ess:design-installation-manual [2019-03-08 14:50] – mvader | ess:design-installation-manual [2019-04-03 13:27] – guy_stewart | ||
Line 410: | Line 410: | ||
This sets the point at which power is taken from the grid when the installation is in self-consumption mode. Setting this value slightly above 0W prevents the system from feeding back power to the grid when there is a bit of over-shoot in the regulation. The default value is therefore 50W - but should be set to a higher value on large systems. | This sets the point at which power is taken from the grid when the installation is in self-consumption mode. Setting this value slightly above 0W prevents the system from feeding back power to the grid when there is a bit of over-shoot in the regulation. The default value is therefore 50W - but should be set to a higher value on large systems. | ||
==== 4.4 Venus-device - Scheduled Charging ==== | ==== 4.4 Venus-device - Scheduled Charging ==== | ||
Line 604: | Line 605: | ||
(This 0.1 V is the threshold for 12 V systems; for 24 V the threshold is 0.2 V above; and for 48 V it is 0.4V above.) | (This 0.1 V is the threshold for 12 V systems; for 24 V the threshold is 0.2 V above; and for 48 V it is 0.4V above.) | ||
+ | ==== 6.5 ESS Battery Status Code Numbers ==== | ||
+ | In addition to the charger states (Bulk/ | ||
+ | The key for these codes is: | ||
+ | * #1: SOC is low | ||
+ | * #2: BatteryLife is active | ||
+ | * #3: BMS disabled charging | ||
+ | * #4: BMS disabled discharge | ||
+ | * #5: Slow Charge in progress (part of BatteryLife, | ||
+ | * #6: User configured a charge limit of zero. | ||
+ | * #7: User configured a discharge limit of zero. | ||
===== 7. Phase compensation - further information ===== | ===== 7. Phase compensation - further information ===== | ||
Line 879: | Line 898: | ||