Victron & Pylontech US2000B and Phantom-S
Compatible Victron products
All 48V Multis and Quattros. And always a Color Control GX is necessary in the system, since that has the canbus port which is used for the (required!) communication between the Pylontech battery and the Victron system.
Notes
- PylonTech batteries can only be used in a Victron ESS installation: an installation that uses the ESS Assistant.
- Derating, based on the dynamic Pylontech charge- and discharge limits:
- Minimum CCGX version is v2.00
- The derating mechanism is not precise. In other words, do not expect a discharge limit of 30A to result in a precise discharge of 30A.
- Actual charge- and discharge limits are visible in the Parameters page. See screenshot below.
Wiring of communication cables
A special RJ-45 cable is necessary to connect the Pylontech to the CCGX. Pinout:
Function | CCGX / VE.Can RJ-45 | Pylontech RJ-45 |
GND | Pin 3 | Pin 2 |
CAN-L | Pin 8 | Pin 5 |
CAN-H | Pin 7 | Pin 4 |
Plug the CCGX side of that cable into one of the VE.Can sockets on the back of the CCGX.
Plug the other end into the CAN port of the battery.
Then, plug a VE.Can terminator in the other VE.Can socket on the CCGX. Two VE.Can terminators are included with the package of the CCGX as an accessory, only one is used. Keep the other one as a spare.
Without properly connecting this cable, the battery will stop charging/discharging after 10 minutes. Also, the battery will not show up on the display of the CCGX.
Multiple batteries
Chain the batteries using the RJ-45 cable supplied by Pylontech using the link ports on the battery:
The system auto configures itself: no software changes necessary.
The battery with the empty link port 0 is the master battery. Connect the master battery to the CCGX.
VEConfigure settings
Parameter | Setting |
Battery type | Lithium |
Charge curve | Fixed |
Absorption voltage | 53.2 V |
Float voltage | 53.0 V |
Absorption time | 1 Hr |
Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 53.0 V.
ESS Assistant
Dynamic cut-off values: 47.3V at 0A, 47.2V at 12A, 47.1V at 35A and 47.0V at 100A.
Restart offset: do not change
- Enable the CAN-bus BMS Service in the CCGX. Menu path: Settings → Services → CAN-bus BMS. Note that this changes the function of a VE.Can port: it is not possible to connect both VE.Can products and an Pylontech battery together.
- After properly wiring and setting up, the Pylontech will be visible as a battery in the device list (if you have multiple batteries a single entry will show up, which represents all batteries).
FAQ
The maximum charge and discharge current is limited to 25A, but the data sheet tells me the maximum is 100A.
The maximum current is limited to keep the battery healthy and reach the 10 year guarantee.
After charging the battery the charge current often changes between 0A and 25A.
This is caused by cell balancing inside the battery. This happens with new batteries and after a deep discharge.
