpoint//. | ||
+ | === d) Maximum inverter power - Modbus-TCP register 2704 === | ||
+ | * -1: No limit | ||
+ | * Any positive number: Maximum power in Watt that the Multi will feed to the loads. | ||
+ | === e) DVCC maximum system charge current - Modbus-TCP register 2705 === | ||
+ | * -1: No limit. Solar Chargers and the Multi will charge to their full capacity or individual configurd limits. | ||
+ | * Any positive number: Maximum combined current in Ampere for battery charging. This limits the solar chargers and the multi, and takes loads into account. Solar chargers take priority over the Multi. | ||
+ | === f) Maximum system grid feed-in - Modbus-TCP register 2706 === | ||
+ | * -1: No limit. If feeding in excess PV is enabled, all of it will be fed in. See registers 2707 and 2708 below. | ||
+ | * Any positive number: Maximum power in 100 Watt units to feed into the grid. | ||
+ | === g) Feed excess DC-coupled PV into the grid - Modbus-TCP register 2707 === | ||
+ | * 0: Excess DC-coupled PV is not fed into the grid. | ||
+ | * 1: Excess DC-coupled PV is fed into the grid | ||
+ | === h) Feed excess AC-coupled PV into the grid - Modbus-TCP register 2708 === | ||
+ | Please note that for historical reasons this register is inverted compared to 2707. | ||
+ | * 0: Excess AC-coupled PV is fed into the grid | ||
+ | * 1: Excess AC-coupled PV is not fed into the grid. | ||
+ | === i) Grid limiting status - Modbus-TCP register 2709 === | ||
+ | When feed-in of excess AC-coupled PV is disabled, or when a limit is set in register 2706, limiting will be active. | ||
+ | * 0: Feed-in of excess power is not limited in any way. | ||
+ | * 1: Feed-in of excess power is limited in some way, either register 2707 is set to 0, or register 2706 is set to a positive number. | ||
==== 2.2 Accessing the control points ==== | ==== 2.2 Accessing the control points ==== | ||
Line 72: | Line 94: | ||
- | MQTT is available both on the local broker on the [[venus-os: | + | MQTT is available both on the local broker on the [[venus-os: |
=== C) Running your own scripts on the CCGX === | === C) Running your own scripts on the CCGX === |