battery_compatibility:axistorage
battery_compatibility:axistorage [2017-05-12 11:25] – [3. VEConfigure settings] edevriesbattery_compatibility:axistorage [2019-08-15 12:18] (current) – replace venus-device with GX device guy_stewart
Line 7: Line 7:
 ==== 1. Introduction ==== ==== 1. Introduction ====
 === 1.1 Compatible Victron products === === 1.1 Compatible Victron products ===
-All 48V Multis and Quattros. And always a Color Control GX is necessary in the system, since that has the canbus port which is used for the (required!) communication between the ESS battery and the Victron system.+All 48V Multis and Quattros. A [[venus-os:start|GX device]] is necessary in the system, since that has the canbus port which is used for the (required!) communication between the ESS battery and the Victron system.
 === 1.2 Notes === === 1.2 Notes ===
Line 15: Line 15:
     * Minimum CCGX version is v1.72         * Minimum CCGX version is v1.72
     * The derating mechanism is not very precise yet. In other words, do not expect a discharge limit of 30A to result in a precise discharge of 30A.     * The derating mechanism is not very precise yet. In other words, do not expect a discharge limit of 30A to result in a precise discharge of 30A.
-    * Actual charge- and discharge limits are visible in the Parameters page. See screenshot below in Chapter 4.+    * Actual charge- and discharge limits are visible in the Parameters page. See screenshot below in Chapter 5.
 +  * AXIstorage batteries and MPPT Solar Chargers with a VE.Can communication port cannot be both connected to the CCGX, because of different canbus speeds. Use Solar Chargers with a VE.Direct comm. port instead.
 === 1.3 System diagram === === 1.3 System diagram ===
 {{ :battery_compatibility:ess-1phase-axistorage.png?nolink |}} {{ :battery_compatibility:ess-1phase-axistorage.png?nolink |}}
-==== 2. Wiring of communication cables ==== +==== 2. GX device needed ====
-To use the AXIstorage ESS in Victron system, it is necessary to use a Color Control GX. The Color Control GX takes care of sending the necessary canbus keep-a-live message to the ESS battery. Without it, the battery will open its internal emergency relay after 10 minutes.+To use the AXIstorage ESS in Victron system, it is necessary to use a ColorControlGX or a VenusGX. The controller takes care of sending the necessary canbus keep-a-live message to the ESS battery. Without it, the battery will open its internal emergency relay after 10 minutes.
-A special RJ-45 cable is necessary to connect the battery to the Color Control GXPinout:+==== 3. Wiring of communication cables ====
 +Use the //VE.Can to CAN-bus BMS type B Cable//, part number ASS030720018. Plug the side which is labeled Battery BMS into the AXIstorage BMS. Plug the side labeled Victron VE.Can into the [[venus-os:start|GX device]].
-^ Function ^ VE.Can RJ-45 ^ AXIstorage RJ-45 ^ +Then, plug a [[https://www.victronenergy.com/accessories/ve-can-rj45-terminator|VE.Can terminator]] in the other VE.Can socket on the [[venus-os:start|GX device]]. Two VE.Can terminators are included with the package of the CCGX as an accessory, only one is used. Keep the other one as a spare.
-| GND      | Pin 3        | Pin 2            | +
-| CAN-L    Pin 8        | Pin 5            | +
-| CAN-H    | Pin 7        | Pin 4            |+
-Place a VE.Can terminator in the empty socket on the CCGX+More information about the cable can be found in [[battery_compatibility:can-bus_bms-cable|its manual]].
-==== 3VEConfigure settings ====+Without properly connecting this cable, the battery will stop charging/discharging after several minutes. Also, the battery will not show up on the display of the of the [[venus-os:start|GX device]].
-=== 3.1 General tab === +
-  - Enabled battery monitor+==== 4. VEConfigure settings ====
 +=== 4.1 General tab ===
 +  - Check "Enable battery monitor"
   - Set the battery capacity to 121.5 Ah   - Set the battery capacity to 121.5 Ah
 +  - The other parameters ("State of charge when bulk finished" and "Charge efficiency") can be left to their default setting. They are not used in this setup.
-=== 3.2 Charger tab ===+=== 4.2 Charger tab ===
 ^ Parameter              ^ Setting ^ ^ Parameter              ^ Setting ^
 | Battery type           | Lithium | | Battery type           | Lithium |
Line 48: Line 51:
 Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 60.00 V. Note: make sure to double check the float voltage after completing Assistants, and if necessary set it back to 60.00 V.
-=== 3.3 ESS Assistant ===+=== 4.3 ESS Assistant ===
 Select the fourth battery type: Select the fourth battery type:
Line 59: Line 62:
-==== 4Color Control GX Configuration ====+==== 5. GX device Configuration ====
-  * Enable the CAN-bus BMS Service in the CCGX. Menu path: //Settings -> Services -> CAN-bus BMS//. Note that this changes the function of a VE.Can port: it is not possible to connect both VE.Can products and a AXIstorage battery together.+  * Select the //CAN-bus BMS (500 kbits/s)// CAN-profile in the [[venus-os:start|GX device]]. Menu path: //Settings -> Services -> CAN-profile//. Note that this changes the function of a VE.Can port: it is not possible to connect both VE.Can products and a AXIstorage battery together.
   * After properly wiring and setting up, the AXIstorage will be visible as a battery in the device list:{{ :battery_compatibility:generic_battery_menu.png?nolink&290 | }}   * After properly wiring and setting up, the AXIstorage will be visible as a battery in the device list:{{ :battery_compatibility:generic_battery_menu.png?nolink&290 | }}
   * The parameters option within the battery page shows the actual battery charge and discharge limits:{{ :battery_compatibility:batteryparameters.png?nolink&290 | }}   * The parameters option within the battery page shows the actual battery charge and discharge limits:{{ :battery_compatibility:batteryparameters.png?nolink&290 | }}
 ~~DISQUS~~ ~~DISQUS~~
battery_compatibility/axistorage.1494581128.txt.gz · Last modified: 2017-05-12 11:25 by edevries