ac_coupling:fronius
ac_coupling:fronius [2015-11-01 11:54] – [AC-coupled PV with Fronius PV Inverters] mvader | ac_coupling:fronius [2020-01-19 15:09] – external edit 127.0.0.1 | ||
This document describes how to setup Energy-storage, | This document describes how to setup Energy-storage, | ||
- | The Victron system monitor, the [[http:// | + | The Victron system monitor, the [[https:// |
===== Frequency shifting ===== | ===== Frequency shifting ===== | ||
- | To make sure that the Fronius PV inverter works well with Victron inverter/ | + | To make sure that the Fronius PV inverter works well with Victron inverter/ |
+ | * The Fronius PV Inverter must be set to Setup MG, short for Micro-Grid. | ||
+ | * For off-grid systems, load the Multi or Quattro | ||
- | With a Fronius PV inverter this is a very easy setup. The Fronius Setup MicroGrid (MG) has been developed in close cooperation with Victron | + | This is a very easy setup. The Fronius Setup Microgrid |
- | | + | **Compatible ROW inverters** (for " |
- | | + | * Fronius |
- | | + | * Fronius Symo (3~, 3 kW up to 20 kW) -> Software // |
- | + | * Fronius | |
- | Compatible inverters | + | * Fronius |
- | * Fronius Galvo (1~, 1.5 kW up to 3.1 kW) -> use latest FW | + | |
- | * Fronius Symo (3~, 3 kW up to 20 kW) -> use latest FW | + | |
- | * Fronius | + | |
- | Recommended for new systems | + | For new systems the Fronius Symo and Fronius Eco inverters |
- | In case of PV modules that need to be grounded, | + | The use of Fronius Galvo inverters |
- | When setting | + | **Compatible UL inverters** (for "US type AC grid") are: |
+ | * Fronius | ||
- | ===== Setting up the Fronius with MG 50/60 ===== | + | For the UL inverters, some more Microgrid Setups are available (e.g. for connection with Neutral conductor or without). Also the UL inverters can be used in 60Hz as well as in 50Hz applications. More information can be found in the user manuals. |
+ | When setting up a system, always update both the Fronius and the Victron devices to their latest firmware versions. For the latest Fronius firmware and information how to update use this link: | ||
+ | [[http:// | ||
+ | ===== Setting up the Fronius with Setup MG50/MG60 ===== | ||
- | - Make sure that the Fronius PV inverter is updated to at least the firmware version mentioned above. See table above. | + | - Make sure that the Fronius PV inverter is updated to at least the firmware version mentioned above. See Inverter list above. |
- After making the inverter operational according to the manual, select the language and after this the country specific setup. | - After making the inverter operational according to the manual, select the language and after this the country specific setup. | ||
- Here choose MG50 or MG60 depending on the system frequency. | - Here choose MG50 or MG60 depending on the system frequency. | ||
Line 46: | Line 56: | ||
- | - Note that it is not necessary to change the default settings in the Assistant. The default settings work together with the default Fronius Micro-grid settings. \\ {{: | + | - Note that it is not necessary to change the default settings in the Assistant. \\ {{: |
- | ===== Frequently asked questions ===== | + | Table for settings for 50Hz and 60Hz frequency |
+ | | ** State ** | ** 50Hz ** | ** 60Hz ** |. | | ||
+ | | Start| 51.0 | 60.2|Hz| | ||
- | === Why doesn' | + | More information on adding Assistants is [[assistants: |
+ | ===== Remote system monitoring ===== | ||
+ | The Victron system can be monitored through Victron VRM Portal if a [[https:// | ||
+ | The Fronius PV inverter data can be [[ccgx: | ||
+ | So the VRM portal is the recommended monitoring platform also for AC-coupled installations. | ||
+ | However, also Fronius offers an equivalent monitoring solution. The Fronius portal is called Fronius Solar.web. The PV system data can be transfered to the portal if the inverter is equipped with a Datamanager 1.0 or Datamanager 2.0. | ||
+ | The usage of both portals in parallel is possible. | ||
+ | A video instruction how to set up the Datamanager 2.0 + Solar.web can be found [[https:// | ||
+ | ===== Zero Feed-in ===== | ||
+ | ==== Q1 Why doesn' | ||
+ | See [[: | ||