energy-meters:et340
energy-meters:et340 [2021-03-20 03:07] – guystewart | energy-meters:et340 [2022-07-15 10:58] (current) – Removed and linked to new manuals stefanie | ||
- | ====== Energy Meter ET340 manual ====== | + | The old Energy Meter manuals |
- | This document is the manual for the 3 phase max 65A per phase Energy Meter. | + | |
- | The Energy Meter can be used to: | + | |
- | - Grid meter, and used as control input for an [[assistants: | + | |
- | The meter is connected to the GX device. There are two options in its wiring: | + | |
- | ===== 2. AC Wiring ===== | + | |
- | === 3-phase diagram: === | + | |
- | When used to measure a PV Inverter, terminals 1, 2 and 3 should face the PV inverter to ensure correct direction of current and power. | + | |
- | === Single phase dual function diagram: === | + | |
- | In this diagram, a single meter is used to both measure the grid and a single phase PV Inverter. | + | |
- | On the GX device go to the grid meter in the Wired AC sensor settings. Make sure 'Phase type' is set to ' | + | |
- | ===== 3. Connection to GX device === | + | |
- | === Step 1. === | + | |
- | Connect the Zigbee to USB converter to the GX device using the supplied USB cable. A few seconds after connecting, the active LED should be on and the TX/RX LED should be blinking (the converter takes its power from the GX device, so the GX device needs to be switched on as well). | + | |
- | === Step 2. === | + | |
- | Connect the Zigbee to RS485 converter to the ET340 energy meter: | + | |
- | | GND | Terminal 10 | | + | |
- | | A | Terminal | + | |
- | | B | Terminal | + | |
- | === Step 3. === | + | |
- | Make sure only one Zigbee device is powered up right now: the Zigbee to USB converter connected to the GX device. Power down all others. //If you don't do this, the Zigbee to RS485 converter may be connected permanently to another Zigbee device.// | + | |
- | === Step 4. === | + | |
- | === note on old and new zigbee converters === | + | |
- | Please note that there is a new zigbee converter available now, that is -not- backwards compatible with the old converters. If you have a non compatible set, please ask your supplier for a correct version. | + | |
- | ASS300400100 - Zigbee to RS485 converter partnumber: DRF2619C | + | |
- | ASS300400100 - Zigbee to USB converter | + | |
- | ASS300420100 - Zigbee to RS485 converter partnumber: DRF2659C | + | |
- | ASS300420200 - Zigbee to USB converter | + | |
- | == note on GX firmware versions: == | + | |
- | for the new type Zigbee converters, Venus OS v2.54 is the minimum required software version | + | |
- | ==== Option B: Wired connection to GX device ==== | + | |
- | Connect the Energy Meter to the GX device using the USB to RS485 cable. The RS485 to USB interface cable between the GX device and the Energy Meter can be extended up to 100 meters; make sure that the extensions of the Data+ (orange) and Data- (yellow) wires form a twisted pair. | + | |
- | | Orange (Data+) | + | |
- | | Yellow (Data-) | + | |
- | | Black (GND) | Terminal 10 | | + | |
- | The red, green and brown wire coming out of the USB to RS485 cable are not used. | + | |
- | == Note on cable length extensions and bus termination == | + | |
- | To ensure signal integrity and robust operation, particularly ensure that; | + | |
- | Extension cabling complies with the minimum cross-sectional area specifications in the USB to RS485 data sheet. | + | |
- | Extension cabling has appropriate shielding and twisted pair cores | + | |
- | The original cable attached to the Victron RS485 to USB interface is reduced to a maximum length of 20cm in installations where the total cable length is over 10m or there are installation/ | + | |
- | Cabling is installed separated/ | + | |
- | All wiring is properly terminated (including unused wires) and properly isolated from weather/ | + | |
- | RS485 networks are traditionally terminated at both ends with 120Ω terminators. This is not required if the cable length is short and you are using the Victron supplied RS485 to USB lengths, but may be required if they are extended for longer cable runs. The ET340 meter has a built in termination resistor that can be enabled by bridging terminals 7 and 9. | + | |
- | For detailed wiring/ | + | |
- | After proper connection and powering up, the meter will be visible on the GX device in the Settings -> Energy Meters menu: | + | |
- | {{ :energy-meters: | + | |
- | ===== 4. Multiple Energy Meters in one system ===== | + | |
- | To connect multiple Energy Meters, wire each meter to a separate RS485-USB converter. Which are then each plugged into a separate USB socket on the GX device. | + | |
- | Connecting multiple ET340 meters to the same RS485-USB cable is not possible: the ET340 meter has no display and its Modbus address can therefor not be changed. | + | |
