battery_compatibility:bmz_ess
battery_compatibility:bmz_ess [2016-10-25 10:45] – mvader | battery_compatibility:bmz_ess [2022-07-18 12:05] (current) – typo dfaber | ||
+ | The combination of Victron products with the BMZ ESS battery has been tested and certified by the R&D departments. The combination is actively supported by both companies. | ||
+ | * ESS 7.0 | ||
+ | * ESS 9.0 | ||
+ | * ESS X | ||
+ | * ESS Z | ||
- | All 48V Multis and Quattros. And always a Color Control | + | All 48V Multis and Quattros. And always a [[venus-os: |
- | * Victron & BMZ integration currently works only in combination with the Hub-4 Assistant. A very flexible configuration for Energy Storage systems. For more information about Hub-4, see its [[system_integration:hub4_grid_parallel|manual]]. | + | * BMZ batteries can only be used in a [[https:// |
+ | * BMZ batteries and MPPT Solar Chargers with a VE.Can communication port cannot be both connected to the CCGX, because of different canbus speeds. Use a Cerbo GX, or Solar Chargers with a VE.Direct comm. port instead. | ||
- | ==== 2. Wiring of communication cables | + | ==== 2. GX device needed |
- | To use the BMZ ESS in Victron system, it is necessary to use a Color Control GX. The Color Control GX takes care of sending | + | To use the BMZ ESS in Victron system, it is necessary to use a Color Control |
- | A special RJ-45 cable is necessary to connect the battery to the Color Control GX. Pinout: | ||
- | ^ Function ^ VE.Can | + | ==== 3. Wiring of communication cables ==== |
- | | GND | Pin 3 | Pin 2 | | + | Use the //VE.Can |
- | | CAN-L | + | |
- | | CAN-H | + | |
- | Place a VE.Can terminator in the empty socket on the CCGX | + | Then, plug a [[https:// |
- | ==== 3. VEConfigure settings ==== | + | More information about the cable can be found in [[battery_compatibility: |
- | === 3.1 Charge tab === | + | |
+ | Without properly connecting this cable, the battery will stop charging/ | ||
+ | ==== 4. VEConfigure settings ==== | ||
+ | - Check " | ||
+ | - Enter the battery capacity: | ||
+ | - BMZ ESS 7.0 - 121.5 Ah | ||
+ | - BMZ ESS 9.0 - 156.6 Ah | ||
+ | - BMZ ESS X - 186.3 Ah | ||
+ | - BMZ ESS Z - 162 Ah | ||
+ | - The other parameters (" | ||
+ | === 4.2 Charger | ||
| Battery type | Lithium | | | Battery type | Lithium | | ||
- | Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 56.7 V. | + | Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 60.00 V. |
- | === 3.2 Hub-4 Assistant === | + | === 4.3 ESS Assistant === |
Select the fourth battery type: | Select the fourth battery type: | ||
Then: | Then: | ||
- | - Enter the battery capacity: | ||
- | - BMZ ESS 3.0 - 121.5 Ah | ||
- | - BMZ ESS 7.0 - 121.5 Ah | ||
- Do not change the dynamic cut-off values, they have already been set correctly after selecting the lithium battery type. | - Do not change the dynamic cut-off values, they have already been set correctly after selecting the lithium battery type. | ||
+ | - Sustain voltage: 50V | ||
- Same for the restart offset: do not change that. | - Same for the restart offset: do not change that. | ||
- | - When required, configure the system to Stop discharging on low SOC. Minimum advised value is (FIXME to be defined by BMZ) | ||
- | ==== 4. Color Control GX Configuration ==== | ||
- | * Enable the CAN-bus BMS Service in the CCGX. Menu path: //Settings -> Services -> CAN-bus BMS//. Note that this changes the function of a VE.Can port: it is not possible to connect both VE.Can products and a BMZ battery together. | + | ==== 5. GX device Configuration ==== |
- | * After properly wiring and setting up, the BMZ ESS will be visible as a battery | + | * Select |
+ | * After properly wiring and setting up, the BMZ ESS will be visible as a battery in the device list:{{ : | ||
- | * Make sure to enable the // | + | ==== 6. DVCC Settings ==== |
battery_compatibility/bmz_ess.1477385149.txt.gz · Last modified: 2016-10-25 10:45 by mvader