ess:ess_mode_2_and_3
ess:ess_mode_2_and_3 [2020-02-10 16:00] – [5. Response times and ramp speed] mvader | ess:ess_mode_2_and_3 [2020-02-17 09:55] – [1.3 - Mode 3] iburger | ||
Line 29: | Line 29: | ||
* Note that there is no AC sensor necessary, since the inverter/ | * Note that there is no AC sensor necessary, since the inverter/ | ||
- | Available control points include the switch (on, charger-only, | + | Available control points include the switch (on, charger-only, |
+ | === Mode 3 with a managed battery === | ||
+ | When using Mode 3 with a managed battery, please note that the maximum discharge current sent by the battery will be ignored. The implemented control loop should take care of discharge limits communicated by the battery. | ||
+ | The exception to the above rule is a zero discharge limit. If a managed battery requests a zero discharge limit, the Multi will stop discharging the battery. | ||
+ | * If grid power is available, the Multi will go into passthru. | ||
+ | * If grid power is not available, the Multi will switch off. | ||
+ | The maximum charge current sent by a managed battery is however always heeded and cannot be overruled by the setpoint. | ||
- | Similar to Mode 2, there are various ways to access those control points. | ||
===== 2. Mode 2 in detail ===== | ===== 2. Mode 2 in detail ===== |